Author Topic: single phase vs 3 phase rac pac power load for amps  (Read 4345 times)
Matt Greiner
Re: single phase vs 3 phase rac pac power load for amps
« Reply #10 on: January 03, 2018, 05:27:53 pm »
I will look into that table as a reference point, thank you Tom. For clarification this is not a 5 wire configuration, it is single phase.  It would be two or three depending on if the neutral counts.
Rob Spence
  • Boston Metro North/West
    • Lynx Audio Services
« Reply #11 on: January 03, 2018, 05:36:02 pm »
Also, consider both the actual expected load and the distance. I use 10-4 for my amp rack but it is only 10 and I know I never exceed 20a (have run on 2 20a circuits).
« Reply #12 on: January 03, 2018, 10:07:59 pm »
10 gauge work for the 30 amps?  Or should I up it to 8 gauge?
I *really* like #8 for 30 Amp circuits if the cable is over 25 ft.  I routinely over-size conductor specifications to minimize voltage drop.
Our arena rigs have #8-5 loomed with the drive snakes for FOH power.
Riley Casey
« Reply #13 on: January 04, 2018, 11:31:09 am »
For all those times you take out the XL3 with dual hot PSUs and two double wide racks of outboard.  When's the last time you put a current clamp on the power lines going to FOH?
« Reply #14 on: January 04, 2018, 02:26:12 pm »
It was the PM4000, but close enough!  These days it could be a run of 12-3 and eventually it might be just that.  The 250' of 8-5 might become amp rack power cables for our next rig....
TJ (Tom) Cornish
  • St. Paul, MN
« Reply #15 on: January 04, 2018, 02:38:38 pm »
The large (for me) power distro order I just placed is largely for L14-20 distribution (and a couple Cali's).  What I like about L14-20 is you can use 12/4 wire, get either 2 120v or one 208v circuit per cord, and no downstream circuit breakers needed.
IMO the various 30A standards are outdated - pretty much anything that requires more than 20A at 120v runs better at 208v anyway, and the 30A size is awkward for a lot of things - not large enough for two heavily loaded 20A circuits per leg, additional cable size requirements, large/expensive breakout boxes, etc.
Page created in 0.041 seconds with 24 queries.