… choices are needed. Power source Inverter generator, Conventional generator, Batteries …
The primary factors limiting the use of non-linear loads on portable generators are their inefficient use of power and the harmonic currents they generate. Because of their radically different designs, inverter generators, like the EU6500is, and conventional AVR generators, like the ES6500, react very differently to these factors. The harmonic currents generated by non-linear loads, in fact, have less of an adverse effect on inverter generators than they do on conventional AVR generators and so do not require de-rating as conventional AVR generators do.
Harmonic currents cause two major problems in conventional AVR generators: heat and voltage waveform distortion. The first problem is that harmonic currents generate heat in the windings, core, and in the electromagnets of the rotor of conventional AVR generators. Since generator ratings are limited by allowable temperature rise, harmonics act as derating factors. In derating, the magnitude of the current is of obvious importance, because losses are proportional to the square of the current. Increased frequency causes increased core losses and increased copper loss from skin effect. 5th and 7th harmonics are the offenders here because they are in the 600 Hz range.
The second difficulty caused by harmonic currents is voltage waveform distortion. According to Ohm’s law, as each harmonic current encounters the impedance of the power distribution system, it will cause a voltage drop at the same harmonic voltage. Because, the capacitors of switch mode power supplies only draw current at the peak of the voltage waveform, this voltage drop occurs only at the peak of the voltage - leading to a flat topping of the voltage waveform.
The more harmonic content in the current, the more voltage distortion occurs throughout the distribution system. This includes the output terminals of the generator where the generator’s source impedance (particularly the subtransient reactance or “Xd”) will create the greatest voltage drops. If the flat topping distortion at the generator’s output terminals is severe, it can cause voltage regulator sensing problems (Self-Excitation or SE) and inaccurate instrument readings.
The effect that harmonic currents have on the generators is factored into the rating limits given them. How rating limits are affected by load can be illustrated in a “Limit Characteristic” graph that plots kVA and kW versus Power Factor. The fluctuations in the kVA line in the illustration below represent the generator’s operating limits depending on whether its load has a leading or lagging Power Factor. It is important to note that a generator’s Limit Characteristic graph will vary by the type of generator. The illustration below (courtesy of Caterpillar) is for a conventional AVR generator. Since the power quality of an AVR generator is intractably linked to its' engine - the effect of harmonics on the engine's governing system is the primary limiting factor. How the engine and its' governing systems are affected by lagging and leading power factor loads is illustrated by the engine kW limit line below.
(http://www.screenlightandgrip.com/images/generators/R_Gen_Rating_Limits.jpg)
A Limit Characteristic graph for a generator illustrates the effect of leading
or lagging Power Factor on the generator's output.
What this generator’s Limit Characteristic graph tells us is that, operating a capacitive non-linear load (the leading power factor quadrant right of the Unity Power Factor center line), this AVR generator first reaches a thermal limit as a consequence of heat generation in the generator's rotor from harmonic currents. And since, conventional AVR generators regulate voltage by means of a power feedback loop from the generator Stator (via the Sensor Coil), through the Exciter (Voltage Regulator), to electromagnets in the Rotor, Armature flux generated by harmonic currents in the Stator leads to erroneous Self-Excitation (SE) and therefore voltage. Put simply, lower power factor loads cause instability of the generator’s voltage output. Finally, since there comes a point as the Power Factor of the load decreases, when harmonics inhibit the successful operation of the generator’s Automatic Voltage Regulator all together, and hence the generator’s capacity to generate any power at all, the kW output eventually drops to zero. Since the voltage instability in conventional AVR generators is a function of the non-linear loads they power, the conventional wisdom is to limit the amount of non-linear loads it can power by roughly half of the generators capacity.
(http://www.screenlightandgrip.com/images/generators/EU_Gen_Rating_Limits.jpg)
The Limit Characteristic graph for an Inverter generator.
Note the negligible effect that leading Power Factor loads have on the generator's power capacity.
As the Limit Characteristic graph for an inverter generator above illustrates, it is a completely different situation with inverter generators. Because the speed of the motor is always changing, inverter generators cannot maintain voltage output by the conventional means of regulating the excitation current in Rotor electromagnets. Instead, inverter generators use permanent magnets in place of electromagnets.
A permanent Magnet is an object made from a material that is naturally magnetized (Neodymium in this case) and hence creates its own persistent magnetic field. Since permanent magnets do not require an excitation circuit, armature flux created by harmonic currents will not cause voltage instability as it does in conventional AVR generators.
(http://www.screenlightandgrip.com/images/generators/waveform_elec_ballast_AVR-I.jpg)
Left: Conventional AVR Generator w/1200W non-pfc electronic ballast. Right: Inverter Generator w/1200W non-pfc electronic ballast.
And since the generator’s inverter completely processes the raw power generated by the permanent magnet (converting it to DC before converting it back to AC by means of a micro-processor), the AC power it generates is completely independent of the engine. By switching IGBTs according to Pulse Width Modulation control logic, an inverter generator is much better able to sustain output voltage against transient loads and, therefore, it has a much lower internal reactance compared to conventional AVR machines. Finally, since the Impedance encountered by harmonic currents that causes voltage waveform distortion is a function of the internal reactance of the generator’s engine to changes in load, a second benefit to using permanent magnets in place of electromagnets in the generator’s Rotor is that as is evident in the oscilloscope shots above, inverter generators consequently are much less susceptible to voltage waveform distortion.
(http://www.screenlightandgrip.com/images/generators/Inverter_Gen_Comp_Chart.jpeg)
TABLE COURTESY OF KIRK KLEINSCHMIDT.
The end result is that leading power factor loads do not cause voltage regulation errors in inverter generators as they do in conventional AVR generators. Inverter generators are able to hold their voltage stable within ±1% of the mean voltage, as opposed to the ±3% of conventional generators using analogue AVRs and are much less susceptible to voltage drop and AC Frequency (Hz) as a function of load (see table above.)
The rock solid power and low sub-transient impedance of inverter generators enable you to operate larger non-linear loads on them than can be operated on conventional AVR generators. For instance, we have struck 6kw HMI Pars on a modified Honda EU6500is inverter generator without problem.
These power quality issues have been vexing film electricians for years, to learn more about how we have learned to remediate the adverse effects of harmonics read a white I have written on the use of portable generators in motion picture production available at http://www.screenlightandgrip.com/html/emailnewsletter_generators.html.