Ground loop with a portable generator
« on: September 21, 2017, 11:49:30 AM »

Greetings,

I have a question about grounding a 3K watt Yamaha inverter generator during power outages. I am planning on bonding the generator from its supplied ground screw to a bare copper ground wire that runs between my central A/C and pool pump. The main breaker will be off during a power outage. I also would like to run a metal security chain between the metal handles on the generator and an aluminum fence. My question is, do I need to be concerned with a potential ground loop by the generator being bonded to both the copper ground wire and the aluminum fence, assuming the fence is bonded to ground at some place?

Thanks in advance for any advice,
Steve 
Logged

Phil Graham

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 66
Re: Ground loop with a portable generator
« Reply #1 on: September 21, 2017, 01:05:49 PM »

Greetings,

I have a question about grounding a 3K watt Yamaha inverter generator during power outages. I am planning on bonding the generator from its supplied ground screw to a bare copper ground wire that runs between my central A/C and pool pump...

Steve,

The Yamaha inverter generator in question is a floating neutral generator. A floating neutral generator does not have the frame, nor the EGC (i.e. ground/green wire) bonded to the neutral return of the inverter. Per the portable generators manufacturing association, floating neutral generators, like the Yamaha, are not designed to be operated connected to the GEC and ground rod when operating cord and plug equipment in a standalone fashion. Doing so can create result in a secondary fault current path through the earth in some cases. Please let me know if this makes sense, as it is a subtle point.

See reply #4 (http://forums.prosoundweb.com/index.php/topic,164927.msg1519827.html#msg1519827) for clarification of what happens when tied to the mains panel, in lieu of service supply from the utility.

P.S. the attached file is actually a PDF from the portable generator manufacturers association explains the secondary fault current path you could create during standalone use. I've had to change the file extension to get it to upload. Please change it back to .pdf and it will open correctly.

Edit: Clarified the use cases between standalone generator use, and panel tied generator use.
« Last Edit: September 21, 2017, 03:15:34 PM by Phil Graham »
Logged

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2672
Re: Ground loop with a portable generator
« Reply #2 on: September 21, 2017, 01:43:52 PM »

Phil,

This does not make sense to me.  The green ground terminal he mentions is connected to the frame of the genny.  The NEC and the owners manual require this to be attaced to a GEC (grounding electrode conductor) to a grounding electrode.  Bonding in the manner the OP describes can do nothing but improve safety.

I would be interested in reading their explanation-but having trouble getting the file into the correct format.
Logged
Steve Swaffer

Phil Graham

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 66
Re: Ground loop with a portable generator
« Reply #3 on: September 21, 2017, 02:20:07 PM »

Phil,

This does not make sense to me.  The green ground terminal he mentions is connected to the frame of the genny.  The NEC and the owners manual require this to be attaced to a GEC (grounding electrode conductor) to a grounding electrode.  Bonding in the manner the OP describes can do nothing but improve safety.

I would be interested in reading their explanation-but having trouble getting the file into the correct format.

Stephen,

Take the attached file, and change the extension to .pdf, and it should open for you in your PDF viewer of choice.

I discussed this whole topic at great length with the PGMA back in 2013 in the course of writing a series of articles on small generators for FOH. details surrounding all of that that are contained in the linked thread, including discussion of the double fault case:
https://soundforums.net/forum/low-earth-orbit/lighting-electrical/8463-nfpa-decision-on-new-section-nec-445-20-for-small-15kw-portable-generators

I think if you read that thread, it will clarify PGMA's thinking.
Logged

Phil Graham

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 66
Re: Ground loop with a portable generator
« Reply #4 on: September 21, 2017, 03:09:06 PM »

Some further thoughts, as I probably have muddied the OPs original q:

If the OP is connecting the generator to their main panel by means of a transfer switch, or open mains breaker, then the Yamaha will already have the single EGC / Grounded conductor / GEC / panel enclosure bond point at the main panel. This point will therefore tie the Yamaha to the grounding electrode. For this use case you would not want a second grounded -> egc bond point at the generator, to prevent objectionable current via the generator's EGC, per NEC 250.6. It is this use case why the manufacturers float the generator neutral.

You could bond the generator's frame to the GEC, of course, which is presumably what the AC -> pool pump wire is acting as.

