Post by: Todd Macdonald on September 29, 2014, 03:55:06 PM
Hello everyone,

I'm going to be touring with a performer that uses lots of silence and sings and plays very softly. Her audiences are respectful but often times PA systems, air conditioning units, bar tending equipment and other devices cause a noticeable distraction during her performances.

Does anyone have any experience with including minimum PA/Room noise floor level requirments for a technical rider?
What are reasonable requests?  I'm trying to write something clear enough for the promoters in each city to understand that its important to double check as well as technically clear so rental companies and venues can be prepared.

Sincerely,
:)
Todd Macdonald
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Doug Fowler on September 29, 2014, 04:31:57 PM
Read the rules, fix your display name.

Thank you for your cooperation.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Ivan Beaver on September 29, 2014, 08:10:58 PM
Hello everyone,

I'm going to be touring with a performer that uses lots of silence and sings and plays very softly. Her audiences are respectful but often times PA systems, air conditioning units, bar tending equipment and other devices cause a noticeable distraction during her performances.

Does anyone have any experience with including minimum PA/Room noise floor level requirments for a technical rider?
What are reasonable requests?  I'm trying to write something clear enough for the promoters in each city to understand that its important to double check as well as technically clear so rental companies and venues can be prepared.

Sincerely,
:)
Todd Macdonald
Not to be rude- but I highly doubt any venue is going to spend LARGE amounts of money to redo the HVAC system to your liking.

I suggest you only choose places to play that meet your requirements.

BTW-what ARE your requirements NC or RC wise?

How do you plan on keeping the audience quiet and not order drinks etc during the performance?
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: g'bye, Dick Rees on September 29, 2014, 08:20:51 PM
I agree.

You cannot expect a one-time exception or alteration of any business practices or operating procedures/equipment due to artist sensitivities.

The one possible exception would be to request people not order espresso drinks during the performance...I hate those machines.

Otherwise it's up to the performer working in non-concert venues to be able to project to the audience and "own the room".   Street performers learn this early on.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Tim Tyler on September 29, 2014, 08:25:41 PM
A venue such as the Birchmere, in Wash. DC, sounds like a candidate with the required rules already in place, but as Ivan says, too many changes from an establishment's norm could be problematic... 

-Tim T
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Mark Cadwallader on September 29, 2014, 11:47:58 PM
From time to time a venue I work at has an artist that not only requires the HVAC be off during the performance, but even the fans in the dimmer room have to be off, even if that means no stage light dimming. He doesn't play there too often, but is a Name You Probably Know in "new age" music. Mark C.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Jim McKeveny on September 30, 2014, 11:39:30 AM
From time to time a venue I work at has an artist that not only requires the HVAC be off during the performance, but even the fans in the dimmer room have to be off, even if that means no stage light dimming. He doesn't play there too often, but is a Name You Probably Know in "new age" music. Mark C.

Are we bringing "Burning Man" indoors?

Open field/clear skies are wonderful, but turnstiles are turnstiles, etc, etc.

You are asking for commerce w/o the "commerciality", I believe.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Milt Hathaway on September 30, 2014, 11:58:44 AM
Open field/clear skies are wonderful, but turnstiles are turnstiles, etc, etc.

You are asking for commerce w/o the "commerciality", I believe.

Yup, some people just aren't meant to be live performers and cannot make that difficult jump from "musician" to "entertainer".
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: g'bye, Dick Rees on September 30, 2014, 12:01:47 PM
From time to time a venue I work at has an artist that not only requires the HVAC be off during the performance, but even the fans in the dimmer room have to be off, even if that means no stage light dimming. He doesn't play there too often, but is a Name You Probably Know in "new age" music. Mark C.

I had a quirky, well-known folkie for an intimate concert.  When the promoter brought him to the hall for sound check, he wouldn't come near anyone without asking, "Do you have cats?  I'm allergic to cats!"  When he found out I had some at home, pretty much refused to be on stage unless I stayed behind the board, even insisting that I move FOH from the optimum position to the back corner of the room.

He gave his concert without much further fuss.  I thought it strange that he had no adverse reaction to sitting in the middle of the oriental carpet I had placed on stage as I had brought it from my living room...where the four of my cats loved to roll and play on it.

