ProSoundWeb Community

Please login or register.

Login with username, password and session length
Advanced search  

Pages: 1 2 3 [4]   Go Down

Author Topic: 3 (Three) Phase Distro tied into single phase (split-phase) supply  (Read 8704 times)

Jonathan Johnson

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3210
  • Southwest Washington (state, not DC)
Re: Fully power 3 phase distro on single phase power?
« Reply #30 on: December 10, 2019, 01:41:25 AM »

The reason for not tying the neutrals together at the load end is because, unless they are very closely matched in resistance, any imbalance in resistance will result in a current imbalance, which could result in one of the neutrals being overloaded.

And, in a camlock setup, if one of the neutral cams should become disconnected, the other neutral could be overloaded.
Logged