---

The NEC compliance of all "floating neutral" generators is contingent on their being no fault current possibility, which is assured by the floating neutral under single fault conditions. The moment that a fault current could flow (e.g. via a second fault through ground), then there must be a low impedance path for that fault current, which their standard egc configuration does not provide. Hence not grounding the floating neutral generator in the event of standalone use with cord and plug connnected equipment.
« Last Edit: September 21, 2017, 03:20:08 PM by Phil Graham »
Logged

Steven Cohen

  • Full Member
  • ***
  • Offline Offline
  • Posts: 150
Re: Ground loop with a portable generator
« Reply #5 on: September 21, 2017, 03:17:26 PM »

Thanks Phil for taking the time to respond.
 I am glad you posted the link to the thread from the SoundForum Network as I was planning on using an external GFCI device to female end of an extension cord. If I understand the floating ground principle correctly, the GFCI would not provide any additional protection as a GFCI needs a bonded ground to function correctly.
I think my best option at this point is to feed a manual transfer switch from the generator’s 125 volt, 30-amp twist lock receptacle to my home’s main electrical service panel. Coincidentally, I have a 35 year old Federal Pacific electrical service panel that needs to replaced due to being a fire hazard, I will have the manual transfer switch installed at the same time.


Some further thoughts:

The NEC compliance of all "floating neutral" generators is contingent on their being no fault current possibility, which is assured by the floating neutral under single fault conditions. The moment that a fault current could flow (e.g. via a second fault through ground), then there must be a low impedance path for that fault current, which their standard egc configuration does not provide. Hence not grounding the floating neutral generator in the event of standalone use.

Further, if the OP are connecting the generator to their main panel by means of a transfer switch, or open mains breaker, then the Yamaha will already have the single EGC / Grounded conductor / GEC bond point in the main panel. This point will therefore tie the Yamaha to the grounding electrode. For this case you would not want a second grounded -> egc bond point at the generator, to prevent objectionable current via the generator's EGC, per NEC 250.6. You could bond the generator's frame to the GEC, of course.
Logged

Scott Holtzman

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 7530
  • Ghost AV - Avon Lake, OH
    • Ghost Audio Visual Systems, LLC
Re: Ground loop with a portable generator
« Reply #6 on: September 21, 2017, 03:27:02 PM »

If I understand the floating ground principle correctly, the GFCI would not provide any additional protection as a GFCI needs a bonded ground to function correctly.


GFCI does not require a ground to function, it detects a difference between the forward and return load.
Logged
Scott AKA "Skyking" Holtzman

Ghost Audio Visual Solutions, LLC
Cleveland OH
www.ghostav.rocks

Phil Graham

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 66
Re: Ground loop with a portable generator
« Reply #7 on: September 21, 2017, 03:29:33 PM »

Thanks Phil for taking the time to respond.
 I am glad you posted the link to the thread from the SoundForum Network as I was planning on using an external GFCI device to female end of an extension cord. If I understand the floating ground principle correctly, the GFCI would not provide any additional protection as a GFCI needs a bonded ground to function correctly.

This is part of of Guy's discussion on "equivalent protection," in the event of a double fault, in the SFN thread. But that is in the context of a standalone floating neutral generator with double fault conditions. A GFCI merely looks for current difference, ground or no, but Guy's point is that this specific fault case bypasses the GFCI's ability to detect the current difference.

I re-organized reply #4 for clarity while you were posting your reply, so maybe have a look at it again for your intended use case.

Quote
I think my best option at this point is to feed a manual transfer switch from the generator’s 125 volt, 30-amp twist lock receptacle to my home’s main electrical service panel...

If you tie the generator into your mains panel, then the EGC -> GEC -> grounded (i.e. neutral) bond is done in the panel, and your Yamaha becomes a "normal" generator with N/G bonding, by means of the panel. You don't want a second N/G bonding at the genny, as that would give two parallel current paths between the panel and the gennie. But because the generator is already tied to the GEC and grounding electrode via the panel, there's no problems with further bonding the generator frame to the GEC, or the fence to the GEC.
« Last Edit: September 21, 2017, 03:42:07 PM by Phil Graham »
Logged

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2672
Re: Ground loop with a portable generator
« Reply #8 on: September 21, 2017, 04:43:10 PM »

My understanding is that he was using the ground screw on the genny-which is essentially the frame of the genny to bond to the fence/egc.  This has absolutely NOTHING to do with ground-neutral bonding-which on that genny could only be accomplished by an internal modification or some sort of a G-N adapter as has been discussed in other threads.  Making sure the fence is in fact bonded to the install (not just earth grounded) adds a significant measure of safety to this setup-even if the genny is connected through a transfer switch and thus bonded to ground.  There was a recent electrocution (Kansas, I believe) of a child that in all liklihood would have been prevented had the fence been bonded to the electrical service (no matter if that is a genny or mains).