Two one-hour sets on a cat carpet and no allergic reaction...but he wouldn't shake anyone's hand.

CATS!!!
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Chris Hindle on September 30, 2014, 12:10:45 PM
  I thought it strange that he had no adverse reaction to sitting in the middle of the oriental carpet I had placed on stage as I had brought it from my living room...where the four of my cats loved to roll and play on it.

Two one-hour sets on a cat carpet and no allergic reaction...but he wouldn't shake anyone's hand.

CATS!!!

Some people just "need" a cause......
Personally, I bet I wash my hands more often than you de-cat the cat carpet.....
I do understand the allergy. My wife is allergic to cat/dog saliva. Fur, no problem. Lick her hand, and in 10 minutes she starts to puff up.
THAT is an allergic reaction.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Art Welter on September 30, 2014, 12:11:48 PM
Does anyone have any experience with including minimum PA/Room noise floor level requirments for a technical rider?
What are reasonable requests? 
Todd,

As others have mentioned, you are unlikely to get any noise reductions in the venues you will play, your only real choice is to not book the act in the obvious offenders.

I have encountered contract riders that specifically request the PA system "must be free of any extraneous hum or noise", though unfortunately, if you encounter a PA with extraneous hum or noise, it is unlikely the providers have read your rider or even have a concept of signal to noise.

Bring isolation transformers and shield (pin 1) lifts along to fix those problems.

Art
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Jim McKeveny on September 30, 2014, 12:18:29 PM
My wife is allergic to cat/dog saliva. Fur, no problem. Lick her hand, and in 10 minutes she starts to puff up.


I have never met your wife,  (but I love her as a fellow human).

I promise to never lick her hand.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Tim McCulloch on September 30, 2014, 01:36:55 PM
I have never met your wife,  (but I love her as a fellow human).

I promise to never lick her hand.

Jim, we had no idea you were really a feline...

Back when I had good employer health insurance (it wasn't in this industry, that's for sure) I went to an allergist for testing.  When the lab did the white cell reactions to guide the scratch tests, they considered a "strong positive reaction" to be 400 white cells or more.  The lab tech counted 8000 on my reaction to dogs and quit counting the cat reaction at 10,000.  And of course the allergist asks me "do you have cats?"  Yeah, 2 of them and no, I'm not getting rid of them.

Three years of allergy shots later (antigen therapy) and I was largely reaction-free with my pets although new cats caused a small reaction.

It sucks because I really like animals and have some degree of allergy to almost every critter with 4 legs.

Back to the OP - nope, if your artist is playing anywhere that liquor or food is the main source of revenue I can almost guarantee that your needs will be ignored completely or only given the most cursory of lip service.

I've seen national act riders that specify that house HVAC will be turned off - it was done - and the stream of ticket buyers demanding refunds as the temperature went up 15 degrees in an hour left the house with no option but to piss off the artist.  This led to much backstage screaming and threats of lawsuits and I'm not sure how it was worked out, but the promoter and venue reps both told me they would not make this accommodation again.  The ultimate irony?  The artist had a line of fans on the downstage lip, pointing at him anywhere he'd stop to pose.

While I appreciate that "artists" need to be in their comfort zone, the artist does not exist without a fan base and pissing off those folks ("sorry, the air conditioning is off because Ms. X demands it) will certainly hurt future attendance, product sales and on-site merch sales.  Man (or woman) up and get medical attention for whatever condition "requires" this abject silliness.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Alex Donkle on September 30, 2014, 03:39:57 PM
I've seen national act riders that specify that house HVAC will be turned off - it was done - and the stream of ticket buyers demanding refunds as the temperature went up 15 degrees in an hour left the house with no option but to piss off the artist.  This led to much backstage screaming and threats of lawsuits and I'm not sure how it was worked out, but the promoter and venue reps both told me they would not make this accommodation again.  The ultimate irony?  The artist had a line of fans on the downstage lip, pointing at him anywhere he'd stop to pose.

Tim, was the HVAC actually noisy in any of those venues?

