Title: 30A to 15A Pigtails?
Post by: Andrew Brubaker on February 07, 2014, 12:48:46 AM
Quick electrical wiring question...

I have my power distro set up with several L14-30 twist lock receptacles that I run to amp racks, stage snakes, etc.
My question is when I am working a gig where I am unable to do a proper tie in would it be possible to make some adapters to "pool" power together for the amp racks? Aka have two 15A edison plugs that then run into an L14-30 receptacle and share a common neutral and ground but each keep their separate hot poles? The idea would be to pull power from two separate circuits with standard edison receptacles and "merge" them together to power the amp rack.

Is this possible?
Title: Re: 30A to 15A Pigtails?
Post by: Mike Sokol on February 07, 2014, 06:43:50 AM
Quick electrical wiring question...

I have my power distro set up with several L14-30 twist lock receptacles that I run to amp racks, stage snakes, etc.
My question is when I am working a gig where I am unable to do a proper tie in would it be possible to make some adapters to "pool" power together for the amp racks? Aka have two 15A edison plugs that then run into an L14-30 receptacle and share a common neutral and ground but each keep their separate hot poles? The idea would be to pull power from two separate circuits with standard edison receptacles and "merge" them together to power the amp rack.

Is this possible?

Possible, but a serious code violation to do so.

The first problem is that you can't guarantee that the two outlets you connect from will be on separate legs (phases) of the panel. If they're on the same phase, then instead of your neutral currents subtracting, they'll add together. So you can easily burn up a neutral wire. However, in your case the two 15-amp services could never draw more than the 30-amp capacity of your plug contacts and cable (assuming you're using 10 gauge wiring). 

The second problem is that any circuit breakers feeding such a receptacle must be ganged together. That is, if one of the legs trips from over-current, the other leg must also trip. This is to prevent 240-volt loads from cross-feeding power from the "on breaker" to the loads connected to the "off breaker". That would create very bad and unsafe conditions for both the gear and the user.

If you do build one of these gadgets and an inspector sees it, he will almost certainly shut down your show. And he'll likely want to put a magnifying glass on your entire rig. Worse still, if there's a fire at your gig, even if it's not your fault", you'll have every lawyer within a hundred miles after you for liability. "It's always the sound guy's fault".

So the answer is this. While it could works in theory, there's too many practical and legal reasons not to do it. Hate to say it, but in these cases running heavy Edison extension cords around is the only good option. And if you're worried about ground-loop hum from multiple outlets, that's the best reason to have 1:1 audio isolation transformers on the inputs of your power amps. 
Title: Re: 30A to 15A Pigtails?
Post by: TJ (Tom) Cornish on February 07, 2014, 07:12:40 AM
Possible, but a serious code violation to do so.

The first problem is that you can't guarantee that the two outlets you connect from will be on separate legs (phases) of the panel. If they're on the same phase, then instead of your neutral currents subtracting, they'll add together. So you can easily burn up a neutral normally. However, in your case, the two 15-amp services could never draw more than the 30-amp capacity of your plug contacts and cable (assuming you're using 10 gauge wiring). 

The second problem is that any circuit breakers feeding such a receptacle must be ganged together. That is, if one of the legs trips from over-current, the other leg must also trip. This is to prevent 240-volt loads from cross-feeding power from the "on breaker" to the loads connected to the "off breaker". That creates very bad and unsafe conditions for both the gear and the user.

If you do build one of these gadgets and an inspector sees it, he certainly shut down your show. And he'll likely want to put a magnifying glass on your entire rig. Worst still, if there's a fire at your gig, even if it's not your fault"  you'll have every lawyer within a hundred miles after you for liability.

So the answer is this. While this could works in theory, there's too many practical and legal reasons not to do it. Hate to say it, but in these cases running heavy Edison extension cords around is the only good option. And if you're worried about ground-loop hum from multiple outlets, that's the best reason to have 1:1 audio isolation transformers on the inputs of your power amps.
In addition to your excellent list of reasons not to make a cheater, there is one more. If one of the receptacles is miswired with a H/N reversal, an adapter like this will short out the circuit. If both receptacles are H/N reversed, you will be shorting 240/208 volts together, which is a significantly bigger bang.
Title: Re: 30A to 15A Pigtails?
Post by: Steve M Smith on February 07, 2014, 07:31:10 AM
I have seen this done in the UK (only once and a long time ago) with two 13 amp plugs into both outlets of a double socket.

Obviously they will both be on the same circuit but will have double the capacity (13 amp fuse in each plug).

However, if one becomes unplugged, there is live 240 volts on the pin of the plug.


Steve.
Title: Re: 30A to 15A Pigtails?
Post by: Keith Broughton on February 07, 2014, 09:02:22 AM
Quick electrical wiring question...