I would argue that a GFCI still provides protection in the case of a double fault.  Sure-it won't detect current flowing from line-line.  GFCI's never will, but if fault current takes an  alternate path bypassing any part of the proper circuit of a GFCI it will still trip.  If there is no path for fault current to follow to trip the GFCI, then there is no path for fault current to follow to electrocute somebody.  I'd rather have the GFCI present in case a fault occurs that I am not aware of-either in the genny or something attached to the genny-that essentially bonds one side of the circuit making it a "neutral".

Stephen,

Not sure what panel you are installing.  Several manufacturers make UL listed kits to allow a breaker in the panel to be interlocked with the main and backfed to be used as a transfer switch.  This is usually far more cost effective than a seperate transfer switch and very easy to incorporate during an upgrade like this.  I've installed several and never had an inspector have an issue.  Just an option to explore.
Logged
Steve Swaffer

Jonathan Johnson

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3209
  • Southwest Washington (state, not DC)
Re: Ground loop with a portable generator
« Reply #9 on: September 22, 2017, 12:32:40 PM »

Red flags flew up in my mind when I read this...

...The main breaker will be off during a power outage...

This made it sound as though you were planning to hook the generator up with a double-male cord plugged in to the generator and an outlet somewhere in the house.

Connecting a generator to premises wiring by means of a double-male cord or wiring into a standard panel is a big no-no. Even if you plan to turn the main breaker is off, there is too much danger of backfeeding electricity into the power grid, which can endanger utility workers and potentially overload your generator.

So I was relieved when I read this later post:

... I was planning on using an external GFCI device to female end of an extension cord. ...

...I think my best option at this point is to feed a manual transfer switch from the generator’s 125 volt, 30-amp twist lock receptacle to my home’s main electrical service panel. Coincidentally, I have a 35 year old Federal Pacific electrical service panel that needs to replaced due to being a fire hazard, I will have the manual transfer switch installed at the same time.

The second part of this is good. A properly installed transfer switch ensures that electricity from a generator can never be inadvertently backfed into the power grid. Besides, if the "far" end of a double-male cord comes unplugged, now you've got exposed live conductors trying to poke things.

When connecting a transfer switch for standby power, it's a good idea to keep a light connected to the utility power and turned on so that you'll know when the utility power comes back on.

* * * * *

If the neutral of the generator is internally bonded to the frame, do not use the onboard GFCI to feed a transfer switch. That's because on the utility or home side of the transfer switch, the ground and neutral will be bonded.

In other words, when feeding a transfer switch, you'll have a ground-neutral bond on both sides of the GFCI. That means there's a potential return path for "neutral" current around the GFCI sensing circuitry from the premises G-N bond, through the equipment grounding conductor of the cord, and the generator's G-N bond. This will cause the GFCI to trip even when there isn't a fault.

If the generator does not have an internal G-N bond, then using the onboard GFCI to feed a transfer switch should not be a problem.

If you're using the generator to power multiple devices, it's recommended to bond ground and neutral. In a floating system, a fault in a single device isn't necessarily a problem, but if you have faults in multiple devices, the lack of a ground-neutral bond at the generator can result in voltage potential between the devices which could cause ground currents in audio interconnects or power cords, or potentially personnel should they come between two pieces of faulty equipment.

If you have audio devices powered by different power sources, such as two generators, a generator and shore power, or shore power from two different houses, you should ensure that the grounds of all power sources are externally bonded to prevent ground currents in audio interconnects or even personnel. (Audio isolation transformers with ground lift can also help.)
Logged
Stop confusing the issue with facts and logic!

Phil Graham

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 66
Re: Ground loop with a portable generator
« Reply #10 on: September 22, 2017, 03:45:16 PM »

Not sure what panel you are installing.  Several manufacturers make UL listed kits to allow a breaker in the panel to be interlocked with the main and backfed to be used as a transfer switch.  This is usually far more cost effective than a seperate transfer switch and very easy to incorporate during an upgrade like this.  I've installed several and never had an inspector have an issue.  Just an option to explore.

