Accepted types of cable jackets for power/signal
« on: January 04, 2019, 11:15:24 AM »

Our outfit has reached a stage (no pun intended) where we will be rapidly phasing out our remaining "orange stuff" for basic power needs along with auditing the rest of our cabling inventory to be sure we're up to code.
Really the two areas that this will affect are AC power and speakon as our XLR is all whirlwind (apart from a few patch cables that will never leave a rack) which I would assume is up to code already. In my searches it seems that SOOW and SJOOW are the two jacket types mentioned the most, and our second-hand AC cables we got from a retired local is a mixture of both types with a couple SEOOW mixed in, all with hubbell hardware.
Is it safe to assume that using any of the above jacket types is fine so long as the conductors are properly rated for the loads they'll be receiving? I know STOOW and SEOOW are other common jacket types but don't know where they fall under service types since I'm not a NEC master. Finding the handful of SEOOW cables is what prompted my concern though it seems it's fine based on a few searches here.
Thanks!
Logged
There are two ways to do anything:
1) Do it right
2) Do it over until you do it right

TJ (Tom) Cornish

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4317
  • St. Paul, MN
Re: Accepted types of cable jackets for power/signal
« Reply #1 on: January 04, 2019, 11:25:40 AM »

Our outfit has reached a stage (no pun intended) where we will be rapidly phasing out our remaining "orange stuff" for basic power needs along with auditing the rest of our cabling inventory to be sure we're up to code.
Really the two areas that this will affect are AC power and speakon as our XLR is all whirlwind (apart from a few patch cables that will never leave a rack) which I would assume is up to code already. In my searches it seems that SOOW and SJOOW are the two jacket types mentioned the most, and our second-hand AC cables we got from a retired local is a mixture of both types with a couple SEOOW mixed in, all with hubbell hardware.
Is it safe to assume that using any of the above jacket types is fine so long as the conductors are properly rated for the loads they'll be receiving? I know STOOW and SEOOW are other common jacket types but don't know where they fall under service types since I'm not a NEC master. Finding the handful of SEOOW cables is what prompted my concern though it seems it's fine based on a few searches here.
Thanks!
The "J" series cables are listed as "junior hard service" and are not allowed for stage use due to the concern of physical damage to the cable leading to injury or fire.  Extra hard service cable - either SOOW or SEOOW - is required for this usage.  There are a number of exemptions in the NEC that allow "J" series cords in some circumstances such as when the cables are protected from physical damage and for short cables, etc.

Whether any of this is relevant to you probably is probably determined by your local inspector, should you ever encounter him/her.  Considering most of the hotels and conference centers I work with commonly use 18-ga orange cords plugged into 100A or more panelboards fed over #4 wire from an illegal plug series (e.g. using NEMA 15-series 3-phase 4 wire plugs with no neutral), I suspect you're unlikely to have any show-stopping interaction from the inspector with SJOOW cables, but rating is important.  Use #12 wire for everything and maintain your inventory so any cords that get damaged get pulled out of service.

Edit - also, speaker cables and other signal wiring are unlikely to reach the eye of the inspector.  Even though today's high-power amps can produce voltage similar to or higher than 120V mains power (an amp that can do 4000 watts into 8Ω puts out almost 180 volts), they aren't handled the same way as mains wiring.  I've never seen anyone use SOOW cord for speaker wire, and it likely wouldn't fit into the connectors you want to use anyway.
« Last Edit: January 04, 2019, 11:33:10 AM by TJ (Tom) Cornish »
Logged

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2671
Re: Accepted types of cable jackets for power/signal
« Reply #2 on: January 04, 2019, 12:43:35 PM »

Note 7 to table 400.4 lists  types:  G,GC,S,SC,SCE,SCT,SE,SEO,SEOO,SEW,SEOW,SEOOW,SO,SOO,SOW,SOOW,ST,STO,STOO,STW,STOW,STOOW,PPE and W as being acceptable on theater stages.  Types ending in W are suitable for wet loctions-so if ever outdoors probably a good idea to use those.
Logged
Steve Swaffer

Taylor Hall

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 869
Re: Accepted types of cable jackets for power/signal
« Reply #3 on: January 04, 2019, 12:49:41 PM »

Gotcha, the J-rated cables are actually 15ft, so I guess they were made with the short runs in mind where they wouldn't see any traffic like you mentioned in the NEC exemptions. We also made prolific use of cable covers and such to keep things out of reach wherever possible, and even our "orange" cables were black so they were unlikely to draw much attention.

