Author Topic: Power and DMX feeds in the came conduit / cable  (Read 1084 times)
David Allred
« on: May 02, 2019, 12:05:19 pm »
Every where I read that this is a no-no, but I found this from how Acclaim Lighting specs their wiring.
As a reference, they exterior lit the Mercedes Benz dome in ATL.
I really want to run my Shielded Cat5e cable in the conduit with the power runs.
Explanations?
« Last Edit: May 02, 2019, 12:09:35 pm by David Allred »
Cailen Waddell
Re: Power and DMX feeds in the came conduit / cable
« Reply #1 on: May 02, 2019, 12:16:02 pm »
Portable cable is not the same thing as install.  Install jumpers arenít cables pulled in conduit.
Rob Spence
  • Boston Metro North/West
    • Lynx Audio Services
« Reply #2 on: May 02, 2019, 12:19:01 pm »
The issue you face is simply having your DMX cable meet the same insulation spec as the power cable.  It is likely that if you purchase DMX cable with appropriate cable jackets then you can run them together. You still have to separate the DMX from the power at the ends as once you strip the external jacket to terminate, you might no longer meet the insulation requirements for a common enclosure. You canít just use random DMX cable.
Of course, even after you meet the NEC requirements, you still must meet the requirements of the local AHJ (Authority Having Jurisdiction - aka, electrical inspector).
In your example, they used cable manufactured for their purpose. I am sure all the conductors, or at least the 3 sets, were all insulated to 600 V since they mention use at 277v.
Edit to talk about example
« Last Edit: May 02, 2019, 12:26:59 pm by Rob Spence »
Erik Jerde
« Reply #3 on: May 03, 2019, 01:35:21 am »
Manufactured, tested, listed assemblies donít have to meet (in the USA) NEC requirements.  If you open up an appliance thatís rated to draw 240V/50A you will (in my experience) find much smaller conductors than NEC requires for building wire.  Thatís because the mfgr has done all the work to make sure itís safe as designed for the intended application.
David Allred
« Reply #4 on: May 04, 2019, 11:14:13 am »
So the cable exits, but not sold to the end user?  They make jumpers to connect lights, that can't  be run through conduit, but don't know the separation needed.  Why don't they sell the raw cable, or at least offer where to get it?
Erik Jerde
« Reply #5 on: May 04, 2019, 03:17:21 pm »
I found the connectors with no problem.  I wouldnít be surprised if the cable is available through the same dealer, but the website is hard on mobile so I didnít look.
¬ę Reply #5 on: May 04, 2019, 03:17:21 pm ¬Ľ
Page created in 0.033 seconds with 24 queries.