Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2245
Re: line clearence
« Reply #10 on: October 31, 2019, 07:16:58 pm »

On resi, it is common to use a reduced size neutral-but most of the heavy loads in resi-oven/ac/water heater etc. are 220 which means they don't load the neutral ever.

A big reason for the limits on wiring over a roof is clearance for first responders/fire personnel.

Logged
Steve Swaffer

Frank Koenig

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 864
Re: line clearence
« Reply #11 on: November 01, 2019, 01:00:46 pm »

On resi, it is common to use a reduced size neutral-but most of the heavy loads in resi-oven/ac/water heater etc. are 220 which means they don't load the neutral ever.

That's interesting. I haven't seen that around here. All my neutrals, including the service drops/laterals put in by the POCO, are full-size. (These days I doubt PG&E is going to take any chances with anything given the extremely deep do do they're in.)

With respect to under sizing things, what strikes me is how much smaller the distribution transformer ratings are than the potential maximum load based on (downstream) overcurrent protection. My barn in the Foothills has 200 A service which, at 80% load, could draw 38.4 kVA. The pole pig is rated at 15 kVA. I guess the transformers have pretty long thermal time constants and the POCO doesn't expect homeowners to be refining aluminum full time.

--Frank
Logged
"Nature abhors a vacuum tube." -- John Pierce, Bell Labs

Tim McCulloch

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 20458
  • Wichita, Kansas USA
Re: line clearence
« Reply #12 on: November 01, 2019, 01:15:01 pm »

That's interesting. I haven't seen that around here. All my neutrals, including the service drops/laterals put in by the POCO, are full-size. (These days I doubt PG&E is going to take any chances with anything given the extremely deep do do they're in.)

With respect to under sizing things, what strikes me is how much smaller the distribution transformer ratings are than the potential maximum load based on (downstream) overcurrent protection. My barn in the Foothills has 200 A service which, at 80% load, could draw 38.4 kVA. The pole pig is rated at 15 kVA. I guess the transformers have pretty long thermal time constants and the POCO doesn't expect homeowners to be refining aluminum full time.

--Frank

I spent 4 years trying to convince my PoCo they had a bad neutral connection in the drops (note the plural) from a transformer cluster.  They figured it out when the lawyer NastyGrams arrived.  They fixed the neutral and while the crew was there I pointed out that one of the phase leg transformers had started to puke its guts out.  Three months later they were back replacing the transformer that exploded and showered a neighboring business owner's car with PCB-laden cooling oil.

I have a pretty low regard for PoCo managers.  They simple assume that customers don't know shit about electricity distribution (and sure, most don't) but when you can speak their language and describe happenings in terms of volts and amperes you'd think the tendency to instantly reject a customer's observations would lower somewhat.  Nope, it takes losing power to a commercial block, swinging voltages and destroyed appliances and equipment (with the ensuing threats of lawsuits) to get them to believe you.
Logged
"Practicing an art, no matter how well or badly, is a way to make your soul grow, for heaven's sake. Sing in the shower. Dance to the radio. Tell stories. Write a poem to a friend, even a lousy poem. Do it as well as you possible can. You will get an enormous reward. You will have created something."  - Kurt Vonnegut

John Roberts {JR}

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 16397
  • Hickory, Mississippi, USA
    • Resotune
Re: line clearence
« Reply #13 on: November 01, 2019, 01:47:57 pm »

I spent 4 years trying to convince my PoCo they had a bad neutral connection in the drops (note the plural) from a transformer cluster.  They figured it out when the lawyer NastyGrams arrived.  They fixed the neutral and while the crew was there I pointed out that one of the phase leg transformers had started to puke its guts out.  Three months later they were back replacing the transformer that exploded and showered a neighboring business owner's car with PCB-laden cooling oil.

I have a pretty low regard for PoCo managers.  They simple assume that customers don't know shit about electricity distribution (and sure, most don't) but when you can speak their language and describe happenings in terms of volts and amperes you'd think the tendency to instantly reject a customer's observations would lower somewhat.  Nope, it takes losing power to a commercial block, swinging voltages and destroyed appliances and equipment (with the ensuing threats of lawsuits) to get them to believe you.
+1

I recall years ago calling my power company when my mains voltage was high and climbing higher one night.  :o

The service guy was convinced that I was mistaken but it was a slow night so he drove out to my house with his big a__ poco truck, to prove me wrong..... BUT I wasn't wrong.  8)

Then he said wait a minute while he drove up the road to the substation a mile away, where the bump auto-former was stuck on boost. As more of my neighbors shut down for the night who knows how high the mains could have climbed as more load dropped off? He probably used some percussive maintenance (hammer) to free the stuck auto-former actuator.

He didn't even say thank you, but I probably saved them from some burned up residential appliance claims.

