Alan Hamilton wrote on Tue, 30 November 2010 17:27 |
I wonder if tight-packing them in the rack contributed to an overheating issue? Also, what is the back of the rack like (filled with rack panels or ventilated in some way)?
The one thing that pulls me away from blaming the dimmers is that (as I read it) all 4 started acting up at once. Even with overheating I'd expect them to not react similarly at the same moment. It wouldn't surprise me to see them all have the same failure mode when overheated, but I wouldn't expect them all to have that happen at once.
|
Hey Alan - I wondered about running them all together as well, but you would think they would think that ultimately someone might use them tightly packed, but I hear ya. Only the bottom four dimmers were on, and it is an open backed rack, becuase I put the socas right on the dimmer pack itself.
They are back to front cooled so I wouldn't think staking them would cause them to over heat, but who knows.... also like I was saying to James, this was in an ice rink , with the ice IN, so the ambiant temp was fairly low ( dimmer friendly if you ask me), so I would of thought cooling would be an issue for either the feeder or the dimmer... but low and behold.... I was wearing my jacket the whole time, and we had a small 15 amp heater keeping our feet warm. Maybe that's what put it over the top for the power...lol
These are the top four dimmers when they were in another rack... they are still on twistlock plugs, whereas the bottom four are hardwaired to the distro in the bottom of the rack....
You can see the soca mounted on the back - so the dimmer is open just like this...