Author Topic: Bonding and false positive tests on GFCI  (Read 30315 times)

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2672
Re: Bonding and false positive tests on GFCI
« Reply #30 on: September 04, 2014, 01:18:46 PM »

Looking online I can't find anything that says the EU 6500 or 7000 has a master GFCI?  Maybe I am overlooking it.  Typically, I see GFCI's on 20  120 volt receptacles-standard OCP on the 30 and 50 A twistlock 120/240 v receptacle.  In a standby situation, GFCI is not necessary - the POCO 's power is not GFCI protected.

With a master GFCI that would obviously be a problem, but otherwise my thinking is that the only real issue is "objectional"  current in the EGC-which should not be detrimental if it is sized appropriately.  And that would be preferable to uninformed people running gennys without a bond.
Logged
Steve Swaffer

Jeff Bankston

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2568
Re: Bonding and false positive tests on GFCI
« Reply #31 on: September 04, 2014, 06:35:01 PM »

in los angeles any generator thats built on a set of wheels has to be connected to a ground rod. even all of our contruction site gens had to have a permit from la building and safety and a ground rod driven at the gen. the electrical inspector would come and inspect before we were allowed to use it. a friend runs gens for tv/movie shoots , i will ask him what is required for his 18 wheeler gen rig.
i just talked to my friend about how he ground gens. he said an city inspector always shows up to make sure the gen is grounded. he said he drives a ground rod, finds a cold water pipe and get permission to connect to it, finds a service and gets permission to connect to it, etc. he told me he has seen burned up gens where the neutral was lost and the guy operating the gen didnt ground it. he doesnt know if an inspector had ben to the site or not. he told me he has heard about guys using rubber mats aroumd gens but he doesnt do that because even though it protects you the gen still isnt grounded. heres a foto of him and one of the gens he ran.
« Last Edit: September 04, 2014, 06:38:26 PM by Jeff Harrell »
Logged

Scott Holtzman

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 7530
  • Ghost AV - Avon Lake, OH
    • Ghost Audio Visual Systems, LLC
Re: Bonding and false positive tests on GFCI
« Reply #32 on: September 05, 2014, 12:28:34 AM »

i just talked to my friend about how he ground gens. he said an city inspector always shows up to make sure the gen is grounded. he said he drives a ground rod, finds a cold water pipe and get permission to connect to it, finds a service and gets permission to connect to it, etc. he told me he has seen burned up gens where the neutral was lost and the guy operating the gen didnt ground it. he doesnt know if an inspector had ben to the site or not. he told me he has heard about guys using rubber mats aroumd gens but he doesnt do that because even though it protects you the gen still isnt grounded. heres a foto of him and one of the gens he ran.

My God man, what happened to his face?
Logged
Scott AKA "Skyking" Holtzman

Ghost Audio Visual Solutions, LLC
Cleveland OH
www.ghostav.rocks

Jonathan Johnson

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3209
  • Southwest Washington (state, not DC)
Re: Bonding and false positive tests on GFCI
« Reply #33 on: September 05, 2014, 01:20:16 AM »

My God man, what happened to his face?
Now you know where Darth Vader gets his power. :P
Logged
Stop confusing the issue with facts and logic!

Jeff Bankston

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2568
Re: Bonding and false positive tests on GFCI
« Reply #34 on: September 05, 2014, 01:40:31 AM »

My God man, what happened to his face?
he had a black out ! lol lol lol !
Logged

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3361
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: Bonding and false positive tests on GFCI
« Reply #35 on: September 05, 2014, 05:37:13 PM »

My God man, what happened to his face?

In a witness protection program?

frank kayser

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1654
  • Maryland suburbs of Washington DC
Re: Bonding and false positive tests on GFCI
« Reply #36 on: September 05, 2014, 06:04:34 PM »

In a witness protection program?
So's the truck...


I guess he's kinda hard to find for a repeat job...
Logged

Jeff Bankston

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2568
Re: Bonding and false positive tests on GFCI
« Reply #37 on: September 05, 2014, 06:29:26 PM »

simi blacked out
Logged

Tim McCulloch

  • SR Forums
  • Hero Member
  • *
  • Offline Offline
  • Posts: 23736
  • Wichita, Kansas USA
Re: Bonding and false positive tests on GFCI
« Reply #38 on: September 05, 2014, 06:54:20 PM »

So's the truck...


I guess he's kinda hard to find for a repeat job...

Or protecting the confidentiality of the grip truck company, who probably didn't provide direct consent to have their name/logo used.
Logged
"If you're passing on your way, from Palm Springs to L.A., Give a wave to good ol' Dave, Say hello to progress and goodbye to the Moonlight Motor Inn." - Steve Spurgin, Moonlight Motor Inn

frank kayser

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 1654
  • Maryland suburbs of Washington DC
Re: Bonding and false positive tests on GFCI
« Reply #39 on: September 05, 2014, 07:56:41 PM »

Or protecting the confidentiality of the grip truck company, who probably didn't provide direct consent to have their name/logo used.
Of course that's the serious answer... wasn't nearly as much fun, though!  :P
Logged