Stephen,

You have links to some of those?
Logged

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2672
Re: Ground loop with a portable generator
« Reply #11 on: September 22, 2017, 04:50:34 PM »

https://www.amazon.com/s/?ie=UTF8&keywords=interlock+kit+square+d&tag=mh0b-20&index=aps&hvadid=77653035794143&hvqmt=b&hvbmt=bb&hvdev=c&ref=pd_sl_8l6i84nkwj_b

http://www.milbankworks.com/specsheets/784572478787_SS.pdf


They are panel specific so just search your manufacturer-I've preferrred Sqyare D panels-they are available at bog box retailers as well.  The Milbank works in their meter/main panel setup-if your POCO allows their models I really like those-they let you setup connection to your genny outside the house-and often in an old install they run service entrance conductors too far through the house for new inspections so it fixes that non-compliance as well.

The other thing I usually do is instead of an inlet, I hard wire a male plug to a piece of SO and coil it up inside a 12"X12" 3R jbox outside.  Most people would only use the 4 wire cable with their genny for emergency power to their house - this is usually a little cheaper than an inlet and you'll never misplace the power cord for your house.  All you'll need in a power outage is the genny and a screwdriver.
Logged
Steve Swaffer

Steven Cohen

  • Full Member
  • ***
  • Offline Offline
  • Posts: 150
Re: Ground loop with a portable generator
« Reply #12 on: September 23, 2017, 10:37:13 AM »

Thanks Stephen for the response.

 You correct in stating that I was referring to using the manufacturer supplied ground screw on the generator connected to a copper ground wire that runs between my pool pump and AC. I was not planning on making any type of internal modification or ground to neutral adapter.

 My original plan was to output the 30 amp/125volt, twist lock receptacle on the generator, connecting a 100 foot, 10/3, GenTran cord with a quad box. Each duplex on the quad box has its own 20 amp breaker. Here is a link to a 25 foot version of the same setup.

https://www.amazon.com/gentran-generator-contractor-receptacles-b10325dw/dp/b001ulbrn2


 For clarity, my original concern was that I would have potentially two paths to ground, one being the known ground of the connection between the ground screw on the generator and the copper bond between my AC and pool pump, and the potential ground of the security chain wrapped around the metal handle of the generator and the other end of the security chain wrapped around an aluminum fence. I was not sure if having two paths to ground, if the aluminum fence is grounded, was unsafe.

I am still a bit unclear if I ground the floating neutral inverter generator using the ground screw connected to a copper ground is unsafe. That is the reason why I am now looking into a manual transfer switch when I have the new electrical service panels installed. I am not sure if an interlock will work because I have my main breaker on one panel outside near the meter, and a sub panel in the garage for the rest of the house, I will ask the electrician if this is an option.

Another issue I will face if I connect the generator to the main service panel is that the main panel is in the front of the townhouse. I want to keep the generator at the rear of the townhouse so it is out of plain view. The townhouse is two floors and connected on both sides. It will be a difficult, expensive run. That is why I originally opted for the single GenTran extension cord with a quad box. But if I cannot ensure that it is as safe as connection to the service panel, the expense is worth the costs.

Thanks again to everyone who has responded with suggestions,
Steve
 

         

My understanding is that he was using the ground screw on the genny-which is essentially the frame of the genny to bond to the fence/egc.  This has absolutely NOTHING to do with ground-neutral bonding-which on that genny could only be accomplished by an internal modification or some sort of a G-N adapter as has been discussed in other threads.  Making sure the fence is in fact bonded to the install (not just earth grounded) adds a significant measure of safety to this setup-even if the genny is connected through a transfer switch and thus bonded to ground.  There was a recent electrocution (Kansas, I believe) of a child that in all liklihood would have been prevented had the fence been bonded to the electrical service (no matter if that is a genny or mains).

I would argue that a GFCI still provides protection in the case of a double fault.  Sure-it won't detect current flowing from line-line.  GFCI's never will, but if fault current takes an  alternate path bypassing any part of the proper circuit of a GFCI it will still trip.  If there is no path for fault current to follow to trip the GFCI, then there is no path for fault current to follow to electrocute somebody.  I'd rather have the GFCI present in case a fault occurs that I am not aware of-either in the genny or something attached to the genny-that essentially bonds one side of the circuit making it a "neutral".

