What's the danger
« on: November 02, 2014, 10:45:06 AM »

I have run my entire rig off of one 20 amp edison with no issues before when I had to and don't currently own any distro nor have I run into any situations so far where I wish I did. Quite content running off wall outlets however....

 If I was to show up at a venue and the only outlet available was an L14-30P would this be safe to use? If not what's the potential danger.

http://www.amazon.com/Conntek-YL1430520S-Generator-Adapter-Connector/dp/B002MGJ2F4/ref=cm_cd_ql_qh_dp_t

Thanks
Logged
We're here to deliver the sound equipment. Who has the check?

Ray Aberle

  • Classic LAB
  • Hero Member
  • *
  • Offline Offline
  • Posts: 3455
  • Located in Vancouver, WA (and serves OR-WA-ID-BC)
    • Kelcema Audio
Re: What's the danger
« Reply #1 on: November 02, 2014, 12:49:19 PM »

If I was to show up at a venue and the only outlet available was an L14-30P would this be safe to use? If not what's the potential danger.

http://www.amazon.com/Conntek-YL1430520S-Generator-Adapter-Connector/dp/B002MGJ2F4/ref=cm_cd_ql_qh_dp_t

I don't see any breakers on it, so there's nothing limiting the 20A female connectors to only getting up to 20A. Since the L14-30 outlet is providing up to 30A per leg, you'd be able to pull more then the capacity of the 20A outs before the L14-30's breaker would trip.

I would not use it.
Logged
Kelcema Audio
Regional - Serving Pacific Northwest (OR, WA, ID, BC)

Tim McCulloch

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 23782
  • Wichita, Kansas USA
Re: What's the danger
« Reply #2 on: November 02, 2014, 01:14:14 PM »

I have run my entire rig off of one 20 amp edison with no issues before when I had to and don't currently own any distro nor have I run into any situations so far where I wish I did. Quite content running off wall outlets however....

 If I was to show up at a venue and the only outlet available was an L14-30P would this be safe to use? If not what's the potential danger.

http://www.amazon.com/Conntek-YL1430520S-Generator-Adapter-Connector/dp/B002MGJ2F4/ref=cm_cd_ql_qh_dp_t

Thanks

Is there a circuit breaker for each of the 20 amp outlets?  If no, then it's not Code.  This device is built on the assumption that the user will power only a single tool or appliance from each outlet (hence no "need" for over-current protection), but in our uses or with cube taps and other multi-outlet devices that do not have internal circuit breakers, it is possible to overload the 12 ga conductors.

Now to answer your implied question, would I use it?  Yes, if I were connecting only a single load to each receptacle.
« Last Edit: November 02, 2014, 02:47:46 PM by Tim McCulloch »
Logged
"If you're passing on your way, from Palm Springs to L.A., Give a wave to good ol' Dave, Say hello to progress and goodbye to the Moonlight Motor Inn." - Steve Spurgin, Moonlight Motor Inn

Keith Broughton

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3667
  • Toronto
Re: What's the danger
« Reply #3 on: November 02, 2014, 02:41:59 PM »

I have run my entire rig off of one 20 amp edison with no issues before when I had to and don't currently own any distro nor have I run into any situations so far where I wish I did. Quite content running off wall outlets however....

 If I was to show up at a venue and the only outlet available was an L14-30P would this be safe to use? If not what's the potential danger.

http://www.amazon.com/Conntek-YL1430520S-Generator-Adapter-Connector/dp/B002MGJ2F4/ref=cm_cd_ql_qh_dp_t

Thanks
Not legal!
Logged
I don't care enough to be apathetic

Steve M Smith

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3381
  • Isle of Wight - England
Re: What's the danger
« Reply #4 on: November 02, 2014, 02:55:46 PM »

Not legal!

Would it actually be an offence (civil or criminal) to use it or is it just not to code?


Steve.
Logged

Ray Aberle

  • Classic LAB
  • Hero Member
  • *
  • Offline Offline
  • Posts: 3455
  • Located in Vancouver, WA (and serves OR-WA-ID-BC)
    • Kelcema Audio
Re: What's the danger
« Reply #5 on: November 02, 2014, 03:18:33 PM »

Would it actually be an offence (civil or criminal) to use it or is it just not to code?