I have my power distro set up with several L14-30 twist lock receptacles that I run to amp racks, stage snakes, etc.
My question is when I am working a gig where I am unable to do a proper tie in would it be possible to make some adapters to "pool" power together for the amp racks? Aka have two 15A edison plugs that then run into an L14-30 receptacle and share a common neutral and ground but each keep their separate hot poles? The idea would be to pull power from two separate circuits with standard edison receptacles and "merge" them together to power the amp rack.

Is this possible?
Technically...I could work.
However...BOBO cable BAD!
Certainly not legal.
Best to avoid.
Title: Re: 30A to 15A Pigtails?
Post by: Kevin Graf on February 07, 2014, 09:03:57 AM
In general, you can't parallel fuses like the way you parallel resistors to double their power handling capacity. With common thermal fuses what happens is one fuse carries slightly more current than the other. The hotter fuse then carries a little bit more current and so on. Now the fuses are not dividing the load evenly and the hot fuse will trip before the cooler fuse.

The exception being very large fuses (the size of a soap can) they may have 50 or 100 carefully matched parallel elements.
Title: Re: 30A to 15A Pigtails?
Post by: Andrew Brubaker on February 07, 2014, 09:10:11 AM
Thank you everyone for the responses. Heavy duty Edison only it is!
Title: Re: 30A to 15A Pigtails?
Post by: Mike Sokol on February 07, 2014, 09:36:28 AM
Thank you everyone for the responses. Heavy duty Edison only it is!

Here's your next challenge... How to determine if two outlets are on separate circuit breakers or wired on the same one. Clubs are notorious for daisy chaining a bunch of stage receptacles on a single 20-amp breaker.

http://forums.prosoundweb.com/index.php/topic,148095.0.html
Title: Re: 30A to 15A Pigtails?
Post by: Keith Broughton on February 07, 2014, 01:08:07 PM
Here's your next challenge... How to determine if two outlets are on separate circuit breakers or wired on the same one. Clubs are notorious for daisy chaining a bunch of stage receptacles on a single 20-amp breaker.

http://forums.prosoundweb.com/index.php/topic,148095.0.html
This is only a partial answer but if you measure 208 between the hots of 2 different extension cables then they are definately on separate breakers.
Title: Re: 30A to 15A Pigtails?
Post by: Jonathan Johnson on February 07, 2014, 01:49:27 PM
One thing to note is that for the aforementioned cheater to provide 30A 120V from two 15A 120V circuits, both circuits MUST be on the same phase and leg of the electrical service.

Another problem with the cheater is that there is nearly 100% certainty that the wiring of the two circuits is different length and therefore different resistances. This means that more current will flow over the circuit with lower resistance; you will likely not get a full 30A before one of the breakers trips (then the other will trip immediately due to overload).

I believe the NEC does permit parallel conductors on one phase/leg (i.e., to achieve 30A service you can parallel two 14 AWG wires rated at 15A each; though it's usually used where larger size of wires are impractical to work with such as in 400A service) but there are specific methods of installation required.
Title: Re: 30A to 15A Pigtails?
Post by: Kevin Graf on February 07, 2014, 02:30:04 PM
[.....................................]

I believe the NEC does permit parallel conductors on one phase/leg (i.e., to achieve 30A service you can parallel two 14 AWG wires rated at 15A each; though it's usually used where larger size of wires are impractical to work with such as in 400A service) but there are specific methods of installation required.

Only large wires can be paralleled. I believe it's 6AWG and bigger.  This is a case of the NEC anticipating that smaller wires might be separated and re-purposed  without resizing the breaker.
Title: Re: 30A to 15A Pigtails?
Post by: Lyle Williams on February 07, 2014, 02:59:13 PM
While there are circumstances (that a layman has no way of being sure of) where the y-cable cheater may work, it is highly dangerous and illegal.  You are not allowed to try and kill people so your show can be 3dB louder.

If one of these was ever seen at a site (even not in service) everything would be shut down on the spot and reported to the OH&S regulator. 

Even once the regulator was done with you, you would never work in sound again.  Seriously, this is such a big screw up that the word would get around everywhere.  All you would be known for would be that y-cable.
Title: Re: 30A to 15A Pigtails?
Post by: TJ (Tom) Cornish on February 07, 2014, 04:02:12 PM
One thing to note is that for the aforementioned cheater to provide 30A 120V from two 15A 120V circuits, both circuits MUST be on the same phase and leg of the electrical service.

Another problem with the cheater is that there is nearly 100% certainty that the wiring of the two circuits is different length and therefore different resistances. This means that more current will flow over the circuit with lower resistance; you will likely not get a full 30A before one of the breakers trips (then the other will trip immediately due to overload).

I believe the NEC does permit parallel conductors on one phase/leg (i.e., to achieve 30A service you can parallel two 14 AWG wires rated at 15A each; though it's usually used where larger size of wires are impractical to work with such as in 400A service) but there are specific methods of installation required.
While not defending the practice, I took the OP to mean that one 15A circuit would feed each leg of the 14-30, in which case it wouldn't make any difference which phase(s) the supply was from.
Title: Re: 30A to 15A Pigtails?
Post by: Mike Sokol on February 07, 2014, 04:40:44 PM
I believe the NEC does permit parallel conductors on one phase/leg (i.e., to achieve 30A service you can parallel two 14 AWG wires rated at 15A each; though it's usually used where larger size of wires are impractical to work with such as in 400A service) but there are specific methods of installation required.

