I found this, regarding AFCI breakers in residences.  I don't know what is code for commercial space.
210.12(B)Dwelling Units.
All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways , or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type installed to provide protection of the branch circuit.
Note 1:  Not all states require this.
Note 2:  AFCIs resemble a GFCI/RCD (Ground-Fault Circuit Interrupt/Residual-Current Device) breaker in that they both have a test button although each has a different function. GFCIs and RCDs are designed to protect against electrical shock of a person, while AFCIs are primarily designed to protect against electrical fires caused by arcing. Some outlets must be protected by both a GFCI and an AFCI, such as an outlet near a wet bar in a family room.
-Dennis
Stephen Swaffer
Re: AFCI Breakers
« Reply #1 on: December 07, 2013, 01:21:52 am »
AFCIs have not been required by the NEC in commercial spaces yet-their purpose is completely different than GFCIs-and they do the most good when used with NM cable wiring-wiring that is prone to being damaged by nails or screws usually not used in commercial applications.  I haven't yet read the 2014 code but I am hearing that virtually every receptacle in residential will be required to be either AFCI or GFCI protected depending on the location.
They do cost more of course-and I have personally dealt with situations where AFCI's would have been very helpful-but I am not going to argue for or against them!
Steve Swaffer
Mike Sokol
Re: AFCI Breakers
« Reply #2 on: December 07, 2013, 02:13:59 am »
First generation AFCI's were very poor at differentiating between the normal sparking of something like a light switch turning on an incandescent bulb, and a partial short inside a wall that's sparking and creating a fire hazard. I think the later gen designs are much better, but have not personally done any testing on them. I would say that running a sound system from AFCI breakers could be fraught with circuit breakers tripping at inopportune times. For instance, how many times have a stage amp's power plug been pulled out of the receptacle accidentally without being switched off first? That spark would probably be enough to shut down your back-line power feed.
The entire argument over the actual need for AFCI's to begin with has always been a money vs. any actual reduction of electrical house fires issue. Plus the random AFCI tripping from normal light switch sparking doesn't make a homeowner happy when they have to reset the breaker every week.
For now, code is only requiring AFCI breakers in branch circuits feeding bedrooms in homes and such. But I can see code extending this to wall circuits in venue stages pretty soon. Then it's going to get interesting when the back-line power goes out during a music set.
Mike Sokol
mike@noshockzone.org
www.NoShockZone.org
Re: AFCI Breakers
« Reply #3 on: December 07, 2013, 03:16:45 am »
Compartmentalization... each duplex outlet protected by its own AFCI (like GFCI outlets can be done today).  If it's a genuine problem, the NFPA committee might carve out an AFCI exemption for specific uses in particular special occupancies as has been done for GFCIs.
Cailen Waddell
Re: AFCI Breakers
« Reply #4 on: December 07, 2013, 07:20:37 am »
Or suddenly every PAC will own a small power distro they tie into a disconnect to provide power and all the outlets will be taped over...
TJ (Tom) Cornish
  • St. Paul, MN
Re: AFCI Breakers
« Reply #5 on: December 07, 2013, 08:35:54 am »
That defeats some of the purpose of AFCIs - the intent is to protect the branch wiring in the walls from picture hanging nails, and the fire mentioned from too many pieces of Romex under a staple. If the AFCI protection was done at the receptacle, the branch wiring would have no AFCI protection.
Stephen Swaffer
Re: AFCI Breakers
« Reply #6 on: December 07, 2013, 11:44:57 am »
In a commercial or stage setting with EMT/GRC used as a wiring method, protection of branch wiring from nails/screws would not be a major concern-but AFCI recepts might be helpful to shut down bad SO cords etc.  But in that situation, GFCI is more important in my mind-if exposed cords get hot enough to burn with people around they should get noticed.  Concealed wiring where people are sleeping is a much bigger concern and easier to justify the cost.  I think the main reason for AFCI receptacles at this point is time is that electricians will no longer be allowed  to install a non-AFCI recept in a residential location-and  AFCIs cannot use a shared neutral-so to extend a circuit with a shared neutral you will need to install an AFCI to feed downstream.
Steve Swaffer
Re: AFCI Breakers
« Reply #7 on: December 07, 2013, 02:32:53 pm »
We're comparing different occupancies... IF the NFPA were to adopt AFCI for our occupancy, the AFCI would be upstream, yes, but I propose that each duplex outlet be protected by its own upstream AFCI.  That way someone doing a hot un-plug wouldn't take out the rest of the stage stringer.
I can see how my 2am post could be interpreted to mean that AFCI *outlets* would be adequate when they clearly are not.  I'll clear that up later.