To the OP, same as what others are saying. Quiet HVAC is not a simple request, and can be extremely expensive to retro-fit an existing HVAC system if it wasn't originally designed to be quiet.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Tim McCulloch on September 30, 2014, 04:04:51 PM
Tim, was the HVAC actually noisy in any of those venues?

To the OP, same as what others are saying. Quiet HVAC is not a simple request, and can be extremely expensive to retro-fit an existing HVAC system if it wasn't originally designed to be quiet.

Arena HVAC is never quiet enough, but some are certainly more objectionable than others.  Even in our PAC's symphony concert hall the HVAC raises the noise floor at least 12dB.  I was in there making physical measurements one night and was surprised by how much of the room's low-level reflections were partially masked by the HVAC noise (the system was turned off).  If Maestro heard what the room really sounded like, he'd be pushing for a new hall....

At the auditorium/arena level the rider requirements for HVAC curtailment is usually for the perceived comfort or health of the performers.  The Queen of Soul requires that any vents in her dressing room be covered with cardboard and taped over, and that no moving air is pumped over or around the stage (at least she is considerate of her audience).  A "rock legend" whose band was very big back in the Spandex and Eyeliner days is the one with the NO HVAC requirement, but brings a half dozen squirrel cage fans to place between monitor wedges...  In both cases, though, the rider asserts the HVAC requirements are for the health of the artist.  I just find Mr. Superstar's requirement a bit specious based on the "fan club" across the stage apron.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Alex Donkle on October 01, 2014, 07:40:37 PM
Arena HVAC is never quiet enough, but some are certainly more objectionable than others.  Even in our PAC's symphony concert hall the HVAC raises the noise floor at least 12dB.  I was in there making physical measurements one night and was surprised by how much of the room's low-level reflections were partially masked by the HVAC noise (the system was turned off).  If Maestro heard what the room really sounded like, he'd be pushing for a new hall....

HVAC does nearly always increase the noise floor in performance venue, but it also depends what the lower level noises the HVAC system is masking. Chair squeaks, audience member coughing, or outdoor noise are generally more distracting than steady-state HVAC (assuming it's in the NC20-30 range of most theatres, arenas are typically around NC40 at the top of the arena bowl but often quieter near the floor just from the distance between those seats in the diffusers).

Or if there are no other noise sources, then it's just unconformable (e.g. anechoic test chamber).
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Ivan Beaver on October 01, 2014, 07:43:42 PM
HVAC does nearly always increase the noise floor in performance venue, but it also depends what the lower level noises the HVAC system is masking. Chair squeaks, audience member coughing, or outdoor noise are generally more distracting than steady-state HVAC (assuming it's in the NC20-30 range of most theatres, arenas are typically around NC40 at the top of the arena bowl but often quieter near the floor just from the distance between those seats in the diffusers).

Or if there are no other noise sources, then it's just unconformable (e.g. anechoic test chamber).
In most new churches around here-we are LUCKY to get an NC of 45-50.

I have measured many that were in the 60-65 range.  NO KIDDING!!!!!!!

The HVAC guys say they can "balance" the system to get it quieter.  Well-maybe-but they won't get anywhere near anything acceptable.

The owners just usually give up and stop trying to get it fixed.  Truly sad
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Frank Koenig on October 01, 2014, 09:26:04 PM
The Dolby Labs screening room in San Francisco is set up to provide simulated HVAC noise through the sound system. If you're in the movie business...

--Frank
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Scott Olewiler on October 02, 2014, 06:18:02 AM

The HVAC guys say they can "balance" the system to get it quieter.  Well-maybe-but they won't get anywhere near anything acceptable.


There are two types of "balancing" in the HVAC world. One is to balance the fan wheel much like you balance a tire to reduce the vibrations from it. The other type is to balance the air by installing a diffuser screen, a piece of metal with perforations in it, which will reduce the turbulence in the air. Neither of these two methods are going to lower your noise floor much.

IF the noise is coming through the ductwork itself, and is not bleed over from the mechanical room,  duct installed sound attentuators or silencers will greatly reduce the noise level passing thru from the motor and fan.  I'm not sure what the claimed reduction is off the top of my head but if you stand on one side of a 3 foot section of this and talk into the "silencer" at a normal conversation level, no one will hear you on the other side.

