Re: 240 volt to 2 x 120 volt 15/20amp connectors
« Reply #10 on: August 22, 2016, 06:29:45 pm »

We use L14-20 connectors in that sort of application. Dedicated outlets on the distro (Motion Labs) with 20 amp 2-pole breakers, 12/4 or bigger cable, and quad boxes or other breakouts to get to Edison.  We're not compatible with other companies L14-30 setups, but we don't need overcurrent devices aside from what's in the distro already. 

Locking connectors and two circuits per cable is reasonably handy for us.
Logged

TJ (Tom) Cornish

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 4284
  • St. Paul, MN
Re: 240 volt to 2 x 120 volt 15/20amp connectors
« Reply #11 on: August 22, 2016, 11:08:53 pm »

We use L14-20 connectors in that sort of application. Dedicated outlets on the distro (Motion Labs) with 20 amp 2-pole breakers, 12/4 or bigger cable, and quad boxes or other breakouts to get to Edison.  We're not compatible with other companies L14-30 setups, but we don't need overcurrent devices aside from what's in the distro already. 

Locking connectors and two circuits per cable is reasonably handy for us.
I am moving to this system, too.  Not needing downstream breakers is very nice, and being able to simply swap out the quad box and have 2 x 120v circuits or 1 x 208/240v circuit - or even both at the same time with a passthrough is very handy.  Being able to use 12/4 and not needing to derate the cable for two circuits is an added bonus.
Logged

Bob Faulkner

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1003
  • Raleigh, NC
Re: 240 volt to 2 x 120 volt 15/20amp connectors
« Reply #12 on: August 23, 2016, 07:51:18 am »

We use L14-20 connectors in that sort of application. Dedicated outlets on the distro (Motion Labs) with 20 amp 2-pole breakers, 12/4 or bigger cable, and quad boxes or other breakouts to get to Edison.  We're not compatible with other companies L14-30 setups, but we don't need overcurrent devices aside from what's in the distro already. 

Locking connectors and two circuits per cable is reasonably handy for us.


I am moving to this system, too.  Not needing downstream breakers is very nice, and being able to simply swap out the quad box and have 2 x 120v circuits or 1 x 208/240v circuit - or even both at the same time with a passthrough is very handy.  Being able to use 12/4 and not needing to derate the cable for two circuits is an added bonus.
Thanks for the info. 