Pages: 1 ... 3 4 [5] 6 7   Go Down
Author Topic: Generator suggestions  (Read 3848 times)
Tim Hite
    • Bad Quail
Re: Generator suggestions
« Reply #40 on: June 28, 2019, 05:33:05 pm »
Capacity balancing is always tricky on the diesel gensets. If the genset is too small you get power fluctuations and if it's too big you get wet stacking. It's even tougher to get it right with nothing but a sound system for a load, since you're be expected to be running 1/8 power or less most of the time with dynamics up to 9/10 power.
I generally go one step up in generator size from my max rated amplifier load, but I'm sure there's a better way to do the selection.
I find that too many times a too small generator is used. They figure they only use 3000 watts so a 3500 watt unit should work when they really need a much larger one to deal with the dynamic load.
Bad Quail
Sound + Light
Joshua Tree, California
Dave Guilford
« Reply #41 on: June 29, 2019, 07:34:11 pm »
Just a follow up.  I selected a MQ7000 tow behind generator and expect to pick it up after the 4th of July.
Iíll have to get a distro and some of that 50a California feeder.  Ug.
« Reply #42 on: June 30, 2019, 05:12:26 am »
Great choice.  Give us a full report please.
Frank Koenig
« Reply #43 on: June 30, 2019, 11:13:14 am »
Agree -- great choice. It looks like the output overcurrent protection on that model is 30 A so you would only need a 30 A feeder unless you also want to use it with larger generators or "stove plug" line power. It could save a bit of weight (and cost). --Frank
Dave Guilford
« Reply #44 on: June 30, 2019, 12:26:09 pm »
Unsure what means
Frank Koenig
« Reply #45 on: June 30, 2019, 12:39:45 pm »
Unsure what means
The feeder cable and downstream distribution need only be sized for the maximum current available from the source. If the source is a 7 kVA generator fitted with 30 A overcurrent protection, as I believe is the case here, then the feeder only needs to be able to handle (and be rated for) 30 A so you can use a smaller wire size and appropriate connectors, NEMA L14-30 in this instance. If you also want to use this same feeder with sources where the current may be as large as 50 A, then you need the 50 A feeder cable with the Cali connectors and adapters to go with your generator.
By the way, did you get the mechanical governor (+/- 5%) or plump for the electronic frequency control (+/- .25%)?
--Frank
Tim Hite
    • Bad Quail
« Reply #46 on: June 30, 2019, 02:09:01 pm »
--Frank
Upholstered in rich, Corinthian leather, no doubt. . .
Bad Quail
Sound + Light
Dave Guilford
« Reply #47 on: June 30, 2019, 11:40:13 pm »
--Frank
Somewhere earlier it was mentioned that the 50a 240v California connector was essentially turning that into 100a at 120v.
Why,  on this mq7000, wouldnít the 25a 240 California connectors deliver 50a at 120?
This generator specifies that it can make 50a at 120v.  Thatís what I need - how do I pull all avail power with this genny?
« Reply #48 on: July 01, 2019, 09:11:20 am »
The connector does not magically "turn" anything into anything.  It's a connector for a 120/240v service.  This service implies that it's a 240v center-tapped circuit so you get 120v from neutral to either hot leg or 240v from hot to hot.  The total available current does not change.
Each hot leg is 30 amps, limited by the circuit breaker, and note that a breaker of that rating is on both the Cali connector and the L14-30.
Tim Hite
    • Bad Quail
« Reply #49 on: July 01, 2019, 11:58:19 am »
The unit you selected will supply 30 amps at 240 volts, so according to the power law:
30A*240V=7200W
You need a bigger generator. Probably something like 15kW, which is the next size up.
50A*240V=12000W
VxA=P
This ties in to my earlier post about sizing your genset correctly, since you need to be pulling a >40% constant load to avoid wet stacking.
You should really really talk to a generator pro to help you get it right.
Bad Quail
Sound + Light
¬ę Reply #49 on: July 01, 2019, 11:58:19 am ¬Ľ
Pages: 1 ... 3 4 [5] 6 7   Go Up
Page created in 0.061 seconds with 23 queries.
