Author Topic: Portable Power Cabling Size  (Read 2320 times)

Kristian Stevenson

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 94
  • Lynchburg, VA
Portable Power Cabling Size
« on: May 20, 2019, 08:35:03 PM »

I'm about to pull the trigger on some 5 conductor cabling to build L21-30 Amp Rack cables. We have one regular setup that dictates the racks be 100' from the PD. What size cable would be acceptable for this use case? I was considering 10/5 SOOW but the voltage drop is a little over 4%.

Would you consider this acceptable? I've read anywhere from 3 to 5% voltage drop is OK (depending on where you read it).
« Last Edit: May 20, 2019, 10:37:57 PM by Kristian Stevenson »
Logged
Kristian Stevenson

Tim McCulloch

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 23783
  • Wichita, Kansas USA
Re: Portable Power Cbaling Size
« Reply #1 on: May 20, 2019, 08:40:12 PM »

Back in the days of large frame analog consoles I used 8/5 for the 250' FOH run because of voltage drop.  We still use that cable and now I can power a small resistance heater for those OctoberFest gigs so my FOH guys don't freeze solid.
Logged
"If you're passing on your way, from Palm Springs to L.A., Give a wave to good ol' Dave, Say hello to progress and goodbye to the Moonlight Motor Inn." - Steve Spurgin, Moonlight Motor Inn

Matthew Knischewsky

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 647
  • Kitchener Ontario Canada
Re: Portable Power Cabling Size
« Reply #2 on: May 20, 2019, 11:40:35 PM »

I'm about to pull the trigger on some 5 conductor cabling to build L21-30 Amp Rack cables. We have one regular setup that dictates the racks be 100' from the PD. What size cable would be acceptable for this use case? I was considering 10/5 SOOW but the voltage drop is a little over 4%.

Would you consider this acceptable? I've read anywhere from 3 to 5% voltage drop is OK (depending on where you read it).

10/5 is fairly standard for L21-30 cables. What's really going to make the difference is the amplifiers in the rack, their loading and how sensitive they are to voltage drop. For example, I've regularly used Crown V racks fed by 100' (and over) of 10/5, no problems with under voltage. Some earlier versions of lightweight amplifiers were not as forgiving.

Voltage drop is usually calculated with a fixed resistive load. Audio loads are not as simple to calculate.
Logged

Tim McCulloch

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 23783
  • Wichita, Kansas USA
Re: Portable Power Cabling Size
« Reply #3 on: May 21, 2019, 12:15:34 AM »

10/5 is fairly standard for L21-30 cables. What's really going to make the difference is the amplifiers in the rack, their loading and how sensitive they are to voltage drop. For example, I've regularly used Crown V racks fed by 100' (and over) of 10/5, no problems with under voltage. Some earlier versions of lightweight amplifiers were not as forgiving.

Voltage drop is usually calculated with a fixed resistive load. Audio loads are not as simple to calculate.

Back in the day of large filter capacitors it was easier to get a grip on current v/ duty cycle.  With Class D amps, not so convenient.

Since I also work as a stage hand I get to see what the big boys use; I haven't noticed anything that looked or felt unusual so haven't paid attention to the markings.  I'll start looking closer.
Logged
"If you're passing on your way, from Palm Springs to L.A., Give a wave to good ol' Dave, Say hello to progress and goodbye to the Moonlight Motor Inn." - Steve Spurgin, Moonlight Motor Inn

Brian Bolly

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 672
  • DC/Baltimore and other Major Airports
Re: Portable Power Cabling Size
« Reply #4 on: May 21, 2019, 06:06:32 AM »

I believe with 5 conductors in the jacket for 30A (L21-30) you need to be on 8/5, but I don't have my copy of the NEC handbook readily available.  Anybody have one handy?
Logged

Erik Jerde

  • Classic LAB
  • Hero Member
  • *
  • Offline Offline
  • Posts: 1400
Re: Portable Power Cabling Size
« Reply #5 on: May 21, 2019, 10:53:06 AM »

It really depends on current draw of the rack.  10ga at 100’ is about 5% drop at 30 amps of draw.  If you’re only drawing 20A you’ve got 3.5% drop.  If you want to be able to pull a full 30A at 100’ and stay at 3% or under then you need 6ga.

The other consideration is if your chosen cable will fit in the connector if you go for larger cables.
Logged

David Haulman

  • Newbie
  • *
  • Offline Offline
  • Posts: 44
  • Brunswick;Ga.
Re: Portable Power Cabling Size
« Reply #6 on: June 07, 2019, 09:30:46 PM »

You have more than 3 current carrying conductors. You will have to derate the 10-5. I think its 40 percent. Not Sure though.
Logged

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2673
Re: Portable Power Cabling Size
« Reply #7 on: June 07, 2019, 10:07:22 PM »

#10 SO cable has an ampacity of 25 amps when there are 3 current carrying conductors.  The neutral only counts if more than 50% of the load is non-linear.  If that is the case, then for 4 current carrying conductors the amapcity is 80% of 25-or 20 amps.

NEC reference is 400.5.
Logged
Steve Swaffer

Kevin Graf

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 344
Re: Portable Power Cabling Size
« Reply #8 on: June 13, 2019, 06:31:52 PM »

Two things to consider:
1] Most Class "D" amplifiers have a SMPS (power supply). A SMPS doesn't much care what the line voltage is, they are self adjusting.
2] The ampacity rating of a cable is for 3 hour continuous current. So unless you are doing full power tone testing, the average power of real audio signals is much less.
Logged
Speedskater

ProSoundWeb Community

Re: Portable Power Cabling Size
« Reply #8 on: June 13, 2019, 06:31:52 PM »