Author Topic: Inverter Generator link kit question - Neutral overload?  (Read 1650 times)
Jonathan Johnson
Re: Inverter Generator link kit question - Neutral overload?
« Reply #10 on: August 18, 2020, 01:34:10 pm »
On that particular link kit, it says "circuit breaker protected".  It is not clear of both receptacles are protected-but I would hope so, in which case even larger gennys would be safe.
The concern would be if you loaded 30 amps on one leg, and 30 amps on the other (and both legs were connected in parallel, not opposite legs of 120/240V service), that would add up to 60 amps on the neutral. If the legs are protected by 50A breakers (but the neutral has no breaker) there's no protection for the neutral and it could be overloaded.
Jonathan Johnson
« Reply #11 on: August 18, 2020, 01:45:57 pm »
For sake of not making assumptions, here's the schematic of the Firman* model 1201 paralleling kit. With respect to the NEMA 14-50R receptacle, the "hots" from the generators are tied together, then pass through a single-pole 50A breaker, then to both "hot" poles of the receptacle which are tied together.
This shows that you cannot overload the neutral, because the sum of the hot legs should not exceed the ampacity of the neutral. I do note, however, that it uses 10 AWG wire, which is usually rated at 30A -- though I understand in certain applications that can be acceptable for 50A. I am not qualified to judge if this is a valid application of that overrating.
https://www.firmanpowerequipment.com/shop/parallel-kit-50amp-1201/
*Note that is Firman, not the Furman we're familiar with.
« Last Edit: August 18, 2020, 10:19:59 pm by Jonathan Johnson »
Stephen Swaffer
« Reply #12 on: August 18, 2020, 10:11:55 pm »
10 AWG does seem undersized-but AWG is only part of what determines "ampacity"-the other is the temperature rating of its insulation-Type TFE lists an ampacity of 107 for #10.  Though I doubt they used that here-there are insulations that would allow 50A ampacity without damaging the wire-but they will run warmer than we are used to.  In my day job, I use a TGGT wire that has insane ampacity ratings-however when you derate for the ambient where it is used it is closer to what we expect.
Not trying to be arguementative-just pointing out that merely knowing the wire gauge doesn't tell me the safe OCPD.  The NEC (which mainly applies to installations) limits OCP for #10 to 30 amps with a fine print note-regardless of the actual ampacity otherwise indicated-but OCP is not the only thing determined by ampacity calcs.
Steve Swaffer
drew gandy
  • Chicago and burbs
« Reply #13 on: August 19, 2020, 12:40:23 pm »
I wish I had time to draw this out. My concern is not overloading the neutral in the generator or even the 'feeder' but various neutrals in the downstream distro. If it has 12ga neutrals for 20A circuits and you feed it from one of these generator setups, I think, you could conceivably put 30+ amps on that 12 ga neutral - inside your distro or subfeed from that panel.
For instance if you have a dual 20A breaker in your distro and out of that you feed 12/4 wire to a quad box (each duplex on it's own circuit) and you put 2 dimpacks on that quad box (one on each circuit) you can load that neutral with more than 20A of current. If you have a true 240V generator feeding this distro, the neutral will not see more than 20A current. As Tim said earlier, the neutral takes up the imbalance. Again, a drawering would really help. I'll see if I can find some time to scribble something up.
Secondly, while discussing the 'ampacity' of different ga wires, one of the big determiners is the heat dissipation capability. If you bundle the wires together in a service cord then the 'ampacity' is supposed to be derated because the heat dissipation is significantly less than for loose conductors of the same size.
You know, just to confuse things even more.
Thanks btw for finding that 'Fireman' schematic.  ;D
Now I know for sure that some of these are simply paralleled together.
Arrogance is usually far worse than ignorance. But every once in awhile they swap places.
« Reply #14 on: August 19, 2020, 04:11:24 pm »
Where's Sokol?
Stephen Swaffer
« Reply #15 on: August 20, 2020, 10:58:41 pm »
Drew,
You are correct in thinking that could overload a neutral.  More than once I have come across "multiwire branch circuits"-the NEC term for shared neutrals that are fed off the same phase becasue someone did not understand what was hapening when they re-arrranged breakers.
I would also question if the neutral could be overloaded if your example quad box was used on a 3 phase system where harmonics could be present and the 2 phases are not 180 opposed.
The safe way would be a five wire cable with dedicated neutrals.  Of course, then you have 4 current carrying conductors instead of 2 (a neutral is ignored if it is only carrying unbalanced current)-which ususally gts you into the derating you mentioned.  Of course, the derating is done from the actual ampacity rating of the conductor-not the maximum breaker size specified by the Fine Print Note for small wires.
Steve Swaffer
Mike Sokol
« Reply #16 on: August 23, 2020, 07:36:41 am »
That's why those parallel kits are only available for smaller 2,000 to 3,000 watt inverter generators. Yes, they do parallel the outputs and can only make 120 volts. And yes, the neutral current will be additive rather than subtractive as they would be in a split-phase 120/240-volt service. But as others have mentioned there's not enough combined amperage with these small generator to overload the neutral conductor. That's why a pair of 2,000 watt generators in parallel can use a 30-amp twist=lock or TT-30 connector, and a pair of 3,000 watt generators in parallel can use a 14-50 receptacle. Be aware that these parallel capable inverter generators are not neutral-ground bonded which can make some amps and stage gear operate erratically or not at all. In that case you'll want to use a neutral bonding plug to create a bonded neutral for your stage power.
So I've been doing a little research on the multitude of 2000w range inverter generators on the market now. (Storm came across and wiped out power to a lot of homes a few days ago).
It seems that the link kits for these do NOT allow for 240v but instead for higher current at 120v. But, some of them appear to provide this power on 240V style connectors - apparently putting the same 'phase' on both hot terminals. These seem to be aimed at RV usage. But I'm having a hard time understanding how this won't lead to overloaded neutrals in systems where the neutrals are shared which is very common with 240v "split phase" power.
What am I missing here?
Mike Sokol
mike@noshockzone.org
www.NoShockZone.org
« Reply #17 on: August 23, 2020, 11:38:48 am »
Drew... it took a little longer for your 'bigger question' to sink in with me.   ::)
Yes, in a multi-wire branch circuit one could overload the neutral of the branch circuit using this kind of "service".  The generator combiner is safe for the reasons Mike & I pointed out but that's a narrower view of your question.
Powering a distro would be dicey depending on how subsequent wiring and loading was done.
You pointed out another reason why combining small, portable generators can be considered a kludge; for some applications (like powering campers and RVs that don't have multi-wire branch circuits or genuine 240V loads) they'll work as intended, for others... there are complications.
« Last Edit: August 23, 2020, 11:41:11 am by Tim McCulloch »
Rob Spence
  • Boston Metro North/West
    • Lynx Audio Services
« Reply #18 on: August 24, 2020, 10:21:28 pm »
Hey Mike. Nice to hear from you!
Page created in 0.03 seconds with 23 queries.