Over July 4 we did an outdoor show at a local university. They supplied us with a breaker panel with different circuits all with GFI outlets. When the band began playing we tripped four of the outlets (not simultaneously) at various times but never any breakers. Panel was located 35' from where we had our rack. Sound system was a modest outdoor set up, we used four circuits: one Crown iTech8k amp powering four Danley TH118 subs, another iTech8k amp powering two EAW LA325 tops, one circuit for the rest of the rack (mixer, etc.), one circuit for the stage. At first all I did was reset the GFI, when it happened again I moved the cable to another circuit. It happened to all of the circuits (except the mixer) at various times. Eventually I just brought levels down and it stopped but I'm not sure that what I did is what solved it. If so, why would the GFI trip and not the breaker? One other factor: we were battling rain and wet conditions but nothing was laying in puddles or anything like that.

Any ideas what was going on here?

Thanks for any insight

Logged
Pi Entertainment Services
Midas M32R / MR18
Behringer X32R
Danley SH50 / SM80 / TH118 / TH115
Fulcrum Acoustic fa22ac
RCF NX 12SMA
Yamaha DSR112 / DZR10
Powersoft X4 / M50Q
Crown iT8k

Kevin Graf

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 342
Re: Tripping GFI
« Reply #1 on: July 07, 2016, 10:01:06 AM »

In effect, GFCIs are designed to trip when they notice a very small amount of current leaking into the Safety Ground, Planet Earth or another circuit. So it could be a power conditioner dumping noise current into the safety ground or a stinger capacitor or stray current from one circuit using your interconnect shields to return on another AC circuit.
Logged
Speedskater

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3361
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: Tripping GFI
« Reply #2 on: July 07, 2016, 10:31:29 AM »

In effect, GFCIs are designed to trip when they notice a very small amount of current leaking into the Safety Ground, Planet Earth or another circuit. So it could be a power conditioner dumping noise current into the safety ground or a stinger capacitor or stray current from one circuit using your interconnect shields to return on another AC circuit.

Yes, power conditioner strips with MOV's often leak a few mA current to the EGC (Safety Ground), so a couple of them onstage can easily add up to the 6 mA trip point on a GFCI. Same for a stinger cap on a backline guitar amplifier. However, there shouldn't be be a path for shield ground loop currents through the GFCI's sensing transformer. That suggests that ground loop currents through the shields shouldn't be able to trip an upstream GFCI unless there was a double-bond of the neutral and EGC Ground in your power distro somewhere. But that mis-wiring condition would make it very easy to trip the GFCI so just turning down the volume wouldn't fix it. More to think about on this problem. 

Kevin Graf

  • Sr. Member
  • ****
  • Offline Offline
  • Posts: 342
Re: Tripping GFI
« Reply #3 on: July 07, 2016, 11:28:36 AM »

If one of the circuits has a Neutral/Safety Ground swap, then the chassis's will be a different potentials and there will be current flow through the interconnect shields. But even without the swap component's AC supply sections do leak current.
Logged
Speedskater

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3361
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: Tripping GFI
« Reply #4 on: July 07, 2016, 12:40:11 PM »

If one of the circuits has a Neutral/Safety Ground swap, then the chassis's will be a different potentials and there will be current flow through the interconnect shields. But even without the swap component's AC supply sections do leak current.

Yes, everything leaks a little. And it's all additive. So a single piece of gear on a GFCI may not trip it. But put 2 or 3 things on a GFCI and the leakage currents can easily add it to the 6 mA tripping threshold. The fact that in this instance the GFCI's would trip under heavy current draw, but not under more moderate current draw suggests some intermingling of the Ground and Neutral. First thing I would do is check your own gear to make sure there's no accidental G-N bond or G-N swap in any of your equipment or extension cords. That's the only thing I can think of that would create a load-dependent GFCI random trip. 

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2631
Re: Tripping GFI
« Reply #5 on: July 07, 2016, 01:12:58 PM »

GFCis are pretty sensitive-they only take .006 amps to trip-so it could have just been moisture from the rain and damp.  It certainly wouldn't have to be laying in a puddle to trip.

The other place I would be suspicious is the GFCIs themselves.  New ones shouldn't reset if they are defective-but I received some new ones this spring that were defective and would trip when a load was applied.  They are designed to fail safe-so more likely to trip when they shouldn't than not to trip when they should.  The fact that it happened on more than one circuit makes this the less likely possibility here.

At least you didn't just bypass them-GFCI's tripping is not necessarily a bad thing.  It could just save a life.
Logged
Steve Swaffer

Tim McCulloch

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 23199
  • Wichita, Kansas USA
Re: Tripping GFI
« Reply #6 on: July 07, 2016, 04:56:24 PM »

GFCis are pretty sensitive-they only take .006 amps to trip-so it could have just been moisture from the rain and damp.  It certainly wouldn't have to be laying in a puddle to trip.

