Generator Education: Backup generators, Power factor, etc
« on: June 17, 2022, 08:58:49 AM »

Hello,


We are looking to have a full-time backup generator installed in our church (In Soweto, Johannesburg, South Africa). The power system in our country leaves much to be desired, and we are on load-shedding (scheduled or not) some portion of nearly every day.


To calculate the size of generator we need, we hired an electrician who specializes in generator installation/etc., he did calculations of our draw with everything powered on, came to the conclusion we need a 35-45 Kw set. This is a 3-phase installation.


I trust them, this is really more for my education: The generators all have a 'power factor' rating, nearly all of the diesel 3ph ones here are 80%. At first I thought this meant that was the max constant load (in other words, only use 80% of the 45kw rating) but from my cursory reading, this appears to be an efficiency rating.


My questions:


1: How oversized should a generator be? If your actual current usage is 35-40kw, will a 45kw generator generally be sufficient or should we be stepping up? Our loads are: Small PA, house and stage lighting (all LED), various office equipment, roof-mounted evaporative coolers. No heaters, no AC. I know bigger will always be better to a point, but two issues: Cost (of course), and from what I've read, if your generator is oversized it will be less efficiently if your regular load is below it's ideal range. Is any of that true, or just mythology?


2: What does the Power Factor rating really mean? Does it matter to me in generator choice?


3: Any other questions that I should be asking?


Thanks in advance!

Logged

Frank Koenig

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1327
  • Palo Alto, CA USA
Re: Generator Education: Backup generators, Power factor, etc
« Reply #1 on: June 17, 2022, 12:08:31 PM »

“Power factor” here refers to an electrical property of the power that is imposed by the load. Specifically, it’s the ratio of power (sometimes called “true power”) to apparent power. Power is the power turned into heat in the load. Apparent power is the product of the RMS voltage and RMS current and, for many purposes, is what is “felt” by the generator, transformer, transmission line, etc. For a sine wave the power factor is the cosine of the phase difference between the current and the voltage and is equal to 1 for a purely resistive load and zero for a purely reactive load.

The 80% may refer to the power factor at which the generator can deliver the rated power, which would mean that the apparent power (in Volt-Amperes)  it can deliver is 125% of the power (in Watts). I would have to see the detailed generator specs to be sure.

In my experience contractors have a way of specifying generators, air conditioners, well pumps and many other things that are larger than what the customer actually needs. (Sound providers, however, never do this ;) ) An over-specified unit not only costs more to begin with but often is less efficient because of its lower utilization. Having said this, engine-driven generators should be sized somewhat generously. There are many factors and it’s a bit of an art. In the case of diesel engines you do not want the generator to be much too large for the steady-state load as the engines become unhappy running for extended periods at very light loads –- see “wet-stacking”. If you’re at all  in doubt get another opinion.

Depending on requirements and budget you might also consider a battery storage system like the Tesla Powerwall.  It would be interesting to compare the life-cycle cost with a generator.

--Frank
« Last Edit: June 17, 2022, 12:12:49 PM by Frank Koenig »
Logged
"Nature abhors a vacuum tube." -- John Pierce, Bell Labs

Chris Hindle

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 2709
  • Montreal, Quebec, Canada, Earth, Sol System,......
Re: Generator Education: Backup generators, Power factor, etc
« Reply #2 on: June 17, 2022, 12:56:24 PM »

Hello,


We are looking to have a full-time backup generator installed in our church (In Soweto, Johannesburg, South Africa). The power system in our country leaves much to be desired, and we are on load-shedding (scheduled or not) some portion of nearly every day.


To calculate the size of generator we need, we hired an electrician who specializes in generator installation/etc., he did calculations of our draw with everything powered on, came to the conclusion we need a 35-45 Kw set. This is a 3-phase installation.

3: Any other questions that I should be asking?

Thanks in advance!
35 to 45 may be good TODAY, but investing like this really demands looking 5 and 10 years down the road...
And YES, sizing a Jenny IS an art...
Chris.
Logged
Ya, Whatever. Just throw a '57 on it, and get off my stage.

Steve-White

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1593
  • Fort Worth
Re: Generator Education: Backup generators, Power factor, etc
« Reply #3 on: June 17, 2022, 01:54:05 PM »

John, 35-45kw is a fairly large genset.  However, without know detailed specs of both the recommended rig (as Frank stated) and your facility it's not possible to advise.

Do you have the load calculations they used in the recommendation/estimate?  I would want to look at the total load -vs- "Demand Factor" for the facility.

Also, power factor, demand factor and duty cycle are each unique things and not generally understood and often mixed together.

Not to in any way contradict what Frank said about "over-sizing" things.  That's the "safe" way out.  For instance, a manufacturer sizing generator capacity must account for altitude and operating environment ambient temperature averages and extremes.

Sizing a gas engine to drive a pump for a pressure washer comes to mind.  When the manufacturer (CAT Pumps in my case) publishes specs for horsepower requirements for a gasoline engine or electric motor they go WAY conservative.  Line voltage sags must be taken into consideration for electric motor sizing and altitude/.temperature - what racers measure as Density/Altitude to tune racing engines.  A 13-15HP gasoline engine running at 8000' or more above sea level will not perform like it does at 750' altitude or sea level.  They post specifications that will run everywhere reliably anywhere short of Mt. Everest if you will.  They don't even offer tables with ranges nor make mention of this.

So, what you're undertaking can be a pretty complex thing - simple, but many factors must be considered.

Running back-up generators on my house for the past 10+ years I've learned "just enough" isn't where I want to be - as any generator, the higher up the load curve it is operating, the more harmonic distortion there is in the output, which at some point will manifest as issues with electronics.