We've never had anyone raise concerns about our current stock of cables, but that doesn't mean it won't happen. We're starting to work with a lot more convention centers and large hotels where we've observed in-house service providers "supervising" from a distance or not-so-casually inspecting what equipment we have while "passing through" the space. Probably just me being hyper-critical of everything I see, but I'm not about to take any chances if I can help it.

Thanks again for the input, guys.
Logged
There are two ways to do anything:
1) Do it right
2) Do it over until you do it right

Jeff Lelko

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2012
  • Cape Canaveral, FL
Re: Accepted types of cable jackets for power/signal
« Reply #4 on: January 04, 2019, 01:16:59 PM »

Hi Taylor, while you're at it you might want to think about building a proper set of power distro gear and not just code-compliant extension cords.  I know we have a number of threads here about stringers and Powercon boxes, so plenty of resources to reference.  I'm a big user of the OA Windsor boxes but there are others on the market too.  The cost is reasonable and if properly thought out ahead of time will give you endless options for getting power where you need it.  Hope this helps!
Logged

TJ (Tom) Cornish

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4317
  • St. Paul, MN
Re: Accepted types of cable jackets for power/signal
« Reply #5 on: January 04, 2019, 01:22:06 PM »

Hi Taylor, while you're at it you might want to think about building a proper set of power distro gear and not just code-compliant extension cords.  I know we have a number of threads here about stringers and Powercon boxes, so plenty of resources to reference.  I'm a big user of the OA Windsor boxes but there are others on the market too.  The cost is reasonable and if properly thought out ahead of time will give you endless options for getting power where you need it.  Hope this helps!
I agree that building cords and stringers is fine for the OP and others (tip - SO/SJ type cord is unidirectional - match up the screw layout of the plugs to the natural twist of the wire.  If you have to cross over, you've got the male/female plugs reversed), however it doesn't really make sense for end users to build distro gear.  This is specifically prohibited by the NEC2017, and isn't really cost effective anyway.  Construction-grade spider boxes are very inexpensive, and if you need a different or larger config than that, Motion Labs/Whirlwind/etc. are your legal options that are reasonably cost effective.
Logged

Jeff Lelko

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2012
  • Cape Canaveral, FL
Re: Accepted types of cable jackets for power/signal
« Reply #6 on: January 04, 2019, 01:35:32 PM »

...however it doesn't really make sense for end users to build distro gear...

Ah, I was wondering if anyone was going to misinterpret that.  By "build distro gear" I don't mean build a power distro.  I meant to assembly a kit of various lengths of Powercon cables (with various ends), Powercon outlet boxes, and the other bits and pieces needed to deploy a working solution in the field.  Definitely best to clarify though!
Logged

Taylor Hall

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 869
Re: Accepted types of cable jackets for power/signal
« Reply #7 on: January 04, 2019, 02:03:55 PM »

Hi Taylor, while you're at it you might want to think about building a proper set of power distro gear and not just code-compliant extension cords.  I know we have a number of threads here about stringers and Powercon boxes, so plenty of resources to reference.  I'm a big user of the OA Windsor boxes but there are others on the market too.  The cost is reasonable and if properly thought out ahead of time will give you endless options for getting power where you need it.  Hope this helps!
We have several Windsor boxes already. We inherited a stringer setup from the aforementioned buyout as well, so we've got a nice little cache of their stuff already.
And yes, we're only messing with making cables, not distro hardware. I know enough to know that I know far too little to try and homebrew anything like that haha. Motion labs/Lex stuff comes up often enough secondhand for good enough prices that it's not worth saving an extra 50 bucks or so to try rolling our own.
Logged
There are two ways to do anything:
1) Do it right
2) Do it over until you do it right

TJ (Tom) Cornish

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4317
  • St. Paul, MN
Re: Accepted types of cable jackets for power/signal
« Reply #8 on: January 04, 2019, 02:09:38 PM »

Ah, I was wondering if anyone was going to misinterpret that.  By "build distro gear" I don't mean build a power distro.  I meant to assembly a kit of various lengths of Powercon cables (with various ends), Powercon outlet boxes, and the other bits and pieces needed to deploy a working solution in the field.  Definitely best to clarify though!
I was pretty sure that was what you meant, but wanted the thread to be clear.
Logged

Frank Koenig

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1318
  • Palo Alto, CA USA
Re: Accepted types of cable jackets for power/signal
« Reply #9 on: January 04, 2019, 03:29:41 PM »

Is it safe to assume that using any of the above jacket types is fine so long as the conductors are properly rated for the loads they'll be receiving?

