Author Topic: The trick to using multiple generators?  (Read 1421 times)
Dave Guilford
« on: July 06, 2020, 09:55:16 pm »
I have a very small multiquip dc7000ss generator thatíll deliver 25amps at 240v.  So basically 50 amps total between 2 circuits (right??).
If I needed more power, is there any reason I canít get a second generator and make sure grounds are tied togrther?  Last time I did separate generators I made sure signal never crossed. Backline on one and PA on the other.  Bass was micíd (no DI) and acoustic guitar / pedals went on PA power (since it needed a DI).
Best practices if I HAVE to use 2 generators?
Chris Hindle
Re: The trick to using multiple generators?
« Reply #1 on: July 07, 2020, 08:47:51 am »
Best Practice?
Rent the "right" Genny for the event.
Almost as good practice?
See if your Genny has a "Link Kit" available, and rent a second unit same as the one you already have.
I don't like splitting supplies between stage power and FOH/Monitiors. Too much chance of singing guitarists to get "tingles", or worse. Wireless Handhelds are a good work around.
Chris.
Dave Guilford
« Reply #2 on: July 07, 2020, 11:44:58 am »
Best Practice?
Chris.
Of course renting the right generator is the real answer.  Sometimes budget doesnít allow for $400+ rental.
That said, putting grounds together from 2 separate generators .. that wonít stop potential shock?  I thought it would, but Iím pretty green on this, which is why I asked.
Better to potentially overload one smaller generator instead?
Stephen Swaffer
« Reply #3 on: July 07, 2020, 12:42:43 pm »
Code requires anything that can potentially become energized to be bonded.  If everything that can be become energized (that is not supposed to be energized!) has a common solid metallic path (ideally to an earth ground somewhere) that is connect to the frame of both generators, then any faults should trip the associated breaker.
The bond needs to be large enough to trip the breaker-a minimum of #12 for 20 A breakers, #10 for 30-60 A breakers.  If it very long, oversized would be better.
Yes, my statement requires some thought-but thinking through is the best way to get it right.
For what it's worth, genny's are a "separately derived service"-but so are transformers.  A lot of venues will have multiple transformers on the premises.  Who worries about sharing their power?  Of course, as long as they are code compliant, they will all be bonded to a common ground.
Steve Swaffer
Dave Guilford
« Reply #4 on: July 07, 2020, 08:51:48 pm »
Sounds like a ďyes ground them togetherĒ answer to me.
« Reply #5 on: July 07, 2020, 09:34:58 pm »
Uh... Dave, exactly how are you proposing to do... eh, what, exactly?  Are you going to parallel the outputs of 2 generators, or are you ensuring that they share a common EGC path?
Dave Guilford
« Reply #6 on: July 08, 2020, 03:38:12 pm »
Hi.  Looking to get more power for backline so I can use my generator for PA
Mike Monte
    • My website
« Reply #7 on: July 10, 2020, 10:12:23 am »
As I understand, multiquip makes a parallel kit:
https://www.multiquip.com/multiquip/pdfs/Parallel_Power_Generation_Overview.pdf
That being said, both units tied to the same ground should work....
fwiw: the info in the above link is a bit confusing to me....
the "paralleling for redundancy" part???
Maybe my coffee hasn't kicked in yet.....
Pardon my ignorance......
With my small power distro I have two inlets.  Each separate inlet powers two 20 amp circuits thus I have an A side and a B side.
My small gen power is: two Honda eu3000is gens joined with the appropriate parallel kit, one gen going to side A, the other to side B.
I have 23amps available per side of my distro thus 46amps total.
If one gen stops, whatever is running from that side of the distro goes down....
I am sure that there must be a way to "sum" both gens' power (Honda used to make a kit for such but not anymore).
In looking at the multiquip link, the pictures do not show such summing...
I am sure that there is a multiquip solution.
Bill Meeks
« Reply #8 on: July 11, 2020, 08:00:46 pm »
I come from the electric power generation world where we measured our generator outputs in hundreds of megawatts (as in over 940 MW per unit at my plant), so maybe things can be a bit more relaxed with small kilowatt-level generators. But when running generators in parallel (which, by the way, is exactly how the US electrical grid works) you have to be super careful to align them in phase and of course frequency before paralleling them. When connecting a generator to the electrical grid, you have special electronic devices that show the phase difference of the incoming generator and the electrical bus (grid) you are connecting it to. The incoming generator is slowly speed shifted until it is in perfect alignment with the grid. You are prevented from closing the output breaker on the generator until it is precisely aligned in frequency and phase with the grid. Failure to do this leads to humongously spectacularly unpleasant consequences when that breaker closes on an out-of-phase generator! At least that is true for the big boys.
So I would think that in order to avoid unpleasant circulating currents and a back-and-forth tussle between the running generator or generators and the unit you are bringing on to parallel the bus, that you would want to align the incoming generator in frequency (speed) and phase before tieing it to the bus. This is probably even more important if one of the generators is significantly larger than the other. When the connection is made and the generators "see each other on the bus", they will come to a common frequency and phase. But that movement to "in phase" could be somewhat violent and will produce some voltage spikes on the bus. So I would not have anything connected to the bus until all the generators were paralleled.
Once paralleled, the generators will tend to share the load fairly equally. And you can have "spinning reserve" as it is called to quickly pick up additional applied load (within reason, of course) without much of a drop in frequency or voltage.
« Last Edit: July 14, 2020, 08:21:47 am by Bill Meeks »
Rob Spence
  • Boston Metro North/West
    • Lynx Audio Services
« Reply #9 on: July 11, 2020, 11:08:16 pm »
The ďparallelĒ kit, as used on inverter generators, the slave simply uses the other generator to sync its inverter.
¬ę Reply #9 on: July 11, 2020, 11:08:16 pm ¬Ľ
Page created in 0.045 seconds with 24 queries.