Stephen,

Not sure what panel you are installing.  Several manufacturers make UL listed kits to allow a breaker in the panel to be interlocked with the main and backfed to be used as a transfer switch.  This is usually far more cost effective than a seperate transfer switch and very easy to incorporate during an upgrade like this.  I've installed several and never had an inspector have an issue.  Just an option to explore.
Logged

Rob Spence

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3531
  • Boston Metro North/West
    • Lynx Audio Services
Re: Ground loop with a portable generator
« Reply #13 on: September 23, 2017, 02:51:14 PM »

This comment only applies to using the generator stand alone.

If using the generator with the quad box you linked to, the security chain to the fence will be fine. The ground wire from the pool will be the safety ground.

However, to make faults to ground trip the circuit breaker, you need to bond the neutral to ground. The easy way, as described by Mike Sokol, is to take a common Nema 5-15 cord cap, wire the neutral screw to the ground screw, paint it an awful color, and plug it into a receptacle on the generator.

Note, the shorting plug should not be used when connecting to a home breaker panel as the main panel will (should?) have bonded the neutral to the ground (per NEC) and you only want that bonding done in one place.


Sent from my iPad using Tapatalk HD
« Last Edit: September 23, 2017, 02:53:25 PM by Rob Spence »
Logged
rob at lynxaudioservices dot com

Dealer for: AKG, Allen & Heath, Ashley, Astatic, Audix, Blue Microphones, CAD, Chauvet, Community, Countryman, Crown, DBX, Electro-Voice, FBT, Furman, Heil, Horizon, Intellistage, JBL, Lab Gruppen, Mid Atlantic, On Stage Stands, Pelican, Peterson Tuners, Presonus, ProCo, QSC, Radial, RCF, Sennheiser, Shure, SKB, Soundcraft, TC Electronics, Telex, Whirlwind and others

Stephen Swaffer

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 2672
Re: Ground loop with a portable generator
« Reply #14 on: September 23, 2017, 04:40:58 PM »

Thanks Stephen for the response.



https://www.amazon.com/gentran-generator-contractor-receptacles-b10325dw/dp/b001ulbrn2


 For clarity, my original concern was that I would have potentially two paths to ground, one being the known ground of the connection between the ground screw on the generator and the copper bond between my AC and pool pump, and the potential ground of the security chain wrapped around the metal handle of the generator and the other end of the security chain wrapped around an aluminum fence. I was not sure if having two paths to ground, if the aluminum fence is grounded, was unsafe.


To this specific question.  The NEC requires any and all "grounding electrodes" present on a premises to be bonded (connected with a metalic path).  Obviously, if multiple paths to ground were an issue that would not be required.  It is common to have ground rods, metal water lines, gas lines and ufer (concrete encased electrodes-usually the rebar of a foundation) all connected in building.  I just finished a large inustrial addition with a separate service than the original building-both steel frame buildings.  For safety purposes we intentionally bonded the frames of both buildings.  There are a LOT of paths to ground in this structure.

In addition, code requires anything metallic that "may" become energized to be bonded to that system-ie a fence that has a power cord run through, over, or near it.

Guys service hi tension lines while energized by wearing a metallic "farady" cage style suite.  The idea is that in a suit like that no part of their body can be energized to a different part than any other.  That is the same idea as bonding metal parts and grounding electrodes (either intentional or incidental) together to create one big metal "cage" of anything metal on a premises.  Your concern of the chain wrapped around the fence and genny without an intentional bond is a perfect example of hazards people often overlook-you were wise to see that as a hazard-I would suggest ensuring that is in fact bonded somehow.

Others have spoken correctly on the ground-neutral bond.  This specific connection should exist for safety-and it should exist in only one place.  Multiple G-N bonds will create undesired, unsafe loops.
Logged
Steve Swaffer

Phil Graham

  • Jr. Member
  • **
  • Offline Offline
  • Posts: 66
Re: Ground loop with a portable generator
« Reply #15 on: September 24, 2017, 12:54:44 PM »

...I was referring to using the manufacturer supplied ground screw on the generator connected to a copper ground wire that runs between my pool pump and AC. I was not planning on making any type of internal modification or ground to neutral adapter.

 My original plan was to output the 30 amp/125volt, twist lock receptacle on the generator, connecting a 100 foot, 10/3, GenTran cord with a quad box. Each duplex on the quad box has its own 20 amp breaker...

