Author Topic: SOOW Cord 6/4 "Non UL"  (Read 9432 times)

Jeff Bankston

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2568
Re: SOOW Cord 6/4 "Non UL"
« Reply #30 on: July 30, 2018, 04:02:43 PM »

SOOW

6/3 - 55A
6/4 - 45A

4/4 - 60A

Logged

Jeff Bankston

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2568
Re: SOOW Cord 6/4 "Non UL"
« Reply #31 on: July 30, 2018, 04:16:20 PM »

Slightly off-topic, but why on earth are you running 4/4 to FOH? Does your mixer pull 50 amps? Is it 1000' from the stage? Do you have massive lights out there?

I can't think of any other reasons to use 4/4 to FOH.
The Midas draws more current than my others boards. I have 3 power supplies. I also added a few other electrical things at FOH. I need a single cable that will reach up to 150' from front of stage and that means at least 160'. Then it has to connect to the main distro so figure 200'. It is single phase and that means 2 hot legs to a 50A breaker(not a 60A). The Midas is on one phase and everything else is on the other phase. With a 120V at the distro  the voltage will be 115V at the Midas on its phase with a 200' cable lenght from the distro with 4/4 cable. With 6/4 the voltage will be 112V. 4/4 cable is the way to go. 6/4 50' cable runs  on 45A breakers for the amp racks is plenty. I put my amps behind the speakers and that saves on copper and others things.
Logged

Tim McCulloch

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 23741
  • Wichita, Kansas USA
Re: SOOW Cord 6/4 "Non UL"
« Reply #32 on: July 30, 2018, 05:03:31 PM »

The Midas draws more current than my others boards. I have 3 power supplies. I also added a few other electrical things at FOH. I need a single cable that will reach up to 150' from front of stage and that means at least 160'. Then it has to connect to the main distro so figure 200'. It is single phase and that means 2 hot legs to a 50A breaker(not a 60A). The Midas is on one phase and everything else is on the other phase. With a 120V at the distro  the voltage will be 115V at the Midas on its phase with a 200' cable lenght from the distro with 4/4 cable. With 6/4 the voltage will be 112V. 4/4 cable is the way to go. 6/4 50' cable runs  on 45A breakers for the amp racks is plenty. I put my amps behind the speakers and that saves on copper and others things.

Can you run the Midas on 240V?  Half the voltage drop....
Logged
"If you're passing on your way, from Palm Springs to L.A., Give a wave to good ol' Dave, Say hello to progress and goodbye to the Moonlight Motor Inn." - Steve Spurgin, Moonlight Motor Inn

Dan Mortensen

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1072
Re: SOOW Cord 6/4 "Non UL"
« Reply #33 on: July 30, 2018, 07:24:43 PM »

The Midas draws more current than my others boards. I have 3 power supplies. I also added a few other electrical things at FOH. I need a single cable that will reach up to 150' from front of stage and that means at least 160'. Then it has to connect to the main distro so figure 200'. It is single phase and that means 2 hot legs to a 50A breaker(not a 60A). The Midas is on one phase and everything else is on the other phase. With a 120V at the distro  the voltage will be 115V at the Midas on its phase with a 200' cable lenght from the distro with 4/4 cable. With 6/4 the voltage will be 112V. 4/4 cable is the way to go. 6/4 50' cable runs  on 45A breakers for the amp racks is plenty. I put my amps behind the speakers and that saves on copper and others things.

Thanks for that explanation. Just out of curiosity nosiness, how much power does the Midas draw? And do you have all 3 power supplies on at the same time?

Note Tim's response. Relevant to it, by using 240v you also get the benefits of running on balanced power, which many people spend $$$ to get from 120v. Using 240v you get them for free.

Sounds like you have a pretty cool rig.
Logged

Frank Koenig

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1318
  • Palo Alto, CA USA
Re: SOOW Cord 6/4 "Non UL"
« Reply #34 on: July 30, 2018, 07:28:56 PM »

Half the voltage drop....

It's better than that. Twice the voltage draws half the current, which causes one half the absolute (in Volts) voltage drop. But the voltage drop as a percentage of the line voltage is only one quarter and the energy loss in the line is one quarter, too, as P = i^2 * R. Increasing distribution voltage is a big win. -F
Logged
"Nature abhors a vacuum tube." -- John Pierce, Bell Labs

Jeff Bankston

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2568
Re: SOOW Cord 6/4 "Non UL"
« Reply #35 on: July 30, 2018, 10:04:12 PM »

Can you run the Midas on 240V?  Half the voltage drop....
I dont know. I have to go to my storage unit and look at the power supply and see. If they will run on 220 it just means adding a 220 outlet to the FOH distro and thats easy.
« Last Edit: July 30, 2018, 10:06:31 PM by Jeff Bankston »
Logged

ProSoundWeb Community

Re: SOOW Cord 6/4 "Non UL"
« Reply #35 on: July 30, 2018, 10:04:12 PM »


Pages: 1 2 3 [4]   Go Up
 



Site Hosted By Ashdown Technologies, Inc.

Page created in 0.034 seconds with 23 queries.