No fuses? No problem!
« on: March 30, 2018, 10:42:35 AM »

Logged
I'm just a guy trying to do the next right thing.

This business is for people with too much energy for desk jobs and too much brain for labor jobs. - Scott Helmke

John Daniluk (JD)

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 69
Re: No fuses? No problem!
« Reply #1 on: March 30, 2018, 11:25:23 AM »

While running a power issue in a club, found bolts replacing the 100a fuses....

jd
Logged

John Roberts {JR}

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 17172
  • Hickory, Mississippi, USA
    • Resotune
Re: No fuses? No problem!
« Reply #2 on: March 30, 2018, 11:59:46 AM »

Back in the '70s I was repairing a custom fixture and found a length of aluminum round stock cut to length and used in place of a standard fuse. I charged an extra "stupidity tax" for that repair.

JR
Logged
Cancel the "cancel culture". Do not participate in mob hatred.

Keith Broughton

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3667
  • Toronto
Re: No fuses? No problem!
« Reply #3 on: March 30, 2018, 05:40:59 PM »

ECM always has an interesting article or two. This one's a doozy :)



http://www.ecmweb.com/ops-maintenance/12-reasons-why-electricians-should-always-be-looking-trouble/gallery?slide=11
I suspect under heavy load or a short, those copper wires would vaporize :o
Logged
I don't care enough to be apathetic

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3361
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: No fuses? No problem!
« Reply #4 on: March 30, 2018, 07:24:03 PM »

I suspect under heavy load or a short, those copper wires would vaporize :o

Yes, we call that a fuseable link... ;)

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2671
Re: No fuses? No problem!
« Reply #5 on: March 30, 2018, 07:57:34 PM »

I have seen 1/2" copper pipe flattened on each end to fit in place of a 100 amp size fuse.  Seems like more work thatn it is worth.

That said, there is a situation where a non-fused disconnect would be acceptable-if the upstream over current protective device is sized appropriately, sometimes code requires a disconnect "within sight" of a load.  If that is the case here, the only real code violation is the fact that those fuse holders are certainly not listed to be used with pieces of solid wire!
Logged
Steve Swaffer

John Roberts {JR}

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 17172
  • Hickory, Mississippi, USA
    • Resotune
Re: No fuses? No problem!
« Reply #6 on: March 31, 2018, 09:32:05 AM »

I suspect under heavy load or a short, those copper wires would vaporize :o
You might be surprised by how much current that takes... About a year ago I needed to DIY a small fuse to get an amp working until replacement fuses arrived. I macgyvered a single stand of the smallest wire I could find (30ga?) tacked across the blown fuse, but decided to look up it's fuse current and that was close to 10A IIRC.  :o

 (BTW kids don't do this at home).

JR
Logged
Cancel the "cancel culture". Do not participate in mob hatred.

Kevin Graf

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 343
Re: No fuses? No problem!
« Reply #7 on: March 31, 2018, 03:17:23 PM »

Yep, fusing current for copper wire:
30AWG  ::  10.2A
12AWG ::  235A
Logged
Speedskater

Scott Holtzman

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 7503
  • Ghost AV - Avon Lake, OH
    • Ghost Audio Visual Systems, LLC
Re: No fuses? No problem!
« Reply #8 on: April 01, 2018, 06:07:30 AM »

Yep, fusing current for copper wire:
30AWG  ::  10.2A
12AWG ::  235A
Those values are in free air, right? 

Sent from my VS995 using Tapatalk

Logged
Scott AKA "Skyking" Holtzman

Ghost Audio Visual Solutions, LLC
Cleveland OH
www.ghostav.rocks

Kevin Graf

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 343
Re: No fuses? No problem!
« Reply #9 on: April 01, 2018, 09:09:31 AM »

Those values are in free air, right?     
Based on Preece  and Onderdonk.
https://www.powerstream.com/wire-fusing-currents.htm
Logged