Standard Outlet Question
« on: September 08, 2015, 01:23:56 PM »

How can you tell if two outlet are on the same circuit (breaker) or on two different circuit (breaker)?

Logged

TJ (Tom) Cornish

  • Hero Member
  • *****
  • Online Online
  • Posts: 4317
  • St. Paul, MN
Re: Standard Outlet Question
« Reply #1 on: September 08, 2015, 01:25:24 PM »

How can you tell if two outlet are on the same circuit (breaker) or on two different circuit (breaker)?
I wrote an article that covers this to some degree. http://tjcornish.com/articles/power-distribution-part-1--.html
Logged

Jonathan Johnson

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3209
  • Southwest Washington (state, not DC)
Re: Standard Outlet Question
« Reply #2 on: September 08, 2015, 01:41:52 PM »

The only way to be sure is to cycle the suspected branch circuit breaker for the receptacles in question.

When disconnecting the power to a receptacle or other electrical device, I use this procedure:
  • Disconnect power. Verify that power is no longer present.
  • Reconnect power. Verify that power is again present.
  • Disconnect power. Verify that power is no longer present.
  • Lock out/tag out disconnect.

The purpose of this method is to guard against an inadvertent false reading, or simultaneous failure or misunderstanding between you and a helper. The lock out/tag out step is necessary to ensure that the circuit is not energized by someone else while you are working on it. Of course, lock out/tag out is not needed when you are just identifying circuits.
Logged
Stop confusing the issue with facts and logic!

TJ (Tom) Cornish

  • Hero Member
  • *****
  • Online Online
  • Posts: 4317
  • St. Paul, MN
Re: Standard Outlet Question
« Reply #3 on: September 08, 2015, 02:24:54 PM »

The only way to be sure is to cycle the suspected branch circuit breaker for the receptacles in question.
That's the only way to be absolutely sure which specific breaker feeds a particular outlet, however you can be sure that two receptacles aren't on the same circuit via other means of varying degrees of confidence, and in at least one case with 100% confidence. 

The reason I wrote articles on power is so I don't have to continually re-type my answers in the forum, so I'm going to stop now so as to not defeat my own purpose.
Logged

Frank DeWitt

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1010
    • LBP DI Box
Re: Standard Outlet Question
« Reply #4 on: September 08, 2015, 02:54:39 PM »

I believe Mike has a method where he uses a cycle relay to apply a large load (about 1000 watts) to a outlet for a short time (about .1 sec if I remember right)  This load will lower the voltage on that outlet and any outlet on that circuit breaker.  It will lower the voltage on other outlets as well, but not near as much.

Do I have that anywhere near right Mike?
Logged
Not to Code

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3361
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: Standard Outlet Question
« Reply #5 on: September 08, 2015, 04:17:11 PM »

I believe Mike has a method where he uses a cycle relay to apply a large load (about 1000 watts) to a outlet for a short time (about .1 sec if I remember right)  This load will lower the voltage on that outlet and any outlet on that circuit breaker.  It will lower the voltage on other outlets as well, but not near as much.

Do I have that anywhere near right Mike?

Sort of but not exactly.... I use that test to identify swapped neutral and ground wires. And the pulse is more like 1 second on and one second off. That so there's enough time for a digital meter to respond to the change. I also use to identify double Ground-Neutral bonds in sub-panels. 

Brook Hovland

  • Full Member
  • ***
  • Offline Offline
  • Posts: 184
    • DiA Events
Re: Standard Outlet Question
« Reply #6 on: September 08, 2015, 04:32:00 PM »

"The reason I wrote articles on power is so I don't have to continually re-type my answers in the forum, so I'm going to stop now so as to not defeat my own purpose."

If there is a best best quote of the day award, that gets it in my book!
Logged

Frank DeWitt

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1010
    • LBP DI Box
Re: Standard Outlet Question
« Reply #7 on: September 08, 2015, 05:35:17 PM »

Sort of but not exactly.... I use that test to identify swapped neutral and ground wires. And the pulse is more like 1 second on and one second off. That so there's enough time for a digital meter to respond to the change. I also use to identify double Ground-Neutral bonds in sub-panels.

OK Thanks Mike,  It seems as if a 1 sec long load would be readable with a analog meter. so my misuse could be done?
Logged
Not to Code

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3361
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: Standard Outlet Question
« Reply #8 on: September 08, 2015, 09:11:48 PM »

OK Thanks Mike,  It seems as if a 1 sec long load would be readable with a analog meter. so my misuse could be done?
Yes, you would certainly see an analog meter needle swinging back and forth at 1/2 Hz. In fact, that's easier to see than a digital display updating at some unknown rate.

frank kayser

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1654
  • Maryland suburbs of Washington DC
Re: Standard Outlet Question
« Reply #9 on: September 09, 2015, 11:06:33 PM »

"The reason I wrote articles on power is so I don't have to continually re-type my answers in the forum, so I'm going to stop now so as to not defeat my own purpose."

If there is a best best quote of the day award, that gets it in my book!

Yeah. That's about as good as it gets. Brought a smile to my face.
Logged

ProSoundWeb Community

Re: Standard Outlet Question
« Reply #9 on: September 09, 2015, 11:06:33 PM »


Pages: [1]   Go Up
 



Site Hosted By Ashdown Technologies, Inc.

Page created in 0.034 seconds with 24 queries.