I have been tasked to deal with a recurring problem in a chapel close to me. There are three XLR sockets located on a small step up to the main sanctuary part of the church. One of these sockets seems to suffer from rising damp. About three years ago I covered the solder connectors on the socket with "Wonder Gel" (http://www.raytech.it/product/low-voltage/wonder-gel?lang=en). This insulating gel cured the problem, but it is back again, despite the gel. Is there any other solution for insulating the connectors on the back of the xlr faceplate?
-
I have been tasked to deal with a recurring problem in a chapel close to me. There are three XLR sockets located on a small step up to the main sanctuary part of the church. One of these sockets seems to suffer from rising damp. About three years ago I covered the solder connectors on the socket with "Wonder Gel" (http://www.raytech.it/product/low-voltage/wonder-gel?lang=en). This insulating gel cured the problem, but it is back again, despite the gel. Is there any other solution for insulating the connectors on the back of the xlr faceplate?
Is it in a plenum or directly exposed to conditioned cold air that might cause temp differential and condensation?
-
It’s sunk directly into the concrete floor. Cables are run inside buried conduit.
Chapel is only heated for two hours per day which is adding to the problem
Sent from my iPhone using Tapatalk
-
It’s sunk directly into the concrete floor. Cables are run inside buried conduit.
Chapel is only heated for two hours per day which is adding to the problem
Sent from my iPhone using Tapatalk
The condensation is coming inside the conduit...which is pretty common. Try closing the end of the conduit off with expanding foam or silicone. Makes it a bit of a pain to pull additional wiring through later, but helps keep the moisture out of the box.
-
That would make sense. Yea I will try that. I won’t be pulling any cables anytime soon so it doesn’t bother me
Sent from my iPhone using Tapatalk
-
It’s sunk directly into the concrete floor. Cables are run inside buried conduit.
I would suspect there is standing water inside the underground conduit. Can sometimes be cleaned out with a shop vac, but hard to get a good seal with cable in the way.
-
I would suspect there is standing water inside the underground conduit. Can sometimes be cleaned out with a shop vac, but hard to get a good seal with cable in the way.
I would blow it out with a compressor rather than try and suck it out.
-
I would blow it out with a compressor rather than try and suck it out.
I would check the other end to see where the water will spray
Sent from my iPad using Tapatalk Pro
-
I would check the other end to see where the water will spray
Sent from my iPad using Tapatalk Pro
What Rob said, it can be putrid too
-
The condensation is coming inside the conduit...which is pretty common. Try closing the end of the conduit off with expanding foam or silicone. Makes it a bit of a pain to pull additional wiring through later, but helps keep the moisture out of the box.
I’d just grab a block of duct seal and shove some of that in there. That’s what it’s for and it’s not the pain-in-the-ass that foam or silicone would be. You can get it at Home Depot or your electrical supply shop.
-
I’d just grab a block of duct seal and shove some of that in there. That’s what it’s for and it’s not the pain-in-the-ass that foam or silicone would be. You can get it at Home Depot or your electrical supply shop.
+1
Sent from my iPad using Tapatalk Pro
-
+1
Sent from my iPad using Tapatalk Pro
You mean firestop?
-
You mean firestop?
No, duct seal. It is like a putty like modeling clay. It never hardens. I still have some from 1974 that is fine. I am blanking on the trade name.
Sent from my iPad using Tapatalk Pro
-
No, duct seal. It is like a putty like modeling clay. It never hardens. I still have some from 1974 that is fine. I am blanking on the trade name.
DUCT SEAL (https://www.homedepot.com/p/Ideal-1-lb-Block-Duct-Seal-Compound-Standard-Pack-6-Blocks-31-601/300496860?cm_mmc=Shopping%7cTHD%7cG%7c0%7cG-VF-PLA-D27E-Electrical%7c&gclid=EAIaIQobChMImv_MwcTn2AIVAlYNCh3KaAySEAQYASABEgIGEvD_BwE&gclsrc=aw.ds&dclid=CK-4gMjE59gCFYpGNwodaN4EqA)
-Hal
-
No, duct seal. It is like a putty like modeling clay. It never hardens. I still have some from 1974 that is fine. I am blanking on the trade name.
Sent from my iPad using Tapatalk Pro
It does get stiffer but I’ve never had it become unusable. Just this past fall at my in-laws I pulled some out of a hole we were patching up and used it to seal some new conduit. Worked great, had probably been there for a decade, exposed to the MN weather and all.