Custom Adapter
« on: October 22, 2018, 12:36:21 PM »

Hey all,
I am trying to come up with a back hand way to get L21-30 3Phase connection before we can have a new PD delivered. Our current PD's have plenty of L14-30 outputs. My thought was make a double L14-30P to L21-30R to get the 3 hot legs needed. They would be plugged into consecutive L14-30 outlets on the PD to keep the load balanced (XY,ZX). Thoughts?
Logged
Kristian Stevenson

TJ (Tom) Cornish

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4317
  • St. Paul, MN
Re: Custom Adapter
« Reply #1 on: October 22, 2018, 02:04:54 PM »

Hey all,
I am trying to come up with a back hand way to get L21-30 3Phase connection before we can have a new PD delivered. Our current PD's have plenty of L14-30 outputs. My thought was make a double L14-30P to L21-30R to get the 3 hot legs needed. They would be plugged into consecutive L14-30 outlets on the PD to keep the load balanced (XY,ZX). Thoughts?
Probably marginally acceptable in the shop; not OK for a gig.
Logged

Frank Koenig

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1318
  • Palo Alto, CA USA
Re: Custom Adapter
« Reply #2 on: October 22, 2018, 03:53:12 PM »

Hey all,
I am trying to come up with a back hand way to get L21-30 3Phase connection before we can have a new PD delivered. Our current PD's have plenty of L14-30 outputs. My thought was make a double L14-30P to L21-30R to get the 3 hot legs needed. They would be plugged into consecutive L14-30 outlets on the PD to keep the load balanced (XY,ZX). Thoughts?

The common-sense test that this fails is that if you unplug one of the L14-30s with a load connected to the L21-30 there will be a live male contact that could hurt somebody. Would I do this "in the lab" with just me around? Sure. But it's not safe around humans :) -F
Logged
"Nature abhors a vacuum tube." -- John Pierce, Bell Labs

Kristian Stevenson

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 94
  • Lynchburg, VA
Re: Custom Adapter
« Reply #3 on: October 24, 2018, 06:00:50 PM »

The common-sense test that this fails is that if you unplug one of the L14-30s with a load connected to the L21-30 there will be a live male contact that could hurt somebody. Would I do this "in the lab" with just me around? Sure. But it's not safe around humans :) -F

Didn't think about that under load scenario - makes sense.