Steve,

Kudos for asking questions. You've inadvertently stepped into a tricky world. Floating neutrals are 'magically' safe and code compliant for their two most common use cases for Joe public:

1. "Cord and plug connected" equipment (e.g. power tools, emergency refrigerator) with no connection to earth. This is safe because there is no fault current path, and is code compliant as per NEC 250.34.

2. Tied to a house panel via transfer switch for backup power. Here the panel provides the neutral -> ground bond, and the floating neutral insures that there aren't two parallel paths to the generator over neutral and EGC, as required by NEC 250.6.

As Stephen has explained, many points of bonding between ground rods and GEC is common, preferred, and to code. Ground to ground is good.

The problem arises when there are multiple neutral -> ground bond points, which can cause the EGC, which is normally not a current carrying conductor, to be a parallel path for the return current to the generator.

Quote
I am still a bit unclear if I ground the floating neutral inverter generator using the ground screw connected to a copper ground is unsafe.

If you are going to bond the generator to your pool GEC, and then use outlets connected via cord and plug, you should create a N -> G bond on the generator in the manner that Rob describes in this thread.

If you are going to use the Yamaha with a transfer switch, then the N -> G bond will be in the panel and the generator is ready to go without any additional bonding.
« Last Edit: September 24, 2017, 02:16:32 PM by Phil Graham »
Logged

Steven Cohen

  • Full Member
  • ***
  • Offline Offline
  • Posts: 150
Re: Ground loop with a portable generator
« Reply #16 on: September 24, 2017, 07:34:30 PM »

Thanks everyone for the information.

Today I made a neutral to ground NEMA 5-15 plug. I will use that plug, along with bonding the generator to the ground wire that runs between my AC and pool pump. If I add a manual transfer switch or interlock in the future, I will not use the neutral to ground NEMA 5-15 plug, the house wiring will bond neutral to ground.

Steve



 
Logged

shelley watreen

  • Newbie
  • *
  • Offline Offline
  • Posts: 5
    • Diesel generator set
Re: Ground loop with a portable generator
« Reply #17 on: November 01, 2017, 02:45:50 AM »


The instructions that came with my new 5500w portable generator says to install a ground rod at least 24" deep.
But mine is not yamaha.

I'm going to be using it to power my welding machine, power tools, air compressor, etc. from the back of my farm trailer, wherever it's needed. ;D ;D ;D
I guess it makes sense, but I've never known anyone that's actually pounded in a ground rod before using their yuchai generator.

I've thought about attaching a GFI protected receptacle to my generator trailer and connecting through that. That's better protection than an earth ground. When it's connected to the house to provide power, the prong on the receptacle causes it to be connected to the house's equipment ground. Most tools I use in the field are double insulated and don't have a ground prong anyhow.  8) 8) 8) 8)
Logged
Starlight Power

Mike Sokol

  • Moderator
  • Hero Member
  • *****
  • Offline Offline
  • Posts: 3361
  • Lead instructor for the No~Shock~Zone
    • No~Shock~Zone Electrical Safety
Re: Ground loop with a portable generator
« Reply #18 on: November 01, 2017, 07:48:10 AM »

The instructions that came with my new 5500w portable generator says to install a ground rod at least 24" deep.
But mine is not yamaha.
shelleywa, please change your login to your full name. Thanks... Mike

shelley watreen

  • Newbie
  • *
  • Offline Offline
  • Posts: 5
    • Diesel generator set
Re: Ground loop with a portable generator
« Reply #19 on: November 02, 2017, 03:50:27 AM »

shelleywa, please change your login to your full name. Thanks... Mike

I have already changed it, Mike.
But i found that i can not upload JPG file as avatar...can u please tell me why...Thanks
Logged
Starlight Power

Scott Holtzman

  • Hero Member
  • *****
  • Offline Offline
  • Posts: 7530
  • Ghost AV - Avon Lake, OH
    • Ghost Audio Visual Systems, LLC
Re: Ground loop with a portable generator
« Reply #20 on: November 02, 2017, 06:05:46 PM »

I have already changed it, Mike.
But i found that i can not upload JPG file as avatar...can u please tell me why...Thanks

GIF and animated GIF's (500kb max I think) for Avatar's.  BMP may work, never tried.

Logged
Scott AKA "Skyking" Holtzman

Ghost Audio Visual Solutions, LLC
Cleveland OH
www.ghostav.rocks

ProSoundWeb Community

Re: Ground loop with a portable generator
« Reply #20 on: November 02, 2017, 06:05:46 PM »