Inverter generator strangeness
« on: April 07, 2019, 11:13:49 pm »

Had a wedding over the weekend and the groom provided an EU3000 Honda generator from our local (reliable) generator company. When I fired it up and ran a load tester on it, the CT70 was showing red and the H and N terminal lights were flipping back and forth. I've not sen anything like it.

Called the generator company tech and they said they've never had a problem powering stuff with the unit. I borrowed a small light from the photographer and plugged it in and nothing bad happened. I ran sound and some HID light fixtures for the evening and everything was fine.

Any guesses as to what was going on there?

CT70 was showing 127VAC with polarity swapping back and forth from H to N. H to G showed .7VAC, no GFCI to test in at the generator.
Logged
Bad Quail
Sound + Light
Joshua Tree, California
Authorized Dealers for all this stuff

Art Welter

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1576
Re: Inverter generator strangeness
« Reply #1 on: April 08, 2019, 12:10:52 am »

When I fired it up and ran a load tester on it, the CT70 was showing red and the H and N terminal lights were flipping back and forth. I've not sen anything like it.

Any guesses as to what was going on there?

CT70 was showing 127VAC with polarity swapping back and forth from H to N. H to G showed .7VAC, no GFCI to test in at the generator.
Tim,

From your description and partial reading of the Extech CT 70 manual, sounds like no earth ground and a H/N reversal.
Someone may have wired the receptacle backwards after replacement.
H/N reversal does not cause a problem "powering stuff", but is a safety concern with certain gear configurations and should be corrected.

Art
« Last Edit: April 08, 2019, 12:27:29 am by Art Welter »
Logged

TJ (Tom) Cornish

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4283
  • St. Paul, MN
Re: Inverter generator strangeness
« Reply #2 on: April 08, 2019, 08:10:45 am »

Had a wedding over the weekend and the groom provided an EU3000 Honda generator from our local (reliable) generator company. When I fired it up and ran a load tester on it, the CT70 was showing red and the H and N terminal lights were flipping back and forth. I've not sen anything like it.

Called the generator company tech and they said they've never had a problem powering stuff with the unit. I borrowed a small light from the photographer and plugged it in and nothing bad happened. I ran sound and some HID light fixtures for the evening and everything was fine.

Any guesses as to what was going on there?

CT70 was showing 127VAC with polarity swapping back and forth from H to N. H to G showed .7VAC, no GFCI to test in at the generator.
I believe this is normal behavior of the single-phase EU series generators.  They provide quasi-balanced power to the frame via capacitor coupling: 60v hot to frame and 60v frame to neutral .  There is no ground of any consequence on these generators - both hot and neutral are floating such that if you short either hot or neutral to the frame, there is no fault current path to trip a breaker.  You are supposed to ground the generator frame to the earth via a ground rod (rarely done in practice), but even if you do that, the CT-70 will not read a ground path, as it is trying to put a load between hot and ground for testing, which it sees as an open circuit (which it is other than the coupling capacitors).

We've discussed these generators extensively going back a few years.  In a building, shock prevention depends on ground -> neutral bonds, GFCIs, and over-current protection devices.  In single-phase isolated power scenarios like this, a different thought process is used - if the power source is totally floating, even if you have a single fault - i.e. hot to ground, in practice nothing happens as there is no fault current path unless you also contact the other current-carrying wire; which ultimately boils down to the same safety as a traditional wiring system - if you touch both hot and neutral even in a fully code-compliant electrical system, you're going to get shocked.

TLDR - your generator is fine; the CT-70 just doesn't know what to do with a different wiring and safety scheme.

Logged

Tim Hite

  • Hero Member
  • *****
  • Online Online
  • Posts: 714
    • Bad Quail
Re: Inverter generator strangeness
« Reply #3 on: April 08, 2019, 11:21:33 am »

Thanks Tom.