Yeah, but NEVER with extension cords...  ::)
Title: Re: 30A to 15A Pigtails?
Post by: Jonathan Johnson on February 07, 2014, 06:40:58 PM
One thing to note is that for the aforementioned cheater to provide 30A 120V from two 15A 120V circuits, both circuits MUST be on the same phase and leg of the electrical service.

While not defending the practice, I took the OP to mean that one 15A circuit would feed each leg of the 14-30, in which case it wouldn't make any difference which phase(s) the supply was from.

I didn't mean to make it sound like I was condoning the practice in a "well, if you did it THIS way it'll be OK" type of manner. Any kind of dual-source cheater is dangerous and should never be considered acceptable practice. Proper tie-ins are proper.

I see now that I was misunderstanding the OP. I made the assumption that the connection was only 120V 30A; the L14-30 connection is in fact rated for 125/250V 30A. Connected properly, it would provide for up to 60A of 120V loads.

From a theoretical standpoint, if each leg of the proposed "cheater" was going to one leg each of the L14-30, phasing doesn't necessarily matter IF there are no double-pole (240V) loads. However, the connection will be limited to 15A 120V on each leg, not 30A. Therefore, the total load could not exceed 30A of 120V loads (or the sum of the capacity of the two 120V circuits). And as Mike pointed out, you could have an overcurrent situation on one of the neutrals for which there is no protection.

---

N.B. -- In the United States, electrical wiring devices are typically rated at 125V or 250V nominal (or a combination thereof). However, the typical single-phase voltage distribution is 120V and 240V (with 208V and 277V variations with 3-phase wiring). Historically it was somewhat lower, so you may see mention from time to time of 110V or 220V. Practically speaking, any mention of voltage between 110V and 125V (or 220V and 250V) is considered to be within the same AC voltage spec. Utility delivery voltage is considered to be acceptable anywhere within that range; less than 110V is considered undervoltage while over 125V is considered overvoltage.
Title: Re: 30A to 15A Pigtails?
Post by: Stephen Swaffer on February 07, 2014, 11:40:35 PM
Actually, you might be able to do it with extension cords as the NEC does allow cables to be paralled; however the minimum size conductor is 1/0  (NEC 2013 310.10 (h) (1)-and finding extension cords that big might be more of a problem than just finding the right tie in.  There are cases where smaller wires can be paralled, but there are severe restrictions-essentially you cannot increase ampacity with smaller wires paralled-it appears to me that it is only allowed to for purposes of reducing voltage drop.
Title: Re: 30A to 15A Pigtails?
Post by: Jonathan Johnson on February 08, 2014, 01:23:02 AM
Actually, you might be able to do it with extension cords as the NEC does allow cables to be paralled; however the minimum size conductor is 1/0  (NEC 2013 310.10 (h) (1)-and finding extension cords that big might be more of a problem than just finding the right tie in.

Probably not, though. I believe that disconnects must interrupt both conductors simultaneously (though code might not even permit parallel disconnects) and since a plug and receptacle is considered a disconnect, there's no way to ensure that two extension cords are unplugged simultaneously.
Title: Re: 30A to 15A Pigtails?
Post by: Tim McCulloch on February 08, 2014, 10:29:49 AM
Probably not, though. I believe that disconnects must interrupt both ALL line conductors simultaneously (though code might not even permit parallel disconnects) and since a plug and receptacle is considered a disconnect, there's no way to ensure that two extension cords are unplugged simultaneously.

You're on the right track.  I fixed it for you.
Title: Re: 30A to 15A Pigtails?
Post by: Andrew Brubaker on February 12, 2014, 10:09:40 PM
I see now that I was misunderstanding the OP. I made the assumption that the connection was only 120V 30A; the L14-30 connection is in fact rated for 125/250V 30A. Connected properly, it would provide for up to 60A of 120V loads.

From a theoretical standpoint, if each leg of the proposed "cheater" was going to one leg each of the L14-30, phasing doesn't necessarily matter IF there are no double-pole (240V) loads. However, the connection will be limited to 15A 120V on each leg, not 30A. Therefore, the total load could not exceed 30A of 120V loads (or the sum of the capacity of the two 120V circuits). And as Mike pointed out, you could have an overcurrent situation on one of the neutrals for which there is no protection.

Yes, that's what I was asking about. And I realize it would not be the full 60A but only 30A. But I'm just going to stick with Edison extension cords when I can't wire in a distro directly. That's what I've done in the past anyways. I was just curious and wanted to get everyone's thoughts if it was possible. And NO was obviously the answer