Steve.
Not to code, and an AHJ could press an issue with it. But, if you used it, started a fire, and caused property or personal damage, you might be liable for something.
Logged
Kelcema Audio
Regional - Serving Pacific Northwest (OR, WA, ID, BC)

Scott Olewiler

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1198
  • Trust me, it will be loud enough.
    • 4th Street Sound
Re: What's the danger
« Reply #6 on: November 02, 2014, 04:16:33 PM »

Ok, I've read enough to not attempt to use anything like this.

So if I get a distro, should it be a 50 amp? It that what you typically have available? I haven't really noticed anything other than wall outlets any where I've worked,but, OTOH, I haven't been looking for anything else either.

I assume the safest bet is to have the 50 amp distro and pigtail, and then a second 30 amp pigtail on hand? Or will I need an assortment of pigtails?
Logged
We're here to deliver the sound equipment. Who has the check?

Rob Spence

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3531
  • Boston Metro North/West
    • Lynx Audio Services
Re: What's the danger
« Reply #7 on: November 02, 2014, 04:42:09 PM »

Ok, I've read enough to not attempt to use anything like this.

So if I get a distro, should it be a 50 amp? It that what you typically have available? I haven't really noticed anything other than wall outlets any where I've worked,but, OTOH, I haven't been looking for anything else either.

I assume the safest bet is to have the 50 amp distro and pigtail, and then a second 30 amp pigtail on hand? Or will I need an assortment of pigtails?

I would have 50a in & through with either 6 20a circuits (or for me, 4 20a & a L14-30 for my amp rack).
CS connectors for the in & through.
A CS to CS feeder cable if you need it.
A 14-50 range plug to CS cable.
A L14-30p to CS cable.

Make the cable lengths what ever you need.



Sent from my iPad using Tapatalk HD
Logged
rob at lynxaudioservices dot com

Dealer for: AKG, Allen & Heath, Ashley, Astatic, Audix, Blue Microphones, CAD, Chauvet, Community, Countryman, Crown, DBX, Electro-Voice, FBT, Furman, Heil, Horizon, Intellistage, JBL, Lab Gruppen, Mid Atlantic, On Stage Stands, Pelican, Peterson Tuners, Presonus, ProCo, QSC, Radial, RCF, Sennheiser, Shure, SKB, Soundcraft, TC Electronics, Telex, Whirlwind and others

Thomas Lamb

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 531
Re: What's the danger
« Reply #8 on: November 02, 2014, 06:05:40 PM »

I have run my entire rig off of one 20 amp edison with no issues before when I had to and don't currently own any distro nor have I run into any situations so far where I wish I did. Quite content running off wall outlets however....

 If I was to show up at a venue and the only outlet available was an L14-30P would this be safe to use? If not what's the potential danger.

http://www.amazon.com/Conntek-YL1430520S-Generator-Adapter-Connector/dp/B002MGJ2F4/ref=cm_cd_ql_qh_dp_t

A BREAKERED distro for this is what you need. I looked on eBay and there aren't any right now. You may want to ask in the marketplace. If you are going to work at this venue often it would definately be worth it. While I wouldn't normally suggest a homebrew distro if you maybe have a friend that's an electrician the parts for something like this could be procured fairly simply and not to expensively at Home Depot.

Thanks
Logged
bigTlamb

"If you suck on a functional analog desk, you'll really suck on a complex digital desk...." Dick Rees

Scott Olewiler

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1198
  • Trust me, it will be loud enough.
    • 4th Street Sound
Re: What's the danger
« Reply #9 on: November 03, 2014, 09:54:50 AM »

I would have 50a in & through with either 6 20a circuits (or for me, 4 20a & a L14-30 for my amp rack).
CS connectors for the in & through.
A CS to CS feeder cable if you need it.
A 14-50 range plug to CS cable.
A L14-30p to CS cable.

Make the cable lengths what ever you need.

Thanks. excellent.
Logged
We're here to deliver the sound equipment. Who has the check?