To be clear, the conductors must be rated for the upstream overcurrent protection, not the load. This must take into account both the heating of the conductor during normal operation and the ability of the conductor to cause a large enough fault current to trip the overcurrent protection when a direct short occurs (either to ground or another current carrying conductor) at the end of the line. There are some exceptions, such as taps, which must be short and sufficient for the immediate downstream overcurrent protection, and line cords on equipment utilizing 15 and 20 A overcurrent protected branch circuits. Love the way it's OK to plug a desk lamp with an 18 AWG cord into a 20 A branch circuit. -F
Logged
"Nature abhors a vacuum tube." -- John Pierce, Bell Labs

Jeff Lelko

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2012
  • Cape Canaveral, FL
Re: Accepted types of cable jackets for power/signal
« Reply #10 on: January 04, 2019, 10:29:20 PM »

We have several Windsor boxes already.

What do you use with them now?
Logged

Scott Holtzman

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 7501
  • Ghost AV - Avon Lake, OH
    • Ghost Audio Visual Systems, LLC
Re: Accepted types of cable jackets for power/signal
« Reply #11 on: January 04, 2019, 10:44:18 PM »

I have the same issue regarding power boxes at hotels on this area, they are home made and awful.  These are top tier 4 star hotels too.

Our three phase distro was bought from another production company that closed after the owner took ill.  It uses a commercial load center but it's built into the back of a birch 5/8 case that is a piece of furniture.  The front is all 19" rack panela with cams, twist locks and Edison outlets.  I have used it with big bennies, fairs and in theaters all over town.  We have been inspected and complemented.  All our feeders are soow and we have the rubbber quad boxes.  It is all mainted well.

Before we stepped up to the three phase we got many miles out of spider boxes.  They are around 1000 bucks and adapt 50 and 100 amp single phase 240 to 120 individually protected circuits.  If you are working venues that provide this power these are a great investment.

SOOW lasts longer and coils easier,  it's worth the investment.  Make sure to put trick line on each and tie them up.  There are videos online that show you how to stitch the line to the cable.

Good luck!

Sent from my VS996 using Tapatalk

Logged
Scott AKA "Skyking" Holtzman

Ghost Audio Visual Solutions, LLC
Cleveland OH
www.ghostav.rocks

Tim Hite

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1221
    • Bad Quail
Re: Accepted types of cable jackets for power/signal
« Reply #12 on: January 05, 2019, 02:40:53 AM »

Got a link handy? I'm just getting a bunch of fishing related stuff on you tube with tie line and cable search terms.


. . .Make sure to put trick line on each and tie them up.  There are videos online that show you how to stitch the line to the cable.


Logged
Bad Quail
Sound + Light + Image
Joshua Tree, California
Authorized Dealer for all this stuff

Scott Holtzman

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 7501
  • Ghost AV - Avon Lake, OH
    • Ghost Audio Visual Systems, LLC
Re: Accepted types of cable jackets for power/signal
« Reply #13 on: January 05, 2019, 03:27:51 AM »

Got a link handy? I'm just getting a bunch of fishing related stuff on you tube with tie line and cable search terms.
Here is a life time of knots.

For cables cut to length (long enough to tie a big ass bow knot arount the max girth of the segment) dovide in two then use a basic strap hitch.  Now take one side around again and make a tight square knot to secure it. 

This to me is a modification of the Kansas City stitch used in telco central offices (where I learned cable stitching, in the phone biz)  https://youtu.be/McqCUfw7AYU

The bowline is the next to learn amd very useful for production duties.

Sent from my VS996 using Tapatalk

Logged
Scott AKA "Skyking" Holtzman

Ghost Audio Visual Solutions, LLC
Cleveland OH
www.ghostav.rocks

Tim Hite

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1221
    • Bad Quail
Re: Accepted types of cable jackets for power/signal
« Reply #14 on: January 05, 2019, 11:13:08 AM »

I've just been doing a surgeons knot around the cable the a half hitch with half bow after wrapping.I was going to use a clove hitch, but those come loose so easily.

I tend to prefer a figure-8 loop or follow-through over bowline because it's more secure if there's slack in the line. Holdover from my rock climbing days.

Here is a life time of knots.

For cables cut to length (long enough to tie a big ass bow knot arount the max girth of the segment) dovide in two then use a basic strap hitch.  Now take one side around again and make a tight square knot to secure it. 

This to me is a modification of the Kansas City stitch used in telco central offices (where I learned cable stitching, in the phone biz)  https://youtu.be/McqCUfw7AYU

The bowline is the next to learn amd very useful for production duties.

Sent from my VS996 using Tapatalk
Logged
Bad Quail
Sound + Light + Image
Joshua Tree, California
Authorized Dealer for all this stuff

ProSoundWeb Community

Re: Accepted types of cable jackets for power/signal
« Reply #14 on: January 05, 2019, 11:13:08 AM »