These are not that expensive to buy or very difficult to install but they will necessarily lengthen your ductwork and can reek havoc on the unit's performance which in turn is going to require a larger fan/motor and/or different evaporator coil. If the sound reduction requirement is not factored into the original unit's configuration I imagine it's a real PITA to retrofit them in.

My day job is working for one of the world's largest HVAC companies. I work in the commercial air handling manufacturing division and we install these sound attentuators in our custom products weekly.  Occasionly we have customers spec out sound testing on the units before they take delivery. That testing often is 3-4 times the cost of the actual unit and in some cases a single test order exceeds my generous annual salary.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Ivan Beaver on October 02, 2014, 07:39:45 AM
There are two types of "balancing" in the HVAC world. One is to balance the fan wheel much like you balance a tire to reduce the vibrations from it. The other type is to balance the air by installing a diffuser screen, a piece of metal with perforations in it, which will reduce the turbulence in the air. Neither of these two methods are going to lower your noise floor much.

IF the noise is coming through the ductwork itself, and is not bleed over from the mechanical room,  duct installed sound attentuators or silencers will greatly reduce the noise level passing thru from the motor and fan.  I'm not sure what the claimed reduction is off the top of my head but if you stand on one side of a 3 foot section of this and talk into the "silencer" at a normal conversation level, no one will hear you on the other side.

These are not that expensive to buy or very difficult to install but they will necessarily lengthen your ductwork and can reek havoc on the unit's performance which in turn is going to require a larger fan/motor and/or different evaporator coil. If the sound reduction requirement is not factored into the original unit's configuration I imagine it's a real PITA to retrofit them in.

My day job is working for one of the world's largest HVAC companies. I work in the commercial air handling manufacturing division and we install these sound attentuators in our custom products weekly.  Occasionly we have customers spec out sound testing on the units before they take delivery. That testing often is 3-4 times the cost of the actual unit and in some cases a single test order exceeds my generous annual salary.
The fundamental problem most of these installs have is that they are simply trying to force to much air through ducts that are to small.

Sometimes there is only 1 or 2 bends before the duct enters the room-so you can easily hear the fan noise.

Of course more/longer ducts and larger ducts cost extra money-and the HVACs company is to supply temp to the room-they are often not concerned with how much noise it makes-because that will cost extra.

Once the system is installed and the walls and ceiling are up-it can get real expensive to fix it.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Steve M Smith on October 02, 2014, 08:00:42 AM
Not particularly relevant, but the start of Deep Purple's Fireball features the studio's air conditioning starting up (intentionally).


Steve.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Alex Donkle on October 03, 2014, 03:41:26 AM
There are two types of "balancing" in the HVAC world. One is to balance the fan wheel much like you balance a tire to reduce the vibrations from it. The other type is to balance the air by installing a diffuser screen, a piece of metal with perforations in it, which will reduce the turbulence in the air. Neither of these two methods are going to lower your noise floor much.

IF the noise is coming through the ductwork itself, and is not bleed over from the mechanical room,  duct installed sound attenuators or silencers will greatly reduce the noise level passing thru from the motor and fan.  I'm not sure what the claimed reduction is off the top of my head but if you stand on one side of a 3 foot section of this and talk into the "silencer" at a normal conversation level, no one will hear you on the other side.

These are not that expensive to buy or very difficult to install but they will necessarily lengthen your ductwork and can reek havoc on the unit's performance which in turn is going to require a larger fan/motor and/or different evaporator coil. If the sound reduction requirement is not factored into the original unit's configuration I imagine it's a real PITA to retrofit them in.

My day job is working for one of the world's largest HVAC companies. I work in the commercial air handling manufacturing division and we install these sound attenuators in our custom products weekly.  Occasionally we have customers spec out sound testing on the units before they take delivery. That testing often is 3-4 times the cost of the actual unit and in some cases a single test order exceeds my generous annual salary.

Scott-
Your experience differs from mine. Duct silencers are typically not integrated into large HVAC equipment that we deal with for new buildings, since that puts them too close to the fan wheel for a laminar airflow through the silencer, which greatly increases the static pressure, causes the fan to spin faster / louder, and defeats the purpose. Occasionally we have large discharge and return plenums added to the built-up AHU connections as those don't add significant pressure drop, but that's it. Silencers are more often installed 4-6' down the duct away from the AHU, ideally centered in the mechanical room wall.