Jay Barracato

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2025
  • Solomons, MD
Re: What's the danger
« Reply #10 on: November 03, 2014, 11:06:03 AM »

I agree with Rob.

Except for small generators, I think you are more likely to run into a 50 amp supply than a 30 amp supply.

Sent from my DROID RAZR HD using Tapatalk

Logged
Jay Barracato

Ray Aberle

  • Classic LAB
  • Hero Member
  • *
  • Offline Offline
  • Posts: 3455
  • Located in Vancouver, WA (and serves OR-WA-ID-BC)
    • Kelcema Audio
Re: What's the danger
« Reply #11 on: November 03, 2014, 11:56:11 AM »

I would have 50a in & through with either 6 20a circuits (or for me, 4 20a & a L14-30 for my amp rack).
CS connectors for the in & through.
A CS to CS feeder cable if you need it.
A 14-50 range plug to CS cable.
A L14-30p to CS cable.

Make the cable lengths what ever you need.

The only other thing I might add is a bare wire to CS cable, less then 10 feet. Maybe some extra 50A breakers of different manufacture for venues where you know you don't have a range plug or other convenient outlet available but you can get to the electrical panel. TEST THIS FIRST, AND ENSURE THAT YOU HAVE A LICENSED ELECTRICIAN OR OTHERWISE QUALIFIED PERSONNEL MAKE THIS CONNECTION. (Gotta cover the legalities...) DO NOT WORK IN A HOT PANEL WITHOUT PERSONAL PROTECTIVE EQUIPMENT. I have had venues that had a spare 50A breaker, not doing anything, and we were able to make use of that breaker with our tails.
Logged
Kelcema Audio
Regional - Serving Pacific Northwest (OR, WA, ID, BC)

Rob Spence

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3531
  • Boston Metro North/West
    • Lynx Audio Services
Re: What's the danger
« Reply #12 on: November 03, 2014, 12:41:07 PM »

The only other thing I might add is a bare wire to CS cable, less then 10 feet. Maybe some extra 50A breakers of different manufacture for venues where you know you don't have a range plug or other convenient outlet available but you can get to the electrical panel. TEST THIS FIRST, AND ENSURE THAT YOU HAVE A LICENSED ELECTRICIAN OR OTHERWISE QUALIFIED PERSONNEL MAKE THIS CONNECTION. (Gotta cover the legalities...) DO NOT WORK IN A HOT PANEL WITHOUT PERSONAL PROTECTIVE EQUIPMENT. I have had venues that had a spare 50A breaker, not doing anything, and we were able to make use of that breaker with our tails.

Ray, I should have mentioned the tails. I have one but to save money for something I use rarely I put a 14-50 range socket on it and use it with the 14-50 to CS cable.  $12 vs $90.


Sent from my iPad using Tapatalk HD
Logged
rob at lynxaudioservices dot com

Dealer for: AKG, Allen & Heath, Ashley, Astatic, Audix, Blue Microphones, CAD, Chauvet, Community, Countryman, Crown, DBX, Electro-Voice, FBT, Furman, Heil, Horizon, Intellistage, JBL, Lab Gruppen, Mid Atlantic, On Stage Stands, Pelican, Peterson Tuners, Presonus, ProCo, QSC, Radial, RCF, Sennheiser, Shure, SKB, Soundcraft, TC Electronics, Telex, Whirlwind and others

Keith Broughton

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3667
  • Toronto
Re: What's the danger
« Reply #13 on: November 03, 2014, 02:23:07 PM »

Would it actually be an offence (civil or criminal) to use it or is it just not to code?


Steve.
OK...OK...It's not to code
Logged
I don't care enough to be apathetic

Cailen Waddell

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1428
Re: What's the danger
« Reply #14 on: November 03, 2014, 08:28:30 PM »


I have run my entire rig off of one 20 amp edison with no issues before when I had to and don't currently own any distro nor have I run into any situations so far where I wish I did. Quite content running off wall outlets however....