The other place I would be suspicious is the GFCIs themselves.  New ones shouldn't reset if they are defective-but I received some new ones this spring that were defective and would trip when a load was applied.  They are designed to fail safe-so more likely to trip when they shouldn't than not to trip when they should.  The fact that it happened on more than one circuit makes this the less likely possibility here.

At least you didn't just bypass them-GFCI's tripping is not necessarily a bad thing.  It could just save a life.

This.

I've had GFCI tripping from plugging the extension cord I use for my lawn mower when there is dew on the grass and the connection is lying on the lawn.

For Robert:  the GFCI is tripping because something is wrong.  That the problem moved with the cord is your clue, and that different GFCIs tripped indicates that a faulty GFCI is unlikely.
Logged
"Art has always held a tenuous position between acts of subversion and status symbol collected by those who profit from the very status quo the art purports to subvert." - Stephen Colbert

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3361
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: Tripping GFI
« Reply #7 on: July 07, 2016, 06:30:40 PM »

One more thing to consider. In old tube guitar amps and microwave ovens, the insulation in their power transformers often start deteriorating from all the heat and constant loading. I've seen as least several of each that developed a live-to-chassis leakage of a few 10's of mA. Certainly enough to trip a GFCI, but not enough to trip a circuit breaker when plugged into a conventional grounded receptacle. Since most affordable clamp-on ammeters don't go down below 10 mA resolution, you can make a current multiplier by wrapping a split-out ground wire in an extension cord around the clamp ammeter jaws 10 times. Now your 10 mA resolution ammeter just became a 1 mA resolution meter. Plugging in your gear one at a time to this ground current sensing cord should give you an indication of anything leaking current to the EGC. I'll build up one of these in the shop tomorrow and post a picture, but it's really simple to find small leakage currents with this booster trick.

John Escallier

  • Newbie
  • *
  • Offline Offline
  • Posts: 11
Re: Tripping GFI
« Reply #8 on: July 08, 2016, 03:34:51 PM »

Yes, everything leaks a little. And it's all additive. So a single piece of gear on a GFCI may not trip it. But put 2 or 3 things on a GFCI and the leakage currents can easily add it to the 6 mA tripping threshold. The fact that in this instance the GFCI's would trip under heavy current draw, but not under more moderate current draw suggests some intermingling of the Ground and Neutral. First thing I would do is check your own gear to make sure there's no accidental G-N bond or G-N swap in any of your equipment or extension cords. That's the only thing I can think of that would create a load-dependent GFCI random trip.

A GN swap should instantly trip out a GFCI.  The inrush far exceeds the time/current trip spec, and any idling transformer will still draw current from the line due to magnetizing inductance even though it's 90 degrees out.  GFCI's do not examine the leakage current phase.

A GN bond, that is another horse.  That's a front runner.

Also, if too many Y's are on the line, the leakage can reach the GFCI levels.  If it's close, audio leakage off the supply rails will be shunted to ground as well.

John
Logged

Steve Garris

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1457
Re: Tripping GFI
« Reply #9 on: July 08, 2016, 05:05:52 PM »

GFCis are pretty sensitive-they only take .006 amps to trip-so it could have just been moisture from the rain and damp.  It certainly wouldn't have to be laying in a puddle to trip.

The other place I would be suspicious is the GFCIs themselves.  New ones shouldn't reset if they are defective-but I received some new ones this spring that were defective and would trip when a load was applied.  They are designed to fail safe-so more likely to trip when they shouldn't than not to trip when they should.  The fact that it happened on more than one circuit makes this the less likely possibility here.

At least you didn't just bypass them-GFCI's tripping is not necessarily a bad thing.  It could just save a life.

I just came to this forum to get an answer on my question, and here I see this post at the top! Same exact thing happened to me last night.

I had a modest setup, under a gazebo but things were getting "moist". My 10 ga cable was plugged into a 20 amp GFI circuit, then split into a 3-way with power surrounding the stage. PA barely on, as the gazebo was horrible for sound. The GFI tripped just once, but I left my cable in that same circuit and re-set it. I unplugged (1) 70w Par front flood, and turned it down just a tiny bit. We made it through the rest of the gig without any power losses.

I did this same venue last summer (weekly shows), and never had a problem. The difference being the rain, and my new SRX system draws more than my old PRX that I used last year. I didn't think it it was that, and wondered if in fact enough moisture was present to cause the GFI to trip. Another possibility was a bad GFI. These shows are usually sunny and dry, but the next time it's wet, I'll do a better job of routing and covering cables.