Balancing HVAC can affect high-frequency noise (the whooshing sound at diffusers) if the flow isn't evenly divided between all the diffusers in the system. Air diffusers noise is directly related to air volume (cubic feet per minute) and how smooth the airflow is. If you have 2 diffusers in a room and one is receiving significantly more air than the other (caused by poor HVAC system balancing), the diffuser receiving more airflow than designed will generate more noise. Low frequency noise is rarely affected by system balancing, unless the system has so much excess pressure drop that the fan has to run at higher RPM to compensate.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Ivan Beaver on October 03, 2014, 07:33:22 AM
Not particularly relevant, but the start of Deep Purple's Fireball features the studio's air conditioning starting up (intentionally).


Steve.
I always wondered what that sound was-thanks :)
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Scott Olewiler on October 03, 2014, 10:01:49 AM
Scott-
Your experience differs from mine. Duct silencers are typically not integrated into large HVAC equipment that we deal with for new buildings, since that puts them too close to the fan wheel for a laminar airflow through the silencer, which greatly increases the static pressure, causes the fan to spin faster / louder, and defeats the purpose. Occasionally we have large discharge and return plenums added to the built-up AHU connections as those don't add significant pressure drop, but that's it. Silencers are more often installed 4-6' down the duct away from the AHU, ideally centered in the mechanical room wall.



The size units we're building are 25 to 45 ft long with tunnels as large as 12' by 12' to begin with and our silencers are usually downstream of the supply fan a good  10-20 ft in the unit itself.  Often we see them upstream of the fans as well. Sometime both upstream and downstream. We don't design here, but just build to what is ordered, so I don't understand all the rationale.  I have noticed silencer usage in the units themselves seems to have dropped with an uptick in energy recovery wheels and have often wondered if they don't have a significant noise reduction quality as a result of their design.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Jeremy Young on October 04, 2014, 02:34:49 PM
How did this turn into an HVAC thread?  My bills are also paid through residential HVAC/Hydronics work (design, wholesale sales and technical support) and a lot of the tools I've learned from this site have actually helped that business.  For example, air-source heat pumps with a specified dB(a) @1m half-space sound rating can sometimes be a higher number than is "acceptable" for some old-timer friendly neighbourhood bylaws or stratas.  some quick use of the ISL to approximate the noise level at the property line (where the bylaw measurement is taken) can quickly aid me in a sale and keep those people off my back.  Thanks PSW forums!

The mechanical trades balancing I'm most familiar with is that which Alex mentions; trying to achieve balance between diffusers (or heat emitters of any kind).  In live audio, I'm blessed with some conveniences.  For example, if I take two monitor wedges (same model, identical electrically for all intents and purposes) and run them on the same amp channel in parallel, even though one might be twice the distance from the amplifier, i would expect to see the exact same voltage applied to both cabinets.  With matched sensitivities, I would expect the "throw" (perceived loudness, which is our goal) to be identical.  Now let's replace that amp with an air-handling unit, the speaker wire with a spiral duct, and the speakers with diffusers.  assuming identical diffusers, i will most certainly not get the same "throw" (velocity of air) at both diffusors.  since the greater duct run creates a higher friction loss (static pressure), we can add friction (almost like an L-pad for a high-sensitivity tweeter) to the shorter run with a mechanical damper partially closed.  Even coverage of the room with equal supply temperatures is typically the goal of most systems designed for human comfort.  Like anything perceived, it's more about comparison than nominal values.

Balancing is typically a mechanical engineer specified step of commissioning any commercial system before it is considered complete during new construction.  Re/Re however has very few strict "rules" about what is acceptable and what is not.  Ivan, I'm sorry to hear the HVAC companies in the areas you've experienced have been unable to keep their duct velocities to acceptable levels.  Larger diameter ducting will extend the life of the blower (if ECM type, also reduce amperage draw), as well as reduce noise. 

With variable volume systems, this really needs to become an automated process to achieve complete control, but that's for another thread.

Sorry, i promise not to compare HVAC and Audio again! (today).