 If I was to show up at a venue and the only outlet available was an L14-30P would this be safe to use? If not what's the potential danger.

http://www.amazon.com/Conntek-YL1430520S-Generator-Adapter-Connector/dp/B002MGJ2F4/ref=cm_cd_ql_qh_dp_t

Thanks

Everyone has said don't use it.  Now - here is a place I might use it.  One of our smaller b rigs has a motion labs distro with 2 20a PowerCon inputs, Edison out on the rear.  Each circuit is breakered.  I could see using it to power this distro as there is over current protection in the distro.  But the flip side is that I can't think of a situation where I would find an l14-30 but not 2 20a ccts. 


Sent from my iPhone using Tapatalk
Logged

Ray Aberle

  • Classic LAB
  • Hero Member
  • *
  • Offline Offline
  • Posts: 3455
  • Located in Vancouver, WA (and serves OR-WA-ID-BC)
    • Kelcema Audio
Re: What's the danger
« Reply #15 on: November 03, 2014, 08:34:52 PM »

Everyone has said don't use it.  Now - here is a place I might use it.  One of our smaller b rigs has a motion labs distro with 2 20a PowerCon inputs, Edison out on the rear.  Each circuit is breakered.  I could see using it to power this distro as there is over current protection in the distro.  But the flip side is that I can't think of a situation where I would find an l14-30 but not 2 20a ccts. 

Yeah, and that overcurrent protection is what matters. It's where it can do some good: it will trip a breaker before burning out the plugs (hopefully). Not in the BEST place, but still helping.
Logged
Kelcema Audio
Regional - Serving Pacific Northwest (OR, WA, ID, BC)

Cailen Waddell

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1428
Re: What's the danger
« Reply #16 on: November 03, 2014, 08:36:06 PM »


Yeah, and that overcurrent protection is what matters. It's where it can do some good: it will trip a breaker before burning out the plugs (hopefully). Not in the BEST place, but still helping.

Yup - and that 1' of cable and connector without over current protection would probably keep me from using it. 


Sent from my iPhone using Tapatalk
Logged

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2673
Re: What's the danger
« Reply #17 on: November 03, 2014, 09:03:16 PM »

Yet you plug in lamps, electronics, etc with 6 feet of 18 awg wire to 20 amp circuits all the time-yes the loads are controlled and known-but so is a load downstream of a 20 amp breaker.

I don't know that I like the cable-it would be far to easy and likely to get misused, than to bail you out in the odd case where it will work. Might make sense if you routinely had a situation like above-but probably a better way to handle it if it becomes a routine occurance. 
Logged
Steve Swaffer

Tim McCulloch

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 23782
  • Wichita, Kansas USA
Re: What's the danger
« Reply #18 on: November 03, 2014, 09:21:17 PM »

To keep things in context, ConnTek makes a bunch of these kinds of adapters and much of their business is aimed at the RV, marine and jobsite markets.

They claim UL listing "compliance" and if you look at the pics of some of the RV extension cords you'll see what looks like a holographic UL sticker.

Logged
"If you're passing on your way, from Palm Springs to L.A., Give a wave to good ol' Dave, Say hello to progress and goodbye to the Moonlight Motor Inn." - Steve Spurgin, Moonlight Motor Inn

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2673
Re: What's the danger
« Reply #19 on: November 04, 2014, 07:47:25 AM »

To me, one of the conundrums of ULl isting is the phrase "listed for the purpose."  I understand UL won't list motors-instead they certify them-because they don't know the final use.  If I can't easily locate a UL listing verification that also tells me "the purpose" it was listed for I don't know the whole story.  I could see this cable being listed for temporary use to run two appliances from-but not necessarily being listed to supply 2 racks of gear.
Logged
Steve Swaffer

Jonathan Johnson

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3210
  • Southwest Washington (state, not DC)
Re: What's the danger
« Reply #20 on: November 04, 2014, 11:25:49 AM »

To me, one of the conundrums of ULl isting...

Mr. Behringer is now an electrical safety tester?  ;)
Logged
Stop confusing the issue with facts and logic!

Mark Cadwallader

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1338
  • Helena, Montana USA
Re: What's the danger
« Reply #21 on: November 04, 2014, 11:33:21 AM »

Mr. Behringer is now an electrical safety tester?  ;)

Perhaps a "value added" service from the Chinese plant managers?
Logged
"Good tools are expensive, but cheap tools are damned expensive."