Title: Power Con Breakout Box
Post by: BobWitte on March 18, 2014, 05:58:40 PM
Looking for a powercon breakout box like this:
http://www.filmandvideolighting.com/chauvet-lighting-powercon-splitter-powerstream-4.html?gclid=CMfOl5v5nL0CFYt9OgodPDEA8g (http://www.filmandvideolighting.com/chauvet-lighting-powercon-splitter-powerstream-4.html?gclid=CMfOl5v5nL0CFYt9OgodPDEA8g)


In fact this one may be fine - just wondering if anyone has seen any other options. This is to neatly distribute power to stage locations - lower power like keyboards, headphone amps for in ears, pedal boards...We have powercon breakout to two duplex outlets for these locations, but at the back of stage we want to neatly distribute power in several directions from one 20 amp source.


Thanks,
Title: Re: Power Con Breakout Box
Post by: Ray Aberle on March 18, 2014, 06:52:32 PM
Looking for a powercon breakout box like this:
http://www.filmandvideolighting.com/chauvet-lighting-powercon-splitter-powerstream-4.html?gclid=CMfOl5v5nL0CFYt9OgodPDEA8g (http://www.filmandvideolighting.com/chauvet-lighting-powercon-splitter-powerstream-4.html?gclid=CMfOl5v5nL0CFYt9OgodPDEA8g)


In fact this one may be fine - just wondering if anyone has seen any other options. This is to neatly distribute power to stage locations - lower power like keyboards, headphone amps for in ears, pedal boards...We have powercon breakout to two duplex outlets for these locations, but at the back of stage we want to neatly distribute power in several directions from one 20 amp source.


Thanks,
You will hear many people say very good things about OA Windsor products. Ken custom builds to order, very high quality products... but probably a bit more expensive then the cheap, mass-produced option from Chauvet that you linked to.

Power is one place I would prefer to not "Cheap out" on....

-Ray
Title: Re: Power Con Breakout Box
Post by: Cailen Waddell on March 18, 2014, 07:35:19 PM
I have 2 dozen of the Chauvet power streams.  They are a fine box for the money. Ken also has fine products.  Choose domestic or import. 
Title: Re: Power Con Breakout Box
Post by: Frank DeWitt on March 18, 2014, 09:27:13 PM
Here is another option.
http://whirlwindusa.com/catalog/power-electrical-distribution/default/power-linktm
Title: Re: Power Con Breakout Box
Post by: Geoff Doane on March 21, 2014, 09:01:13 PM
Looking for a powercon breakout box like this:
http://www.filmandvideolighting.com/chauvet-lighting-powercon-splitter-powerstream-4.html?gclid=CMfOl5v5nL0CFYt9OgodPDEA8g (http://www.filmandvideolighting.com/chauvet-lighting-powercon-splitter-powerstream-4.html?gclid=CMfOl5v5nL0CFYt9OgodPDEA8g)


Am I the only one who feels that putting a 20A breaker on a box like this is redundant, or perhaps even encourages someone to feed it from a higher capacity circuit?  PowerCons are only rated at 20A anyway, so shouldn't whatever is feeding the blue input connector be protected at 20 (or maybe only 15, depending where it's plugged in) amps?

GTD
Title: Re: Power Con Breakout Box
Post by: Rob Spence on March 21, 2014, 09:28:43 PM
Am I the only one who feels that putting a 20A breaker on a box like this is redundant, or perhaps even encourages someone to feed it from a higher capacity circuit?  PowerCons are only rated at 20A anyway, so shouldn't whatever is feeding the blue input connector be protected at 20 (or maybe only 15, depending where it's plugged in) amps?

GTD

I suspect it is a UL thing or some such. Power strips have em too.


Sent from my iPad using Tapatalk HD
Title: Re: Power Con Breakout Box
Post by: Mac Kerr on March 21, 2014, 09:41:15 PM
Am I the only one who feels that putting a 20A breaker on a box like this is redundant, or perhaps even encourages someone to feed it from a higher capacity circuit?  PowerCons are only rated at 20A anyway, so shouldn't whatever is feeding the blue input connector be protected at 20 (or maybe only 15, depending where it's plugged in) amps?

GTD

There is no wiring diagram to verify where that breaker is in the circuit, but I would expect it to be on the 4 outlets on the side of the box to protect the rest of the circuit that may be on the feed through from losing power due to a problem with the load on the 4 outlets.

Mac
Title: Re: Power Con Breakout Box
Post by: Jonathan Johnson on March 22, 2014, 11:45:44 AM
Am I the only one who feels that putting a 20A breaker on a box like this is redundant, or perhaps even encourages someone to feed it from a higher capacity circuit?  PowerCons are only rated at 20A anyway, so shouldn't whatever is feeding the blue input connector be protected at 20 (or maybe only 15, depending where it's plugged in) amps?

GTD

Europe has 13A and 26A circuits. It needs to protect the 20A-rated supplying the PowerCon box if connected to a higher ampacity circuit, as it may be sold or used in markets other than the U.S.