JR

 
Logged
Don't tune your drums half-ass. Listen to what a properly "cleared" drum sounds like.   http://circularscience.com/

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2245
Re: line clearence
« Reply #14 on: November 01, 2019, 06:44:44 pm »

That's interesting. I haven't seen that around here. All my neutrals, including the service drops/laterals put in by the POCO, are full-size. (These days I doubt PG&E is going to take any chances with anything given the extremely deep do do they're in.)

With respect to under sizing things, what strikes me is how much smaller the distribution transformer ratings are than the potential maximum load based on (downstream) overcurrent protection. My barn in the Foothills has 200 A service which, at 80% load, could draw 38.4 kVA. The pole pig is rated at 15 kVA. I guess the transformers have pretty long thermal time constants and the POCO doesn't expect homeowners to be refining aluminum full time.

--Frank

The building my office is in has a 3000 amp/3 phase/480 volt service that I installed about 9 years ago.  The NEC requires 8 parallel runs of 500 mcm copper to meet that ampacity.  Base on their interpretation of the expected load, they ran 4 parallel runs of 500 mcm aluminum.  Since then, our load has increased-regularly drawing 1500 amps plus for long perios\ds of times-but the poco hasn't seen fit to use the other 4 runs of 5 inch pvc conduit they required me to install.

I suspect their attitude towards transformers is that if its overloaded they could replace it-but they would likely scrap the old one-so why not run the old one until it lets the smoke out?
Logged
Steve Swaffer

Frank Koenig

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 864
Re: line clearence
« Reply #15 on: November 02, 2019, 12:00:30 pm »

+1

I recall years ago calling my power company when my mains voltage was high and climbing higher one night.  :o

The service guy was convinced that I was mistaken but it was a slow night so he drove out to my house with his big a__ poco truck, to prove me wrong..... BUT I wasn't wrong.  8)

Then he said wait a minute while he drove up the road to the substation a mile away, where the bump auto-former was stuck on boost. As more of my neighbors shut down for the night who knows how high the mains could have climbed as more load dropped off? He probably used some percussive maintenance (hammer) to free the stuck auto-former actuator.

He didn't even say thank you, but I probably saved them from some burned up residential appliance claims.

JR

I had something very similar happen within the last year. At the Sierra Foothills place we have a little home-brew (Raspberry Pi based) telemetry system that monitors line voltage, among many other things. We have a text message alarm set at 130 V. One day I'm down in Palo Alto and my phone dings and sure enough the voltage is up around 138 or something. I knew it was real as we have a second monitor at another building that agreed. I call PG&E's main trouble number and try to explain the situation. The dispatcher had no idea what I was talking about (people frequently have no idea what I'm talking about, but we're not here to talk about that) but we came to an agreement to treat it as an outage and they sent out a truck.

About 2 hours later I get a call from the fellow on the truck (PG&E had, to their credit, successfully relayed my number to him) who acknowledged that the voltage was high (and rising :o ) and thanked me profusely.  I never found out what the cause was but in this case, apparently, a customer's monitoring had saved PG&E from a big problem. None of our stuff smoked, thankfully.

--Frank
Logged
"Nature abhors a vacuum tube." -- John Pierce, Bell Labs

John Roberts {JR}

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 16397
  • Hickory, Mississippi, USA
    • Resotune
Re: line clearence
« Reply #16 on: November 02, 2019, 12:31:35 pm »

I had something very similar happen within the last year. At the Sierra Foothills place we have a little home-brew (Raspberry Pi based) telemetry system that monitors line voltage, among many other things. We have a text message alarm set at 130 V. One day I'm down in Palo Alto and my phone dings and sure enough the voltage is up around 138 or something. I knew it was real as we have a second monitor at another building that agreed. I call PG&E's main trouble number and try to explain the situation. The dispatcher had no idea what I was talking about (people frequently have no idea what I'm talking about, but we're not here to talk about that) but we came to an agreement to treat it as an outage and they sent out a truck.

About 2 hours later I get a call from the fellow on the truck (PG&E had, to their credit, successfully relayed my number to him) who acknowledged that the voltage was high (and rising :o ) and thanked me profusely.  I never found out what the cause was but in this case, apparently, a customer's monitoring had saved PG&E from a big problem. None of our stuff smoked, thankfully.

--Frank
Probably same technology... a stuck auto former used to bump line voltage up/down to manage changing load locally. 

At least you got a thank you... 8)  Customers are unlikely to even recognize too much voltage. I noticed that my incandescent lights were brighter than I remembered. I suspect long term memory for brightness is as challenged as long term memory for loudness. So these were pretty bright.

JR

PS: FWIW that same substation looks like it now has monitoring instrumentation on high voltage lines leaving the sub-station in three directions, so they might be able to catch future events themselves.
Logged