To bring this back to point for the OP, I couldn't imagine requesting a venue to stop making drinks, or providing space conditioning for it's ticket holders based on the required noise floor for a quiet passage of a performance. personally i would find a lack of human comfort more distracting than some low level constant noise during a quiet passage in a performance.

In your shoes I would take the opposite approach: stating that the system provide a specific minimum of dynamic range above the noise floor of the venue.  That way if the "quiet" passage is meant to be 10-20dB (just a random number, please be nice) below the louder passages, and let's say you wanted the quietest passages to be 10dB above the noise floor, then you could say you need a system that can adequately provide a minimum of 30dB above the noise floor of the venue.  That way you get your comparative levels you wanted, specific to the loudness of the venue. 

However, I've been in busy bars during sound check for a band, where the audience sound level was 90dB at mixing position.  Give people some beer and a hockey game on mute, and they'll make more noise than any walk-in cooler or unbalancing ceiling fan you can find.  If I needed 30dB above that, we would have other comfort issues at hand unless i had a large box of earplugs handy for the audience. 

That's my two cents on the matter!  Good luck!
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: brian maddox on October 05, 2014, 08:46:18 AM
The Dolby Labs screening room in San Francisco is set up to provide simulated HVAC noise through the sound system. If you're in the movie business...

--Frank

Funny I happen to BE in SF.  where is this screening room you speak of.....
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Jason Raboin on October 05, 2014, 01:11:56 PM
I have worked in venues and with artists that have specific needs outside the realm of normal.  The only way to ensure success is to have management alert the agent to the needs and have them agreed upon during the booking process.  If it is really that crucial, it should be discussed by the agent with the venue buyer and not just written in a rider.  By the time it gets to the advance it may be too late.  A venue may agree to suspend wait service, or not make drinks at the bar during the set, but doing so may result in a lower guarantee to compensate the venue for a potential loss of income.  Once the contract is signed a venue is less likely to agree to stipulations that may impact their income or impact the comfort level of their patrons. 

My primary artist will not play venues with a bar inside the theatre.  Seating is only allowed between songs.  There are to be no servers or vendors walking in the venue during the show.  This is all in the rider and agreed upon before it gets to me to do the advance.

As to the actual question - PA system noise, I have not found this to be an issue in most modern sound systems.  I assume that the show is pretty quiet, so there are many places in the system you can turn it down and reduce the noise floor.  I guess I would stay away from moving light rigs, as the fans can be a distraction.

During the advance and in the rider you could ask that amp racks be placed as far off stage as possible to reduce amp fan noise.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: George Dougherty on October 05, 2014, 10:57:24 PM
I had a quirky, well-known folkie for an intimate concert.  When the promoter brought him to the hall for sound check, he wouldn't come near anyone without asking, "Do you have cats?  I'm allergic to cats!"  When he found out I had some at home, pretty much refused to be on stage unless I stayed behind the board, even insisting that I move FOH from the optimum position to the back corner of the room.

He gave his concert without much further fuss.  I thought it strange that he had no adverse reaction to sitting in the middle of the oriental carpet I had placed on stage as I had brought it from my living room...where the four of my cats loved to roll and play on it.

Two one-hour sets on a cat carpet and no allergic reaction...but he wouldn't shake anyone's hand.

CATS!!!

Sounds like an over reaction but I have a friend that ended up in the hospital from visiting a house that "used" to have cats. It's rare but some people do have very strong reactions.
Title: Re: Minimum PA/Room noise floor level requirments for a technical rider
Post by: Frank Koenig on October 05, 2014, 11:55:58 PM
Funny I happen to BE in SF.  where is this screening room you speak of.....

It's at the Dolby corporate headquarters at 100 Potrero Ave. They hold AES San Francisco Section meetings there now and then (thank you Dolby). We got a demo of the simulated HVAC noise at Dan Dugan's very interesting presentation on nature sound recording a couple years ago. It was along the lines of "now everyone be really quiet and describe what you hear". And we're all like "it's pretty quiet but I hear some rumbling, sounds like HVAC". Then they turn it off and tell us that it was coming out of the speakers.

I suppose that to demonstrate to clients what various cinema processing schemes sound like you need realistic movie theater background noise. -F