Art, this definitely wasn't a H/N reverse polarity situation. The indicator light was moving back and forth between hot and neutral. In an RP situation, the indicator lights for polarity would be unchanging.
Logged
Bad Quail
Sound + Light
Joshua Tree, California
Authorized Dealers for all this stuff

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3356
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: Inverter generator strangeness
« Reply #4 on: April 08, 2019, 04:53:26 pm »

Thanks Tom.

Art, this definitely wasn't a H/N reverse polarity situation. The indicator light was moving back and forth between hot and neutral. In an RP situation, the indicator lights for polarity would be unchanging.

I've written about this issue extensively for the RV industry, and even created a video showing how to correct it using a simple G-N generator bonding plug. Here's my latest article: https://www.rvtravel.com/rv-electricity-generator-neutral-bonding-basics/
Logged
Mike Sokol
mike@noshockzone.org
www.NoShockZone.org

Tim Hite

  • Hero Member
  • *****
  • Online Online
  • Posts: 714
    • Bad Quail
Re: Inverter generator strangeness
« Reply #5 on: April 09, 2019, 11:15:22 am »

Thanks Mike, figured you'd covered this already. Just didn't recognize the strange error condition.
Logged
Bad Quail
Sound + Light
Joshua Tree, California
Authorized Dealers for all this stuff

Jeff Robinson

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 76
  • Kansas City, MO
Re: Inverter generator strangeness
« Reply #6 on: April 22, 2019, 12:57:56 pm »

Had a wedding over the weekend and the groom provided an EU3000 Honda generator from our local (reliable) generator company. When I fired it up and ran a load tester on it, the CT70 was showing red and the H and N terminal lights were flipping back and forth. I've not sen anything like it.

Called the generator company tech and they said they've never had a problem powering stuff with the unit. I borrowed a small light from the photographer and plugged it in and nothing bad happened. I ran sound and some HID light fixtures for the evening and everything was fine.

Any guesses as to what was going on there?

CT70 was showing 127VAC with polarity swapping back and forth from H to N. H to G showed .7VAC, no GFCI to test in at the generator.

What we have here is a 'separately derived' source. See NFPA 70 (the code) 250.20(D), 250.30 and 250.104(D) per the index of my 2005 copy.

250.30(A)(1) states: System Bonding Jumper. An unspliced system bonding jumper … shall be used to connect the equipment grounding conductors of the separately derived system to the grounded conductor. …
See: https://www.ecmweb.com/code-basics/grounding-and-bonding-separately-derived-systems

Ths applies to both generators and transformers (necessary for OCDs to trip when a short circuit occurs). Bonding elsewhere (other than the service entrance) will cause GFCI/RCD devices to trip unnecessarily because of circulating currents due to voltage buildup in the current carrying neutral.

If the generator is the only source, also see articles 520, 525-IV, 525.30, 31 & 32

Two weeks ago I installed a transformer on a 240V circuit (no neutral was pulled to the convenient attic fan source that has not been used in decades) to power a 120V load and the other end of the MC line fed a duplex in a metal box (not installed by me) and the hot terminal touched the grounded metal box, causing the fuse I added to the transformer to blow, because I bonded the secondary, per code, preventing the box from becoming hot, I did ground the circuit as well.

HTH, FYI, ETC. (If you need the difference between grounded and grounding explained, you are not qualified.)

Edit: adding link about balanced (symmetrical) technical power (+/- 60V)
http://paul-lehrman.com/S2N/Articles/PowerGrounding.html
I use this to feed my home theater rack because it reduces both video and audio noise floors.

Jeff Robinson
« Last Edit: April 22, 2019, 01:45:07 pm by Jeff Robinson »
Logged
Excerpt from Shelley's 'Ode to a Skylark':
__________________________________
Hail to thee, blithe Spirit!
Bird thou never wert
That from Heaven, or near it
Pourest thy full heart
In profuse strains of unpremeditated art
...
Such harmonious madness
From my lips would flow
The world should listen then, as I am listening now!

ProSoundWeb Community

Re: Inverter generator strangeness
« Reply #6 on: April 22, 2019, 12:57:56 pm »


Pages: [1]   Go Up
 



Page created in 0.122 seconds with 24 queries.