Sound Reinforcement - Forums for Live Sound Professionals - Your Displayed Name Must Be Your Real Full Name To Post In The Live Sound Forums > AC Power and Grounding

Correct wire size L 14/30

<< < (4/4)

Scott Holtzman:

--- Quote from: Steve Crump on October 27, 2023, 04:14:45 PM ---I called for a quote today. 6-4 SOOW 2.95 per ft and SEOOW 3.25 per foot.

This based on what the vendor had to pay at time of purchase.

What we are paying for copper wire is way down from the past few months.

But the real reason I came back to post is because after all these post I decided to go unbox the 6-4 cord that I purchased and see what I thought of it in order to post my opinion. I already have cords that I use, so what I previously purchased was still stored. Well, what is shown on line and what is in the box is different. It is 6-4 but, it is STOW.

Outside of box indicates that same as the verbiage online.

--- End quote ---


What is STOW?

Caleb Dueck:

--- Quote from: Scott Holtzman on October 27, 2023, 11:18:56 PM ---
What is STOW?

--- End quote ---

Service (not SJ or Service Junior)
Thermoplastic
Oil resistant outer insulation
Water resistant outer insulation

If this is off, please correct me. 

Rob Timmerman:

--- Quote from: Steve-White on October 27, 2023, 12:46:45 PM ---This is confusing to me.  I've read through it a couple of times and it still doesn't make sense.  In this situation, optimal wire gauge is determined by load -vs- distance.  That's it, pure and simple - Load and Distance.  Nothing to do with L1, L1-L2, single phase, 3-phase.

The Neutral is always considered a current carrying conductor regardless of load type, condition or power format.

Power Factor/Demand Factor modeling isn't typically used for something like this, just down and dirty estimates based upon maximum current draw conditions.

Agreed on #8 being the best solution here at 100' distance.

--- End quote ---

There are two factors to consider when sizing power conductors: performance and safety/regulatory.  The safety/regulatory perspective sets the minimum size you can use, but you are free to upsize the conductors for performance if you so desire.  My comment about 10AWG being suitable in some cases but 8AWG being appropriate for an L14-30 feeding nonlinear loads on a 3-phase service was based on the NEC (the model code for the US).

Last time I checked, for the purposes of derating based on conductor count, the NEC does not consider the grounded (neutral) conductor to be current-carrying if the conductor only carries the unbalanced current from other conductors.  However, this exception does not apply to 3-phase circuits missing a phase conductor, or circuits that have nonlinear loads.  Logically, this makes sense, as the derating factors based on conductor count come from the ability of the conductors to dissipate heat to the environment and the temperature rise limits of the conductors.

Tim McCulloch:

--- Quote from: Scott Holtzman on October 26, 2023, 09:10:15 PM ---The issue is SE is less than 1/2 the price of SO.  To me it feels the same as SJ even though some of the properties are superior to SO. 

Plastic cable just doesn’t belong on a stage.  It doesn’t sit flat and sure doesn’t roll correctly. 


Sent from my iPhone using Tapatalk

--- End quote ---
All of the #10 and #8 purchased in the last 15 years at my old shop was SEOOW.  It handled as well as SOOW.  It's not the same as thermoplastic outer jacket.  Not at all.

Steve Crump:

--- Quote from: Scott Holtzman on October 27, 2023, 11:18:56 PM ---
What is STOW?

--- End quote ---

Caleb is correct.

Today when I was cleaning off my trailer from last weekends event I took time to look at my cords. The 100' is SEOOW and the 50' is SOOW, both are 6-4. I really didn't feel or see a difference that would make me grab one over the other except for length.