Battery backup - well that's certainly an option.  I run a combination of both.  Short term, all electronics are on APC UPS's, and for longer term outages which worst case have been 4-5 days during winter storms, the generators reign supreme.

I'd be tempted to have the wiring done and do some testing with rental portable rigs or have the contractor demonstrate various size generators to ensure proper capacity and not buying something you don't need.  There is a "Sweet Spot" that you want to find where budget and performance align.
Logged

Bill Meeks

  • Full Member
  • ***
  • Offline Offline
  • Posts: 244
  • Vidalia, Georgia - USA
Re: Generator Education: Backup generators, Power factor, etc
« Reply #4 on: June 17, 2022, 03:23:41 PM »

One reason for "oversizing" a genset is to provide reserve for large load spikes due to HVAC startups. When starting, a load like the compressor in typical residential and commercial heat pumps can draw very large current surges for a short time. If the generator set is not capable of supporting that, the frequency and voltage will sag considerably and the heat pump or other load with that startup in-rush current will fail to start.

Frank has a good point about not going way oversized, but you may not want to size based solely on steady-state loads if you want things like the heating and air conditioning to operate normally while on the generator. Your electrician and generator supplier have hopefully taken this into account when recommending a generator size.
Logged

Steve-White

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1593
  • Fort Worth
Re: Generator Education: Backup generators, Power factor, etc
« Reply #5 on: June 17, 2022, 06:56:55 PM »

^^^  Correct.  Especially if the loads are a mix of motors and electronics.  That being said, there is a sweet spot that needs to be found.  I've tried keeping electronics on separate inverter generator and main loads on conventional.  In the end, I just upsized the single main generator to handle both.

This is why I suggested some testing as running more generator than necessary is a waste of initial outlay and operating expenses.
Logged

Noah D Mitchell

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 358
Re: Generator Education: Backup generators, Power factor, etc
« Reply #6 on: June 20, 2022, 04:01:09 AM »

Thanks for all the great advice and input.


After digesting all of this and talking to another generator company, I think we're on the right track. The quoted setup is sufficient for everything running with a healthy amount of headroom, but not so much that we are 'overspec'd' by too much. We don't have to worry about startup things like AC, heaters, etc. thankfully.


Again, thanks for all the input. PSW is often the voice of reason.
Logged

Dave Garoutte

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3406
  • San Rafael, CA
Re: Generator Education: Backup generators, Power factor, etc
« Reply #7 on: June 20, 2022, 04:19:38 PM »


Again, thanks for all the input. PSW is often the voice of reason.

Often!!?? >:(
Logged
Nothing can be made idiot-proof; only idiot resistant.

Events.  Stage, PA, Lighting and Backline rentals.
Chauvet dealer.  Home of the Angler.
Inventor.  And now, Streaming Video!

Brian Jojade

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3422
    • HappyMac Digital Electronics
Re: Generator Education: Backup generators, Power factor, etc
« Reply #8 on: June 20, 2022, 10:49:10 PM »

If you are experiencing regular outages, a combination of battery and generator are a good idea.  Generators take time to spin up, and sudden changes in current draw sometimes aren't handled as well.

For battery banks, you can install large systems like the power wall, or multiple smaller systems on individual components.  The advantage of multiple smaller systems is you can prioritize what needs unstoppable power, but when you add up the maintenance cost for many units, you start to get to the cost of a full system.  Even with that, you can decide which circuits get power protection vs others by breaking up your circuits appropriately.
Logged
Brian Jojade

Noah D Mitchell

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 358
Re: Generator Education: Backup generators, Power factor, etc
« Reply #9 on: June 21, 2022, 12:10:08 AM »

If you are experiencing regular outages, a combination of battery and generator are a good idea.  Generators take time to spin up, and sudden changes in current draw sometimes aren't handled as well.

For battery banks, you can install large systems like the power wall, or multiple smaller systems on individual components.  The advantage of multiple smaller systems is you can prioritize what needs unstoppable power, but when you add up the maintenance cost for many units, you start to get to the cost of a full system.  Even with that, you can decide which circuits get power protection vs others by breaking up your circuits appropriately.


That is what we’ve got essentially. We have a collection of large and small battery units on crucial components, now just adding a ‘proper’ generator so we don’t have to wheel out the portable ones every day (then guard them) and put them away when we’re done.


Load shedding is such a common thing here that we’ve even got an app from the PoCo telling us when the next outage is coming.
Logged

Paul Johnson

  • Full Member
  • ***
  • Offline Offline
  • Posts: 157
  • Currently - Lowestoft - UK
Re: Generator Education: Backup generators, Power factor, etc
« Reply #10 on: June 21, 2022, 05:31:56 AM »

I suppose the real snag is what kinds of loads you have - the inductive ones, the resistive ones, and those that snatch chunks of the waveforms - the generators have real issues with some combinations. probably the best advice comes from the generator suppliers.Let them tell you if their product will be sufficient.
Logged

Frank Koenig

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1327
  • Palo Alto, CA USA
Re: Generator Education: Backup generators, Power factor, etc
« Reply #11 on: June 21, 2022, 10:04:12 AM »

If you are experiencing regular outages, a combination of battery and generator are a good idea.  Generators take time to spin up, and sudden changes in current draw sometimes aren't handled as well.

Agree that the battery-generator combo is ideal, especially if there are long periods with light loads such as (small) refrigeration, IT stuff and security systems that need to keep going when the facility is inactive. The next level is to get enough photovoltaics and storage so that you can give the generator the heave-ho and the PoCo the middle finger. I suppose the level after that is to generate enough that you can sell power to your neighbors as a microgrid  8)

--Frank